To view or edit properties for a selected panel in a circuit, click Modify | Electrical Equipment tab
Properties panel
Properties.
| Parameter | Description |
| Electrical Engineering | |
| Schedule Header Notes | Specify static text to add to the Panel Schedule header. |
| Schedule Footer Notes | Specify static text to add to the Panel Schedule footer. |
| Electrical Loads | |
| Total Connected | The sum of the loads connected to the panel |
| Total Estimated Demand | The total estimated load demand. |
| Total Demand Factor | The total demand factor. |
| Total Connected | The sum of the Power loads connected to the panel |
| Total Estimated Demand (Amps) | The portion of the total Other load, adjusted for demand factor, connected to this panel. See the example for HVAC Total Estimated Demand. See About Demand Factors. |
| Apparent Load Phase A | The real and reactive power used by Phase A. (Phase A Apparent Current x Voltage) |
| Apparent Load Phase B | The real and reactive power used by Phase B. (Phase B Apparent Current x Voltage) |
| Apparent Load Phase C | The real and reactive power used by Phase C. (Phase C Apparent Current x Voltage) |
| General | |
| Panel Name | Name assigned to the panel |
| Mounting | Surface or Recessed |
| Enclosure | Type of panel enclosure - Type 1 or Type 2 |
| Electrical Circuiting | |
| Max #1 Pole Breakers | The number of single pole breakers for the panel |
| Mains | The rating for the mains feeding the panel |
| Circuit Naming | Determines the format for the Circuit Number parameter that appears for circuit properties and identifies the circuit in the System Browser. Prefix types:
| Circuit Prefix Separator | The character or string that separates the prefix from the circuit number. |
| Circuit Prefix | The text string used as the prefix when Prefixed is selected for Circuit Naming. |
| Modifications | Can be used to note features or changes that will appear under the Modifications section of the panel schedule. |
| Short Circuit Rating | Short circuit rating defined by the manufacturer. |
| HVAC Estimated Demand |
The portion of the total HVAC load, adjusted for demand factor, connected to this panel. For example, assume that HVAC demand factors are specified as 100% for 0 VA - 100 VA and 50% for greater than 100 VA. Further, assume a total HVAC load for the project of 600 VA. When the HVAC demand factor is applied, the total estimated demand is (100 VA x 100%) + (500 VA x 50%) = 350 VA. Now consider three panels, P1 with a total HVAC load of 100VA, P2 with a total HVAC load of 200VA, and P3 with a total HVAC load of 300VA. Each panel’s portion of the total estimated demand (350 VA) is calculated based on their share of the total HVAC load connected. Thus, P1 = 1/6, P2 = 1/3, and P3 = 1/2 or 58.3 VA, 116.7 VA, and 175 VA, respectively. See About Demand Factors. |
| HVAC Connected | The sum of the HVAC loads connected to the panel |
| Lighting Total Estimated Demand | The portion of the total Lighting load, adjusted for demand factor, connected to this panel. See the example for HVAC Total Estimated Demand. See About Demand Factors. |
| Lighting Total Connected | The sum of the Lighting loads connected to the panel |
| Total Estimated Demand | The total load, adjusted for demand factor, connected to this panel. See the example for HVAC Total Estimated Demand. See About Demand Factors. |
| Distribution System Types | Distribution System specified for this panel |
| Electrical Data | Voltage and number of poles feeding the panel. |
| Circuits | Click Edit to open the Edit Circuits on Panel dialog. |