Learn how to perform verification for groups of members in the service limit state.
- Continue working in your project or open the project
Frame_3D_Design.rtd.
Note: The Tutorial files are located in C:\ProgramData\Autodesk\Examples\Tutorials
- In the Calculations dialog, select
Code group verification option, and then type "1to4" in the same line.
- In the
Limit states group of options select
SLS, in order to perform calculations for the service limit state, and then type the following loads:
- Dead loads: "1",
- Live loads: "4",
- Total loads: "1to4".
- In the Calculations dialog, click
Calculations.
- The Code Group Verification dialog opens displaying the most significant information about the sections. The
Messages tab (as shown below), contains important information for the next steps in the design process:
Note: The Member Type for Bracings does not determine limit values for deflections. The next step explains how to set these parameters in order to perform the verification as required.
- Close the
Code Group Verification dialog, and then in the Calculation Result Archiving dialog click
Cancel.
A calculation result can be saved in the calculation result archive. In this tutorial we will save the calculation result at the end of the verification process.
- Click
(Design
Steel Members Design - Options
Code parameters).
The Member Type dialog opens.
- Select
Simple bar, and then click
(New steel member type definition).
The Member Definition Parameters dialog opens.
Tip: Select the Member Type that is most similar to the new type that you want to create so that some of the basic properties are automatically applied.
- Type
Simple bar_1 in the
Member type text box, and then click
Service.
The Serviceability - Displacement limiting values dialog opens.
- Select the following values:
- In the
Deflection limits (local system) group of options, select the
Absolute value for Dead, Live and Total Loads,
- In the
Node displacement limits (global system) group of options, select the
Relative value for Total Loads.
- Click
OK.
- Click
Save and close the
Member Definition Parameters dialog.
The new member type is now listed in the Member Type dialog box.
- Ensure that
Simple bar_1 is selected, type "4 5 16 17" in the Lines/Bars field as shown below.
Alternatively, place the cursor in the Lines/Bars field, then go to the drawing area, and hold the
Ctrl key to select bracings with numbers
4,
5,
16 and
17.
- Click
Apply, and then click
Close.
- In the Calculation dialog, click
Calculations.
Results of the Code Group Verification are shown below.
Note: All sections are now properly defined for all the groups of members.
- To visualize the detailed results for a selected group, click
4 Simple bar_1_4 in the Bracings group.
The row is highlighted in black and the Results dialog is displayed:
- Review the results, and then click
OK.
- Close the dialog, and then click
Save in the Calculation Result Archiving dialog.
A final calculation result is saved in the calculation result archive.
- Save the project as
Frame_3D_Verification.rtd.
Click
here to go to the Summary.