The parameters of the seismic simplified analysis according to the equivalent lateral force method depend on a seismic code and a method of defining values of the fundamental periods selected in the Seismic Analysis dialog.
 Job Preferences 
 Design Codes. 
			 
Analysis Types.
				The Analysis Types dialog displays.
The New Case Definition dialog opens.
The Seismic Analysis dialog opens.
The Parameters dialog opens.
 
  The fundamental period Ta is calculated according to the equation 4.6:
Ta = Ct * hn x
where:
Ct - building period coefficient depending on the type of seismic-force-resisting system that is used (given by the code)
x = building period formula exponent (given by the code)
h - structure height (m), defined by difference between Structure range and Reference level
Only Ta on both directions is to be defined.
According to this method you can calculate the exact value for both X and Y directions. If the option Periods with maximal mass participation is off in the Seismic Analysis dialog, the first mode in direction where more masses is active. If this option is on, one of modes, which fulfill limitations and most masses is active in the direction. The maximal period is calculated according to the formula:
Tmax = Cu * Ta,
where:
Cu - Upper Limit Coefficient (Table 12.8-1),
Ta - Approximative Period
(A, B, C, D, E or F) based on the site soil properties, classified according to Chapter 20 of ASCE 7.
as specified in ASCE 7-10 Section 1613.3.1, shown in Figures 1613.3.1(1) through 1613.3.1(6) or ASCE 7-16 Section 11.4.4:
The lateral seismic force induced at any level is determined from:
Fx = V * wx * hk x / (Σ wi * hki) (eq. 12.8-11 and 12.8-12)
where:
wx and wi - floor weight
h - height from base level to appropriate floor level
V - base shear force (this value is already calculated in Robot)
| Period | k | 
|---|---|
|  
						 < 0,5 sec  | 
 
						 1  | 
|  
						 0,5 - 2,5 sec  | 
 
						 Linear interpolation  | 
|  
						 > 2,5 sec  | 
 
						 2  |