The chilled water loop is has a chiller and a variable speed pump to supply chilled water. As an option, the chiller may be water-cooled, in which case it is attached to a condenser loop.
| Property | Value | Notes |
| High temperature loop supply temperature | 15°C | Determined by the air system (typically 12.7778°C). |
| High temperature loop return temperature | 18.333°C | Determined by the air system (typically between 12.7778°C and 18.3333°C by default). |
| Low temperature loop supply temperature | 6.6667°C | |
| Low temperature loop return temperature | 15.5556°C | Set by hot water loop if hot water coil is included in the system. |
The chilled water loop is comprised of 2 main components.
The chiller can be air-or water-cooled, and has the following assumptions.
| Leaving water temperature | N/A | Determined by the loop design stated above. |
| Minimum part load ratio | 0.15 | |
| Flow control | Variable | Modulates flow to meet set point. |
| COP | 5.5 | |
| Condenser entering water temperature | N/A | Determined by the condenser loop (typically 29.44°C). |
The pump in the default chiller configuration has the following assumptions.
| Pressure rise | 179344.014 Pa | |
| Flow type | Variable Speed | |
| Flow control | Intermittent | Only runs when there is demand. |