A water source heat pump operates like a traditional air source heat pump, but it extracts and dissipates heat by way of water instead of air.
Required Objects
The water source heat pump (WSHP) must have the following properties.
- It must be attached to a conditioned zone.
- It must be connected to a condenser loop.
Design Assumptions
- If the Draw Ventilation property is selected, the following will occur.
- The unit will provide the design outdoor air flow.
- The fan will run constantly during occupied hours.
- If the Draw Ventilation property is not selected, the following will occur.
- The unit will not provide any ventilation.
- The fan will cycle on and off to meet conditioning needs.
| Property
Value
Notes
| System air flow
Constant
| Cooling supply air temperature
12.78C
| Heating supply air temperature
40C
Cooling Coil
The cooling coil has the following assumptions.
- It has a single speed DX coil.
- The sensible-to-latent heat ratio is auto-sized to meet system needs during sizing.
| Property
Value
Notes
| Coil leaving air temperature
12.78°C
| COP
3.0
Heating Coil
The heating coil has the following assumptions.
- The coil is a DX single speed heating coil.
| Property
Value
Notes
40°C
| COP
3.0
Supplemental Heating Coil
This is an electric resistance coil with an efficiency of 1.0.
Supply Fan
The supply fan has the following properties.
| Property
Value
Notes
| Pressure rise
300 Pa
| Total efficiency
60%
| Motor efficiency
80%