Runtime messages
These messages may be displayed while a simulation is being processed. Many of them are for information but some are serious warnings. All warnings should be checked and investigated if necessary.
Key to Messages
Left Column
The error message number is used internally by InfoWorks. This number is unique, and may be useful when contacting Innovyze Support.
Centre Column
Name:
The error or warning message that is displayed and written out to the Log File. When the simulation is complete, you can view the log results in a separate window.
Info:
Additional information about the error or warning, such as the name of the network object where the anomaly occurred
Cause:
Why the message has been displayed
Advice:
What, if anything, you need to do about it.
Right Column
Information only - no further action needed
Warning - action may be required
Error - action necessary
List of Runtime Messages
The blue text is the actual text that will be displayed in the log file. Click the blue text for further information.
022
Pumps cannot provide PST Duty Head
Info
Pumping Station name, duty head required and duty head provided.
Cause
The combination of pumps cannot provide the required duty head.
Advice
InfoWorks WS will use the available head, so no computational inaccuracy will occur. Check the pump data for the pumping station.
024
Monthly Demand Coefficients are not normalised for category
Info
Name of the Demand Category
Cause
The sum of all twelve monthly coefficients is not twelve, and therefore the annual average will not be 1.
Advice
You should generally give normalised values for these coefficients, although you are allowed to enter arbitrary values.
025
Weekly Demand Coefficients are not normalised for category
Info
Cause
The sum of all seven daily coefficients is not seven, and therefore the weekly average will not be 1.
Advice
038
Number of equations and system coeff's
Info
Number of equations and system coefficients (measure of the size of matrix to be solved). Average bandwidth (no. of equations / no. of coefficients). Maximum bandwidth (after network reorganisation to minimise matrix bandwidth and number of coefficients to be calculated in each iteration).
Cause
For information
Advice
For information only. No action required.
041
HYDRANT node must have SINGLE connection
Info
Node name
Cause
Node to which hydrant control has been applied is connected to more than one link.
Advice
Check that hydrant control has been applied to correct node. Add node with short link to network to model hydrant.
042
HYDRANT node cannot be Reservoir/Fixed Head
Info
Node name
Cause
Node to which hydrant control has been applied is a Reservoir or a Fixed Head node.
Advice
043
Hydrant ignored - available flow = 0 (disabled), Node
Info
Node name
Cause
Hydrant opening percentage has been specified as zero.
Advice
This may be intentional. If not, check hydrant opening percentage.
046
No Reservoir/FixHead in disconnected network part(s)
Info
Number of disconnected networks
Cause
One or more disconnected networks does not contain a means of calculating head.
Advice
Ensure that each disconnected network contains a Reservoir of Fixed Head Node.
047
Network has disconnected parts
Info
Cause
Network contains two or more disconnected sections.
Advice
106
Control - INITIAL time must be less than FINAL!
Info
Start Time and End Time of simulation
Cause
The Start Time specified in the Hydraulic Run Schedule is later than the End Time.
Advice
Amend Start Time / End Time of simulation
411
PST - Control policy table is empty, PST is OFF
Info
Name of the pumping station
Cause
The pump control data sheet is empty or there are no available pumps in the pumping station. All the pumps in the pumping station are set to OFF.
Advice
Make sure a control policy is defined for each pumping station in the Control Set and run the simulation again.
436
PST Flow is set too high
Info
Pump name, flow set, PST nominal flow
Cause
The flow profile specified for a PST in FLOW control mode is outside of the PST defined curve range.
Advice
Check pump curves are correct. Check specified flow is correct. Replace pumps in station with more suitable units.
442
Pipe permanently closed/unavailable
Info
Pipe name
Cause
Pipe is closed due to pipe control.
Advice
448
No pipe specified for Hydrant target point
Info
None
Cause
Missing parameter in the Fire Flow Options dialog when running a Forced Fire Flow simulation.
The Insert FF_Target_Point node in pipe option has been selected in the Fire Flow Options dialog, but a pipe ID has not been entered.
Advice
Check the parameters in the Fire Flow Options dialog (accessed via the Schedule Hydraulic Run View).
449
Hydrant target point not found in network
Info
None
Cause
Incorrect parameter in the Fire Flow Options dialog when running a Forced Fire Flow simulation.
The Insert FF_Target_Point node in pipe option has been selected in the Fire Flow Options dialog and a pipe ID that does not exist in the network has been entered.
Advice
450
No node specified for Hydrant target point
Info
None
Cause
The Use existing node option has been selected in the Fire Flow Options dialog, but a node ID has not been entered.
Advice
451
Hydrant target point node not found in network
Info
None
Cause
The Use existing node option has been selected in the Fire Flow Options dialog, and a node ID that does not exist in the network has been entered.
Advice
452
Close pipe option will be ignored
Info
None
Cause
Unexpected option selected in the Fire Flow Options dialog when running a Forced Fire Flow simulation.
The Close connected pipe option has been selected in the Fire Flow Options dialog, but the node selected as the hydrant target point does not have a "From" link and a "To" link.
Advice
453
Hydrant target point split pipe distance too small
Info
None
Cause
Distance along pipe parameter defined in the Fire Flow Options dialog (when running a Forced Fire Flow simulation) is too small.
The Insert FF_Target_Point node in pipe option has been selected in the Fire Flow Options dialog and the Distance along pipe value specified is less than the minimum allowable pipe length (0.1m).
Advice
454
Hydrant target point pipe too short to split
Info
None
Cause
Pipe selected in the Fire Flow Options dialog (when running a Forced Fire Flow simulation) is too short.
The Insert FF_Target_Point node in pipe option has been selected in the Fire Flow Options dialog and the length of the pipe to be split is less than twice the minimum allowable pipe length (0.1m).
Advice
455
Hydrant target point split pipe distance too large
Info
None
Cause
Distance along pipe parameter defined in the Fire Flow Options dialog (when running a Forced Fire Flow simulation) is too large.
The Insert FF_Target_Point node in pipe option has been selected in the Fire Flow Options dialog and the length of selected pipe - Distance along pipe value specified is less than the minimum allowable pipe length (0.1m).
Advice
456
Test flows must be greater than zero
Info
None
Cause
A Test Flow specified in the Fire Flow Options dialog is less than or equal to zero.
Advice
457
Hydrant target point node must be Node, Hydrant or Transfer Node
Info
None
Cause
The Use existing node option has been selected in the Fire Flow Options dialog and the selected node is not an allowable type.
Allowable types of hydrant target point node are:
  • Basic Node
  • Hydrant Node
  • Transfer Node
Advice
547
Pumping against TRANSFER or from DEMAND zone
Info
Pump station name. Demand downstream of pump station.
Cause
Negative flow is required through pumping station in a branched part of the network to satisfy demand.
Advice
Check direction of pump station. Check boundary conditions of demand zone (for example check for missing reservoirs or fixed head nodes).
800
Reservoir FULL - Total Overflow
Info
Cumulative overflow from start of simulation. Name of the reservoir.
Cause
The reservoir is full and overspilling (inflow remains higher than outflow).
Advice
This may be intentional if modelling an emergency case.
If not, select all the reservoirs and use the Non Time Varying Report to see all reservoirs that have suffered from overspill. For reservoirs where overspill is excessive, you can display a grid of time varying results for the reservoir and analyse the overspill further.
Your aim should be to define a control policy that prevents significant loss through overspill.
801
Reservoir EMPTY - Total Deficit
Info
Cumulative deficit from start of simulation. Name of the reservoir.
Cause
The reservoir is empty because outflows have exceeded inflows by a sufficient margin that the reservoir is completely empty. From now on, results are of dubious value. InfoWorks will continue computation, assuming that the reservoir water level never falls below the reservoir bottom level.
The water deficit (the amount of water "invented" by the software to maintain the minimum water level) is recorded and available in the simulation results.
Advice
You may want to deliberately analyse this situation. If so, bear in mind that InfoWorks artificially maintains a minimum water level, so results elsewhere in the network will not reflect an actual occurrence of this kind.
If not, select all the reservoirs and use the Non Time Varying Report to see all reservoirs that have suffered from water deficit. For reservoirs where deficit has occurred, you can display a grid of time varying results for the reservoir and analyse the deficit further.
Your aim should be to develop a control policy that prevents reservoirs emptying and maintains adequate reserves.
810
Pump OFF - suction below cut-off level
Info
Name of the pumping station, the pump number, and the total number of pumps in pumping station.
Cause
Pressure (head) in the suction (upstream) node of this pumping station has dropped below the dangerous level for the pump mentioned. InfoWorks has stopped the pump. The pump will restart when local pressure reaches a safe level.
Advice
This should not occur in normal operation. You may have created this situation intentionally to analyse an emergency case. You should aim to develop a control policy that prevents this situation arising.
811
PST (FLOW) Flow change by timer control
Info
Name of the pumping station. Old and new value of flow.
Cause
A scheduled change of flow in the pumping station.
Advice
812
PST (PLAN) No. of active pumps changed
Info
Name of the pumping station. Old and new number of active pumps.
Cause
A scheduled change in the pumping station. One or more pumps has been switched on or off.
Advice
813
PST (AUTO) Level Control pumps change
Info
Name of the pumping station. Old and new STATUS for all pumps.
Cause
A scheduled change in the pumping station. One or more units is switched on or off.
Advice
814
PST (FLOW) OFF by Timer Control
Info
Cause
The pumping station has been switched off as scheduled.
Advice
815
PST (PLAN) OFF by Timer control
Info
Cause
A scheduled change in the pumping station. All pumps are switched off.
Advice
816
PST (AUTO) OFF by Pressure Control
Info
Cause
Advice
817
PST (FLOW) ON by Timer control
Info
Cause
A scheduled change in the pumping station. The pumping station is restarted.
Advice
818
PST (PLAN) ON by Timer control
Info
Cause
Advice
819
PST (AUTO) ON by Pressure Control
Info
Name of the pumping station. Old and new status for all pumps.
Cause
Advice
820
PST (PLAN) Pump Speed Change
Info
Name of the pumping station. Pump unit number. Old and new speed for pump.
Cause
A scheduled change in the pumping station. The speed of the pump is changed.
Advice
821
Control Valve Opening Change
Info
Name of the valve. Old and new opening.
Cause
A scheduled change of valve opening.
Advice
823
Float Valve Closed
Info
Labels of both end nodes for the float valve.
Cause
This float valve was closed to prevent overspilling in the reservoir (downstream node).
Advice
824
Float Valve Activated
Info
Cause
Water level in the reservoir (downstream node) is increasing, and the float valve starts to throttle the inflow to prevent overspilling.
Advice
826
Exceptional Flow at NODE
Info
Node name and exceptional demand flow.
Cause
Exceptional Demand is defined in the Control Data for the node.
Advice
827
Exceptional Flow cancelled - Node isolated
Info
Cause
All exceptional demand assigned to this node will be deleted because the node is isolated from the rest of the network.
Advice
This may be intentional. If not, you must fix the error that has left this node isolated.
829
Hydrant Operation in progress at Node
Info
Node name
Cause
A scheduled opening of hydrant.
Advice
830
Hydrant operation cancelled - Node isolated
Info
Node name
Cause
All hydrant operation assigned to this node will be deleted because the node is isolated from the rest of the network.
Advice
835
PST outside (right) of defined curve range
Info
Name of the pumping station. Head delivered by pumping station.
Cause
Pumping station is operating outside of curve defined by user specified pump curves (delivering lower head and higher flow than defined by curve).
Advice
Check sufficient points have been specified for pump curves of units in the pumping station. Replace pumps in station with more suitable units.
836
PST operates on ZERO FLOW - Head too high
Info
Name of the pumping station. Head from first entry of pump curve / pumping station curve.
Cause
Head required cannot be provided with the existing pumps in the pumping station.
Advice
Check for hydraulic restrictions downstream of pump. Check pump curves of units in the pumping station. Replace pumps in station with more suitable units.
837
PST OFF by Pressure Control
Info
Name of the pumping station. Old and new STATUS of all pumps.
Cause
The pumping station is switched off because pressure at the control node is outside the limits specified in the pumping station control data (Pressure On and Pressure Off).
Advice
Probably no action required. Examine the control policy if this event was unexpected.
838
PST ON by Pressure Control
Info
Cause
The pumping station has been switched on. Pressure at the control node has returned within the bounds set in the control data for this node (Pressure On and Pressure Off).
Advice
850
Node isolated, Demand DELETED
Info
Name of node. Demand deleted from this node.
Cause
All demand assigned to this node will be deleted because the node is isolated from the rest of the network.
Advice
852
Transfer CANCELLED - Node isolated
Info
Name of node. Demand assigned to node.
Cause
All demand assigned to this transfer node will be deleted because the node is isolated from the rest of the network.
Advice
This may be intentional. If not, you must fix the error that has left this transfer node isolated.
854
FLOW change to meet DEMAND/TRANSFER
Info
The name of both end nodes of the pump, flow specified from PST, new flow value.
Cause
Flow required by demand/transfer differs from that specified in flow profile for PST in FLOW control mode.
Advice
Check that FLOW control mode is the correct control mode for the PST or check if the demand area/transfer is isolated from alternative supplies.
855
Demand suppressed by pipe closures
Info
Number of nodes.
Cause
Demand cannot be met due to closed pipes isolating demand nodes.
Advice
This may be intentional. If not, you must fix the error that has left these nodes isolated. To view node names of isolated nodes, choose to "Show imagessages for all isolated nodes with demand" in the Simulation Options dialog when running a simulation.
856
Pipe Closed
Info
The name of both end nodes of the pipe
Cause
The pipe has been closed as scheduled.
Advice
857
Pipe reopened
Info
Cause
The pipe has been opened as scheduled.
Advice
858
Link - Time Closures replicated for next day
Info
Name of link
Cause
May occur if a simulation is run over a time period greater than 24 hours. Time varying link controls specified for 24 hours or less will be replicated for the following day.
Advice
861
PST - Time Profile replicated for next day
Info
Name of pumping station
Cause
May occur if a simulation is run over a time period greater than 24 hours. Time varying pump controls specified for 24 hours or less will be replicated for the following day.
Advice
862
VALVE - Time Profile replicated for next day
Info
Name of valve
Cause
May occur if a simulation is run over a time period greater than 24 hours. Time varying valve controls specified for 24 hours or less will be replicated for the following day.
Advice
863
TRANSFER - Time Profile replicated for next day
Info
Name of node
Cause
May occur if a simulation is run over a time period greater than 24 hours. Time varying transfer node controls specified for 24 hours or less will be replicated for the following day.
Advice
864
Fix.Head - Time Profile replicated for next day
Info
Name of fixed head node
Cause
May occur if a simulation is run over a time period greater than 24 hours. Time varying fixed head node controls specified for 24 hours or less will be replicated for the following day.
Advice
865
!! SOLUTION INVALID (Iteration, Max.error, Node)
Info
Number of iterations reached, Maximum Error, Node name at which maximum error occurred.
Cause
InfoWorks WS could not compute solution for timestep.
Advice
Review system operation and control policy.
870
Calibration
Info
Time, number of calibration steps taken, calibration factor applied at step, sum of fractional differences between calculated and measured pressures and flows
Cause
A calibration run type has been carried out.
Advice
For information only, No action required.
871
Watsed: Invalid combination of Sediment Density and Diameter
Info
None
Cause
The pipe sedimentation calculations are based on the well established Ackers-White theory for sedimentation modelling. The dimensionless grain size is outside the range of application for the Ackers-White model.
Advice
Review sediment density and diameter values.
952
!! INVALID SNAPSHOTS
Info
Number of timesteps
Cause
InfoWorks WS could not compute solution for number of timesteps.
Advice
1005
Electric Tariffs file missing/not used
Info
None
Cause
An Electricity Tariff file has not been selected for use in the Hydraulic Run Schedule.
Advice
1114
PST not found in the control - will be shut off
Info
Cause
The Control Set does not contain any data for this pumping station. InfoWorks WS assumes that the pumping station is switched off for the duration of the simulation.
Advice
You can do this if you want, but it is probably less confusing to create control data for the pumping station, and explicitly set all pumps to OFF.
2000
The rtc/upc definitions for this event contain errors. See above for details.
Info
UPC error messages displayed in run log above error message.
Cause
There are errors in the UPC scenario used to run the simulation
Advice
Check that the correct UPC scenario has been used.
2001
Cannot create results file
Info
None
Cause
May occur due to disk space problems. May occur if the working folder is on a server and there are network problems.
Advice
Check for adequate disk space. Check for possible network problems.
2002
Cannot write summary to results file
Info
None
Cause
Advice
2003
Cannot write results at time
Info
Simulation time step
Cause
Advice