The Distribution Systems table defines distribution systems that are available in your project.
-  Name - A unique name that identifies a distribution system.
- Phase - Either Three or Single, selected from the drop-down list
- Configuration - After you click the value, you can select Wye or Delta, from the drop-down list (three-phase systems only).
- Wires - This parameter specifies to the number of conductors (3 or 4 for three-phase, 2 or 3 for single-phase). This affects the read only parameter of Connected Phases on electrical components.
-  L-L Voltage - After you click the value, you can select a Voltage Definition that represents the voltage measured between any two phases. The specification of this parameter depends on the Phase and Wire selections. For example, L-L Voltage is not applicable for a single-phase, 2-wire system.
-  L-G Voltage - After you click the value, you can select a Voltage Definition that represents the voltage measured between a phase and ground. L-G is always available.
- High Leg Phase - When a 4 wire Delta Configuration is selected, set which phase is the High Leg Phase. The High-Leg setting will only impact analytical systems.
Click Add and enter parameters to specify a new distribution system. Click Delete to remove a selected distribution system. You cannot delete a distribution system that is currently assigned to a device in a project.