Select Links to be included in Analysis
Selection List (drop target)
Use drag and drop or the Browse button to add a
selection list of potentially critical links to be analysed.
Browse
Click to open a dialog from which you can choose a run.
Clear
Click to clear the entry in the Run box.
Analysis Criteria
Minimum Pressure and
Duration
If the pressure in the network falls below minimum pressure for at least the duration period during the simulation, the test link will be considered to be a critical main and results for that link will be saved.
Maximum Pressure
and
Duration
If the pressure in the network exceeds Maximum pressure for at least the duration specified, the test link will be considered to be a critical main and results for that link will be saved.
Event Demand Efficiency
If the average ratio of actual to nominal demand during the simulation is less than the Actual/Nominal Demand specified, the test link will be considered to be a critical main and results for that link will be saved.
Failure Count Type
Set the item type at which failures are to be assessed:
If the number of items affected by the pipe failure is less than the specified number in the
Ignore if count is less thanfield, the failure will be ignored.
Nodes to exclude from Analysis
selection list of nodes to be excluded in the analysis of potentially critical links.
These nodes will not be checked against the minimum pressure, maximum pressure and actual/nominal demand criteria. This may result in a test link passing analysis, which may have failed if nodes had not been excluded.
| Single Pipe of Isolation Area
Select whether a single link or a group of links in an isolation area is to be closed for analysis.
Close single link for each test
Each link included in the
Select Links to be included in Analysis selection list will be closed separately and a simulation run. There will be one simulation run per selected link.
Close isolation area for each test
For each isolation area code found in the
Select Links to be included in Analysis selection list, all links in the isolation area will be closed and a simulation run. There will be one simulation run per isolation area.
Link Outage Period
Whole Simulation
Link outage will be applied throughout the simulation.
Start at Peak Network Demand
Link outage will start at peak network demand determined using the
demand diagram used in the run.
Start at:
Enter a start date and time for link outage. This time must be within the run start and end times.
Duration of outage
The outage period for the test link. This field is used when using the
Start at Peak Network Demand and
Start at: Date-Time
options only.
Report to end of Outage Period only
Check this box to save simulation results for critical links from the start of the simulation until the end of the link outage period only.
| Leakage Options
Include leakage (bursting) in link outage
Check this box to include leakage representing a burst at the midpoint of the test link from the start of the outage period for the leakage duration.
(Only enabled when using the
Close single link for each test option.)
Leakage Flow of [100mm Pipe] at [50m] Pressure [units]
Leakage rate for a reference pipe of 100 mm diameter at 50 m pressure.
For each test link the leakage rate is scaled as a function of test link diameter divided by reference diameter.
Leakage is determined by actual pressure / standard pressure using standard orifice behaviour.
Q
=Cd
A (2gH)0.5
where
Q is Discharge
Cd is Discharge Coefficient
A is cross-sectional area of pipe
g is acceleration due to gravity
H is effective Head
The calculated leakage is applied equally at the test link end nodes and is added to any existing leakage demand. In the case where one of the test link end nodes is not a basic node, the calculated leakage is not divided between the end nodes, but is applied to the basic node only.
Leakage Duration (mins)
Allow Pipe Flow during Leakage Period
Check this box to allow flow through the test link from the start of the outage period for the
Leakage Duration.
If this box is unchecked, the test link will be assumed to be closed.
Discard time varying results
Check this box to cause time varying results to be discarded. This will save a lot of space if the summary is the only item of interest.
If this box is checked, the run is only of use in updating criticality: when the base simulation is opened it will not attempt to open the service level report and a message will explain this.
You update criticality by using the
Update criticality option on the
Network menu. See Update Criticality dialog.
| Criticality criteria options
Click to view and modify the criteria to be used when determining criticality grades. See
Criticality Criteria dialog.
| Service level report options
Click to view and modify the settings to be used for the Service Level Summary report. See
Service Level Summary dialog.
| Test cases per thread (parallel processing)
The simulation will run for a certain number of test cases.
The ideal is to split these exactly between the available processor cores (for example, if there are 200 test cases on an eight-core machine, the ideal setting would be 25 test cases per thread).