Fixed Head Node Data Fields
Fixed Head Node data fields can be edited on the Fixed Head Node Grid View of the Nodes Grid or the Fixed Head Property Sheet.
The following table describes all the Fixed Head Node specific data needed to define a Fixed Head Node.
Further information, including units details, about all the Network Object fields stored in the database can be found in the data fields topics listed in the Network Data Fields topic.
Fields that are common to the majority of objects can be found in the Common Data Fields topic.
The pages on the Property Sheet are listed below. When the network object has Control Data additional pages may be displayed on the property sheet. These pages are marked as follows:
- additional page displayed when Control Data is open
  1. Node Definition Page
  2. User Page - see Common Data Fields topic for details of user fields
  3. Hyperlinks Page - see Common Data Fields topic for details of hyperlinks fields
  4. Notes Page - see Common Data Fields topic for details of notes fields
  5. Fixed Head Control Page
  6. Node Control Page
  7. Water Quality Profile Page
  8. Water Quality Turbidity Profile
  9. Water Quality Age Profile Page
  10. Transient - Pressure Page - fields only enabled when InfoWorks TS (Transient System) licence is present
  11. Control Notes Page
The Grid column tells you if the data item is available for editing in the grid view.
Note: Use the scroll bar at the bottom of the table to view its entire content.
Database Table Name: wn_fixed_head
Field Name
Help Text
Flag
Grid
Property Page
Size
Precision
Units
Database Field
Data Type
Default
Error Lower Limit
Error Upper Limit
Warning Lower Limit
Warning Upper Limit
Node ID
Name of the node
YES
YES
1
30
0
node_id
Text
Area Code
The Area Code parameter is used for closer spatial modelling of demand - each node is allocated to an area and demand can then be factored by area.
The factor is set using the Demand Scaling Editor.
YES
YES
1
30
0
area
Text
Asset ID
For reference only. Designed as a reference to an asset database, but could be used for anything.
YES
YES
1
30
0
asset_id
Text
Fire Zone
The Fire Zone field is used when checking minimum pressure constraints during Hydrant Testing simulations. Different pressure constraints may be applied to nodes in a given Fire Zone to nodes outside of the Fire Zone. See Fire Flow Data for more details.
YES
YES
1
30
0
fire_zone
Text
System Type
For information. Type in a system type or select an option from the dropdown list:
Database Value
Description
Help Text
POTABLE
Potable
System used to transport water of a quality suitable for drinking.
RAW
Raw
System used to transport water used as a source supply for potable water before it has been treated.
RECYCLED
Recycled
System used to transport wastewater effluent that has been treated to provide a non-potable supply suitable for uses such as irrigation.
YES
YES
1
40
0
system_type
Text
Isolation Area
Area identifier used to identify groups of objects to be closed when carrying out a Critical Link Analysis.
YES
YES
1
30
0
isolation_area
Text
X
X coordinate
YES
YES
1
2
XY
x
Double
Y
Y coordinate
YES
YES
1
2
XY
y
Double
Elevation
Elevation above datum of pipe invert.
YES
YES
1
2
Z
z
Double
-999
9999
Ground Level
Elevation above datum of ground surface.
YES
YES
1
2
Z
ground_level
Double
-999
9999
Highest Property Level
Elevation above datum level of the highest property supplied by the node
YES
YES
1
2
Z
highest_property
Double
-999
9999
InfoNet Unique ID
The InfoNet Unique ID and InfoNet Network ID are unique identifiers associated with the corresponding object and network in an InfoAssetdatabase. When importing from InfoNet, these identifiers can be copied from the InfoNet database in order to maintain links between the two networks.
YES
YES
NO
0
asset_uid
GUID
InfoNet Network ID
See InfoNet Unique ID
NO
YES
NO
0
asset_network_uid
GUID
Fixed Head Node Control Data
Database Table Name: wn_ctl_fixed_head
Field Name
Help Text
Flag
Grid
Property Page
Size
Precision
Units
Database Field
Data Type
Default
Error Lower Limit
Error Upper Limit
Warning Lower Limit
Warning Upper Limit
Constant Head
Fixed Water Level
YES
YES
5
2
Z
fixed_level
Double
Date-Time/Head Grid
The Head Grid allows you to edit a list of head against date/time values. The Head Grid can only be viewed and edited on the Fixed Head Control Page and is fully described there.
Database Table Name: wn_ctl_level_profile
Position in Data Structure
Field Name
Help Text
Flag
Size
Units
Database Table
Database Field
Type
Default
Error Lower Limit
Error Upper Limit
Warning Lower Limit
Warning Upper Limit
1
Date & Time
Date and time value
YES
date_time
2
Head
Water level at this date and time
NO
Z
water_level
Double
-999
9999
NO
YES
5
0
levels
Array
Linear Profile
This checkbox decides if values in the profile grid are interpolated.
  • checked - linear interpolation is carried out between values
  • unchecked - The value entered in the grid changes at each time point, and is maintained until the next time point is reached.
YES
YES
5
0
linear_levels_profile
Boolean
1
Before First Point (fixed head control)
Database Value
Description
Help Text
0
Extend Back
The first value in the profile grid is extended back to the start of the simulation (and repeat period for repeated profiles).
1
Extrapolate Back
Applies to Linear Profiles only: the first two values in the profile grid are used to extrapolate back to the start of the simulation (and repeat period for repeated profiles).
(If Extrapolate Back is selected for a non linear profile, the profile will be extended back.)
2
Zero/Unchanged
A value of zero or "off" is applied from the start of the simulation until the date / time of the first value in the profile grid (and from the start of the repeat period for repeated profiles).
YES
YES
5
0
before_levels_profile
Integer
1
After Last Point (fixed head control)
Database Value
Description
Help Text
0
Extend Forward
The last value in the profile grid is extended to the end of the simulation or repeat period.
1
Extrapolate Forward
Applies to Linear Profiles only: the last two values in the profile grid are used to extrapolate forward to the end of the simulation or repeat period.
(If Extrapolate Forward is selected for a non linear profile, the profile will be extended forward.)
YES
YES
5
0
after_levels_profile
Integer
0
Repeat Profile (fixed head control)
Check the Repeat Profile box to repeat a profile (from 00:00 for the selected Repeat Period) for the duration of the simulation.
Note:
When using the Repeat Profile option; if the defined profile spans over the selected Repeat Period, the profile will not be repeated.
YES
YES
5
0
repeat_levels_profile
Boolean
1
Repeat Period (fixed head control)
Profile period which will be repeated throughout simulation, if the Repeat Profile box is checked.
Database Value
Description
Help Text
0
1 day
Repeat Period
1
1 week
Repeat Period
2
2 weeks
Repeat Period
YES
YES
5
0
repeat_levels_period
Integer
0
Live Data Point ID
Name of the associated Live Data Point, Live Data Feed, or Live Data Composite Feed.
Note: Duplicate IDs are shown once.
YES
YES
6
100
0
live_data_point_id
Text
Initial Concentration
The initial concentration of the substance being tested at the start of the simulation. Only one substance can be tested at a time.
These nodes are inputs to the system. The Initial Concentration represents a continuous input concentration over the period of the simulation.
If you have defined a time dependent concentration for a node, the time dependent concentration overrides this value between its start and end times.
YES
YES
7
2
WN_C
initial_concentration
0
9999
SourceType
Method by which concentration profile defined in the Water Quality grid is applied during the simulation.
Database Value
Description
Help Text
0
Fixed Concentration
Concentration at a node is set to the profile defined in the Water Quality grid.
Use a concentration value of < 0 in the profile to switch off the concentration source and allow inflow from upstream pipes to set concentration at the node.
1
Additional Concentration
Concentration profile defined in the Water Quality grid is applied to water leaving the node in addition to the calculated concentration.
2
Concentration Booster
Concentration in water leaving the node is set to the profile defined in the Water Quality grid (provided that the concentration calculated during the simulation is less than the defined concentration).
3
Additional Mass Flow
Mass Flow profile defined in the Water Quality grid is applied to water leaving the node in addition to the calculated concentration.
YES
YES
7
0
wq_source_type
Integer
0
Initial Age of Water (hr)
Age of water at the start of the simulation
YES
YES
7
2
initial_age
Double
0
Date-Time/Concentration Grid
The concentration of pollutant entering the system at this node between the Water Quality start and end times. This concentration does not depend on flow rate. These values can be interpolated, depending on the state of the Linear WQ Profile check box.
Database Table Name: wn_ctl_node_wq_conc
Field Name
Help Text
Flag
Size
Units
Database Table
Database Field
Type
Default
Error Lower Limit
Error Upper Limit
Warning Lower Limit
Warning Upper Limit
1
Date Time
The date and time at which the concentration value takes effect.
NO
wn_ctl_node_wq_conc
wqc_date_time
2
Conc.
The concentration of pollutant entering at this node at this time
NO
WN_C
wn_ctl_node_wq_conc
wqc_concentration
0.0
9999
NO
YES
7
0
wq_profile
Array
Date-Time/Mass Flow Grid
Mass flow profile grid displayed when Additional Mass Flow is selected in the Source Type field.
Database Table Name: wn_ctl_node_wq_flow
Field Name
Help Text
Flag
Size
Units
Database Table
Database Field
Type
Default
Error Lower Limit
Error Upper Limit
Warning Lower Limit
Warning Upper Limit
1
Date Time
The date and time at which the mass flow value takes effect.
NO
wn_ctl_node_wq_flow
wqf_date_time
2
Mass Flow
The mass flow rate of pollutant entering at this node at this time
NO
WN_MF
wn_ctl_node_wq_flow
wqf_additional_mass
0.0
0
9999
NO
YES
7
0
wq_flow_profile
Array
Linear WQ/Age Profile
YES
YES
7
0
linear_wq_profile
Boolean
0
Before First Point (water quality profile)
Database Value
Description
Help Text
0
Extend Back
1
Extrapolate Back
2
Zero/Unchanged
YES
YES
7
0
before_wq_profile
Integer
2
After Last Point (water quality profile)
Database Value
Description
Help Text
0
Extend Forward
1
Extrapolate Forward
YES
YES
7
0
after_wq_profile
Integer
0
Repeat Profile (water quality profile)
Note:
YES
YES
7
0
repeat_wq_profile
Boolean
0
Repeat Period (water quality profile)
Database Value
Description
Help Text
0
1 day
Repeat Period
1
1 week
Repeat Period
2
2 weeks
Repeat Period
YES
YES
7
0
repeat_wq_period
Integer
0
Bulk Coeff Mode
Method by which Bulk Coefficient is applied to water entering the system at the node:
Database Value
Description
Help Text
0
Not active
Bulk coefficient for the node is not applied to water entering the system at the node.
WQ bulk coefficient values specified at individual pipes will be used to calculate change in concentration.
1
Replace
The Bulk coefficient specified at the node will override the WQ bulk coefficient values specified at individual pipes when calculating change in concentration.
2
Scale
The Bulk coefficient specified at the node will be applied as a multiplying factor to WQ bulk coefficient values specified at individual pipes.
YES YES 7 0 wq_bulk_coeff_mode Integer 0
Bulk Coeff
Reaction rate parameter used to calculate the change in concentration of a substance as it reacts with material in the bulk flow.
The value specified here is applied to water entering the system at the node.
The bulk coefficient has a positive value if the concentration of the substance grows over time, and a negative value if the concentration decays over time.
YES YES 7 2 wq_bulk_coeff Double 0
Res Bulk Coeff Mode
Method by which Res Bulk Coefficient is applied to water entering the system at the node:
Database Value
Description
Help Text
0
Not active
Res bulk coefficient for the node is not applied to water entering the system at the node.
WQ reaction coefficient values specified at individual reservoirs will be used to calculate change in concentration.
1
Replace
The Res bulk coefficient specified at the node will override the WQ reaction coefficient values specified at individual reservoirs when calculating change in concentration.
2
Scale
The Res bulk coefficient specified at the node will be applied as a multiplying factor to WQ Reaction coefficient values specified at individual reservoirs.
YES YES 7 0 wq_res_bulk_coeff_mode Integer 0
Res Bulk Coeff
Reaction rate parameter used to calculate the change in concentration of a substance as it reacts with material in a reservoir.
YES YES 7 2 wq_res_bulk_coeff Double 0
Initial Turbidity
Initial turbidity at node at start of simulation.
See Water Quality - Turbidity Analysis for further information.
YES YES 8 2 WN_TURBIDITY wq_initial_turbidity Single 0 9999
Turbidity Source Type
Method by which turbidity profile defined in the Turbidity grid is applied during the simulation.
Database Value
Description
Help Text
0
Fixed Turbidity
Turbidity at node is set to the profile defined in the Turbidity grid.
Use a turbidity value of < 0 in the profile to switch off the turbidity source and allow turbidity from upstream pipes to set turbidity at the node.
1
Additional Turbidity
Turbidity profile defined in the Turbidity grid is applied to water leaving the node in addition to the calculated turbidity.
YES NO 8 0 wq_turb_source_type Integer 0
Turbidity Profile
Database Table Name: wn_ctl_node_wq_turb
A series of time / turbidity pairs that define the turbidity profile at the node. These values can be interpolated, depending on the state of the Linear Profile flag.
Field Name
Help Text
Flag
Size
Units
Database Table
Database Field
Type
Default
Error Lower Limit
Error Upper Limit
Warning Lower Limit
Warning Upper Limit
1
Date Time
Date and time value
YES
wn_ctl_node_wq_turb
wqt_date_time
Date/Time
2
Turbidity
Turbidity at node
YES
WN_TURBIDITY
wn_ctl_node_wq_turb
wqt_turbidity
Single
0.0
9999
NO NO 8 0 wq_turbidity_profile Array
Linear Turbidity Profile
This checkbox decides if values in the Turbidity profile grid are interpolated:
YES NO 8 0 wq_turb_linear_profile Boolean 0
Before First Point (Turbidity)
Database Value
Description
Help Text
0
Extend Back
1
Extrapolate Back
2
Zero/Unchanged
YES NO 8 0 wq_turb_before_profile Integer 2
After Last Point (Turbidity)
Database Value
Description
Help Text
0
Extend Forward
1
Extrapolate Forward
YES NO 8 0 wq_turb_after_profile Integer 0
Repeat Profile (Turbidity)
Note:
YES NO 8 0 wq_turb_repeat_profile Boolean 0
Repeat Period (Turbidity)
Database Value
Description
Help Text
0
1 day
Repeat Period
1
1 week
Repeat Period
2
2 weeks
Repeat Period
YES NO 8 0 wq_turb_repeat_period Integer 0
Enable Surge
A change in pressure at the fixed head will produce a transient.
Check this option to enable Transient Simulation fields.
YES YES 9 iwts_enable_surge_SPD Boolean
Time/Pressure grid
Transient Simulation field.
Profile defining pressure variation at the well at a time relative to the start of the simulation.
Database Table Name: wn_ctl_iwts_surge_pres_tme
Field Name
Help Text
Flag
Size
Units
Database Table
Database Field
Type
Default
Error Lower Limit
Error Upper Limit
Warning Lower Limit
Warning Upper Limit
1
Time
The time (relative to the start of the simulation) at which the pressure value takes effect.
NO
time
Double
0.0
2
Pressure
The pressure at the node at the corresponding time
NO
WN_P
pressure
Double
0.0
NO NO 9 iwts_surge_pressure_time Array
Notes
You can keep freeform notes about any object in your network. The notes field can be up to 64,000 characters in size, or about 10 pages of printed text.
NO
YES
10
0
notes
Memo
Node ID
Name of the node
YES
YES
1
30
0
node_id
Text
Asset ID
YES
YES
1
30
asset_id
Text
Time Dependent Concentration
This field is obsolete and is not displayed in the interface. This data is now entered in the Water Quality Grid.
The field is maintained for backwards compatibility with old CSV data files. If this value is set when the data is imported, InfoWorks will calculate appropriate values for the Water Quality Grid.
YES
YES
NO
2
WN_C
time_related_concentration
0
9999
WQ Start Date & Time
YES
YES
NO
0
wq_start_date_time
WQ End Date & Time
YES
YES
NO
0
wq_end_date_time
Exceptional Flow
A read only check box displayed only on the grid view. This box is checked if data has been entered in the Exceptional Flow Grid on the property sheet
NO
YES
NO
0
exf_selected
Boolean
Water Quality
A read only check box displayed only on the grid view. This box is checked if data has been entered in the Water Quality Grid on the property sheet
NO
YES
NO
0
wqc_selected
Boolean
Fixed Head Node Results
Results fields are displayed on the grid when opened while viewing a replay of a simulation, and on a special results page placed at the front of Property Sheets displayed while viewing a simulation replay.
For details of results fields for nodes, see the Node Results Data Fields topic.