Meter data fields can be edited on the Meter Grid View of the Links Grid or the Meter Property Sheet.
The following table describes all the Meter specific data needed to define a Meter.
Further information, including units details, about all the Network Object fields stored in the database can be found in the data fields topics listed in the Network Data Fields topic.
Fields that are common to the majority of objects can be found in the Common Data Fields topic.
The pages on the Property Sheet are listed below. When the network object has Control Data additional pages may be displayed on the property sheet. These pages are marked as follows:
- additional page displayed when
Control Data is open
The Grid column tells you if the data item is available for editing in the grid view.
Database Table Name: wn_meter
Field Name |
Help Text |
Flag |
Grid |
Property Page |
Size |
Precision |
Units |
Database Field |
Data Type |
Default |
Error Lower Limit |
Error Upper Limit |
Warning Lower Limit |
Warning Upper Limit |
From Node ID |
Name of the From Node for this pipe. You can select the name from the dropdown list of existing nodes, or type the name of a node you have yet to add to the model. From and To represent the typical direction of flow for the pipe. Flow will not always be in this direction. |
YES |
YES |
1 |
30 |
0 |
us_node_id |
Text |
To Node ID |
Name of the To Node for this pipe. From and To represent the typical direction of flow for the pipe. Flow will not always be in this direction. |
YES |
YES |
1 |
30 |
0 |
ds_node_id |
Text |
Suffix |
A suffix added by InfoWorks to ensure that all link Ids are unique |
YES |
YES |
NO |
1 |
0 |
link_suffix |
Text |
Area Code |
The Area Code parameter is used for closer spatial modelling of demand - each node is allocated to an area and demand can then be factored by area. The factor is set using the Demand Scaling Editor. |
YES |
YES |
1 |
30 |
0 |
area |
Text |
Asset ID |
For reference only. Designed as a reference to an asset database, but could be used for anything. |
YES |
YES |
1 |
30 |
0 |
asset_id |
Text |
Local Loss Coefficient |
Local Headloss Coefficient used by the Darcy Weisbach roughness formula |
YES |
YES |
1 |
4 |
local_loss |
0 |
10000000000 |
Length |
The length of the pipe. |
YES |
YES |
1 |
2 |
L |
length |
0.1 |
99000 |
Diameter |
Internal diameter of the pipe |
YES |
YES |
1 |
1 |
PS |
diameter |
10 |
20000 |
Friction Type |
The formula used for roughness calculations. Can be Darcy Weisbach, Hazen Williams, Colebrook White, or Modified Hazen-Williams. See Pipe Calculations for more information.
YES |
YES |
1 |
2 |
1 |
roughness_type |
Text |
CW - k |
The value for the friction coefficient appropriate to the chosen roughness type. Follow the links above for more details |
YES |
YES |
1 |
6 |
WN_K |
k |
0.001 |
200 |
DW - f |
YES |
YES |
1 |
6 |
darcy_weissbach |
0.002 |
0.09 |
HW - c |
YES |
YES |
1 |
1 |
hazen_williams |
20 |
5000 |
50 |
200 |
Material |
Link material. For reference only. |
YES |
YES |
1 |
10 |
0 |
material |
Text |
Year |
Year of installation. For reference only. |
YES |
YES |
1 |
0 |
year |
Integer |
WQ Bulk Coefficient |
The bulk coefficient, kb, is a reaction rate parameter used to calculate the change in concentration of a substance as it reacts with material in the bulk flow. The bulk coefficient has a positive value if the concentration of the substance grows over time, and a negative value if the concentration decays over time. Note:
Source dependent bulk coefficient values may be specified at individual nodes which may override or scale the pipe Bulk Coefficient value when calculating reaction rates for water that entered the system at the node.
YES |
YES |
1 |
2 |
bulk_coeff |
-0.5 |
-10 |
10 |
WQ Wall Coefficient |
The wall coefficient, kw, is a reaction rate parameter used to calculate the change in concentration of a substance as it reacts with material along the pipe walls. The wall coefficient has a positive value if the concentration of the substance grows in time, and a negative value if the concentration decays in time. |
YES |
YES |
1 |
2 |
wall_coeff |
-0.3 |
-10 |
10 |
Criticality |
The criticality grade of the link. This provides an indication of the significance of the effect on the network if the link fails. This field may be updated from a Critical Link Analysis simulation. |
YES |
YES |
1 |
0 |
criticality |
Integer |
Wave Celerity |
Velocity of propagation of pressure waves caused by sudden increase or decrease in flow rate. See Transients Advisor for more details. |
YES |
YES |
1 |
V |
wave_celerity |
1400 |
Criticality Count |
Number of items (Nodes, Properties, Customer Points or Connections) assessed as critical in the event of link failure. This field may be updated from a Critical Link Analysis simulation. |
YES |
YES |
1 |
0 |
criticality_count |
Integer |
Pressure Rating |
Maximum design working pressure of link |
YES |
YES |
1 |
WN_P |
pressure_rating |
System Type |
For information. Type in a system type or select an option from the dropdown list:
YES |
YES |
1 |
40 |
0 |
system_type |
Text |
Isolation Area |
Area identifier used to identify groups of objects to be closed when carrying out a Critical Link Analysis. |
YES |
YES |
1 |
30 |
0 |
isolation_area |
Text |
Meter Diameter |
The internal diameter of the meter |
YES |
YES |
2 |
0 |
PS |
meter_diameter |
10 |
20000 |
Loss Coeff |
The local loss coefficient of the meter, used to represent the losses caused by the meter measuring apparatus, such as a turbine blade. |
YES |
YES |
2 |
4 |
loss_when_open |
0 |
10000 |
Construction Type |
Construction Type is another descriptive field that gives further information on metering method and construction. This is useful for future advanced maintenance and asset management reporting. There are a number of built in construction types available, and you can add your own user defined types. See Meter Construction Types. |
YES |
YES |
2 |
10 |
0 |
construction_type |
Text |
Meter Id |
This field can be used to link the meter data to a corporate billing system. This gives you the opportunity to provide real consumption and flow figures. These figures are at present mostly derived using demographic tools based on, for example, the number of people, property count and specific consumption |
YES |
YES |
2 |
30 |
0 |
billing_id |
Text |
Bends |
This field defines the geometry of the link. The underlying data consists of a series of (x,y) pairs defining the vertices of the link. Each link is made up of a series of straight lines between the defined (x,y) points. This data is not displayed on the grid or property sheet. Link vertices are included when you export link data to CSV files. There are two options available for exporting link vertices. These are selected on the Select CSV Export Options dialog using the Coordinate Arrays Format dropdown list. The options are:
NO |
YES |
NO |
0 |
XY |
bends |
Array |
From Node ID |
YES |
YES |
1 |
30 |
0 |
us_node_id |
Text |
To Node ID |
YES |
YES |
1 |
30 |
0 |
ds_node_id |
Text |
Suffix |
YES |
YES |
NO |
1 |
0 |
link_suffix |
Text |
Area Code |
YES |
YES |
1 |
30 |
0 |
area |
Text |
Asset ID |
YES |
YES |
1 |
30 |
0 |
asset_id |
Text |
YES |
YES |
1 |
4 |
local_loss |
0 |
10000000000 |
Length |
YES |
YES |
1 |
2 |
L |
length |
0.1 |
99000 |
Diameter |
YES |
YES |
1 |
1 |
PS |
diameter |
10 |
20000 |
Friction Type |
The formula used for roughness calculations. Can be Darcy Weisbach, Hazen Williams, or Colebrook White. See Pipe Calculations for more information.
YES |
YES |
1 |
2 |
1 |
roughness_type |
Text |
CW - k |
YES |
YES |
1 |
6 |
WN_K |
k |
0.001 |
200 |
DW - f |
YES |
YES |
1 |
6 |
darcy_weissbach |
0.002 |
0.09 |
HW - c |
YES |
YES |
1 |
1 |
hazen_williams |
20 |
5000 |
50 |
200 |
Material |
YES |
YES |
1 |
10 |
0 |
material |
Text |
Year |
YES |
YES |
1 |
0 |
year |
Integer |
The bulk coefficient, kb, is a reaction rate parameter used to calculate the change in concentration of a substance as it reacts with material in the bulk flow. The bulk coefficient has a positive value if the concentration of the substance grows over time, and a negative value if the concentration decays over time. |
YES |
YES |
1 |
2 |
bulk_coeff |
-0.5 |
-10 |
10 |
The wall coefficient, kf, is a reaction rate parameter used to calculate the change in concentration of a substance as it reacts with material along the pipe walls. The wall coefficient has a positive value if the concentration of the substance grows in time, and a negative value if the concentration decays in time. |
YES |
YES |
1 |
2 |
wall_coeff |
-0.3 |
-10 |
10 |
Criticality |
YES |
YES |
1 |
0 |
criticality |
Integer |
Wave Celerity |
YES |
YES |
1 |
V |
wave_celerity |
1400 |
Criticality Count |
YES |
YES |
1 |
0 |
criticality_count |
Integer |
Pressure Rating |
YES |
YES |
1 |
WN_P |
pressure_rating |
InfoNet Unique ID |
The InfoNet Unique ID and InfoNet Network ID are unique identifiers associated with the corresponding object and network in an InfoAsset database. When importing from InfoAsset, these identifiers can be copied from the InfoAsset database in order to maintain links between the two networks. |
YES |
YES |
NO |
0 |
asset_uid |
GUID |
InfoNet Network ID |
See InfoNet Unique ID |
NO |
YES |
NO |
0 |
asset_network_uid |
GUID |
Database Table Name: wn_ctl_meter
Field Name |
Help Text |
Flag |
Grid |
Property Page |
Size |
Precision |
Units |
Database Field |
Data Type |
Default |
Error Lower Limit |
Error Upper Limit |
Live Data Point ID |
Name of the associated Live Data Point, Live Data Feed, or Live Data Composite Feed. Note: Duplicate IDs are shown once.
YES |
YES |
4 |
100 |
0 |
live_data_point_id |
Text |
PoW Unit Cost (from - to) |
Cost per cubic metre, in user defined currency units, of transferring water between the From Node and To Node. Prices can be negative to allow for exports or bulk water sale. |
YES |
YES |
4 |
2 |
WN_VCOST |
usds_pow_cost |
PoW Category (from - to) |
The category into which this cost falls, for flow between the From Node and To Node.
YES |
YES |
4 |
16 |
0 |
usds_pow_cat |
Text |
PoW Unit Cost (to - from) |
Cost per cubic metre, in user defined currency units, of transferring water between the To Node and From Node. Prices can be negative to allow for exports or bulk water sale. |
YES |
YES |
4 |
2 |
WN_VCOST |
dsus_pow_cost |
PoW Category (to - from) |
The category into which this cost falls, for flow between the To Node and From Node.
YES |
YES |
4 |
16 |
0 |
dsus_pow_cat |
Text |
Pipe Status |
You can set a time-varying profile for the pipe closed state in the grid. See Closed Pipes for more information The data in this grid is only used if the Pipe Closed checkbox is un-checked. Database Table Name: wn_ctl_pipe_status
YES |
YES |
5 |
0 |
status |
Array |
Pipe Closed |
The pipe is permanently closed if the box is checked |
YES |
YES |
5 |
0 |
pipe_closed |
Boolean |
Repeat Period |
Profile period which will be repeated throughout simulation, if the Repeat Profile box is checked.
YES |
YES |
5 |
0 |
repeat_status_period |
Integer |
0 |
Repeat Profile |
Check the Repeat Profile box to repeat a profile (from 00:00 for the selected Repeat Period) for the duration of the simulation. Note: When using the Repeat Profile option; if the defined profile spans over the selected Repeat Period, the profile will not be repeated.
YES |
YES |
5 |
0 |
repeat_status |
Boolean |
1 |
| Maximum Shear Strength |
The maximum value for the corrosion layer shear strength on the pipe wall. The maximum value for which the hydraulic shear strength will result in material being eroded from the pipe wall. See Water Quality - Turbidity Analysis for further information. |
YES | YES | 6 | WN_STRESS | wq_max_shear_strength | Double | |||||||||||||||||||||||||||||||||||||||||||||||||
| Initial Shear Strength |
The initial value for the corrosion layer shear strength on the pipe wall. The hydraulic shear strength must rise above this initial value to begin the erosion of material from the pipe wall. See Water Quality - Turbidity Analysis for further information. |
YES | YES | 6 | WN_STRESS | wq_init_shear_strength | Double | |||||||||||||||||||||||||||||||||||||||||||||||||
| Erosion Coefficient |
Parameter used to calculate the quantity of material eroded from the pipe wall when the hydraulic shear stress exceeds the corrosion layer shear strength; the excess shear. See Water Quality - Turbidity Analysis for further information. |
YES | YES | 6 | WN_RATE | wq_erosion_coefficient | Double | |||||||||||||||||||||||||||||||||||||||||||||||||
| Erosion Exponent |
The power to which the ratio of excess shear to maximum shear strength is raised when calculating the quantity of material released from the pipe wall. A value of zero will be interpreted as meaning the erosion is independent of the excess shear. See Water Quality - Turbidity Analysis for further information. |
YES | YES | 6 | wq_erosion_exponent | Double | ||||||||||||||||||||||||||||||||||||||||||||||||||
| Release Coefficient |
Parameter used to calculate the increase in turbidity as a result of material eroded from the pipe wall. See Water Quality - Turbidity Analysis for further information. |
YES | YES | 6 | WN_TURBLEN | wq_release_coefficient | Double | |||||||||||||||||||||||||||||||||||||||||||||||||
Notes |
You can keep freeform notes about any object in your network. The notes field can be up to 64,000 characters in size, or about 10 pages of printed text. |
NO |
YES |
10 |
0 |
notes |
Memo |
From Node ID |
YES |
YES |
1 |
30 |
0 |
us_node_id |
Text |
To Node ID |
YES |
YES |
1 |
30 |
0 |
ds_node_id |
Text |
Suffix |
YES |
YES |
NO |
1 |
0 |
link_suffix |
Text |
Asset ID |
YES |
YES |
1 |
30 |
asset_id |
Text |
PoW |
Read only field that indicates if Price of Water data has been entered on the property sheet |
NO |
YES |
NO |
0 |
pow_selected |
Boolean |
| Pipe Break | Refer to Pipe Data Fields for more details. |
All results fields are displayed on the grid when opened while viewing a replay of a simulation, and on a special results page placed at the front of Property Sheets displayed while viewing a simulation replay.
For details of results fields for links, see the Link Results Data Fields topic.
