Valve data fields can be edited on the Valve Grid View or the Valve Property Sheet.
The following table describes all the data needed to define a Valve.
Further information, including units details, about all the Network Object fields stored in the database can be found in the data fields topics listed in the Network Data Fields topic.
Fields that are common to the majority of objects can be found in the Common Data Fields topic.
The pages on the Property Sheet are listed below. When the network object has Control Data additional pages may be displayed on the property sheet. These pages are marked as follows:
- additional page displayed when
Control Data is open
The Grid column tells you if the data item is available for editing in the grid view.
Database Table Name: wn_valve
Field Name |
Help Text |
Flag |
Grid |
Property Page |
Size |
Precision |
Units |
Database Field |
Data Type |
Default |
Error Lower Limit |
Error Upper Limit |
Warning Lower Limit |
Warning Upper Limit |
From Node ID |
Name of the From Node for this pipe. You can select the name from the dropdown list of existing nodes, or type the name of a node you have yet to add to the model. From and To represent the typical direction of flow for the pipe. Flow will not always be in this direction. |
YES |
YES |
1 |
30 |
0 |
us_node_id |
Text |
To Node ID |
Name of the To Node for this pipe. From and To represent the typical direction of flow for the pipe. Flow will not always be in this direction. |
YES |
YES |
1 |
30 |
0 |
ds_node_id |
Text |
Suffix |
A suffix added by InfoWorks to ensure that all link Ids are unique |
YES |
YES |
NO |
1 |
0 |
link_suffix |
Text |
Area Code |
The Area Code parameter is used for closer spatial modelling of demand - each node is allocated to an area and demand can then be factored by area. The factor is set using the Demand Scaling Editor. |
YES |
YES |
1 |
30 |
0 |
area |
Text |
Asset ID |
For reference only. Designed as a reference to an asset database, but could be used for anything. |
YES |
YES |
1 |
30 |
0 |
asset_id |
Text |
Local Loss Coefficient |
Local Headloss Coefficient used by the Darcy Weisbach roughness formula |
YES |
YES |
1 |
4 |
local_loss |
0 |
10000000000 |
Length |
The length of the pipe. |
YES |
YES |
1 |
2 |
L |
length |
0.1 |
99000 |
Friction Type |
The formula used for roughness calculations. Can be Darcy Weisbach, Hazen Williams, Colebrook White, or Modified Hazen-Williams. See Pipe Calculations for more information.
YES |
YES |
1 |
2 |
1 |
roughness_type |
Text |
CW - k |
The value for the friction coefficient appropriate to the chosen roughness type. Follow the links above for more details |
YES |
YES |
1 |
6 |
WN_K |
k |
0.001 |
200 |
DW - f |
YES |
YES |
1 |
6 |
darcy_weissbach |
0.002 |
0.09 |
HW - c |
YES |
YES |
1 |
1 |
hazen_williams |
20 |
5000 |
50 |
200 |
Material |
Link material. For reference only. |
YES |
YES |
1 |
10 |
0 |
material |
Text |
Year |
Year of installation. For reference only. |
YES |
YES |
1 |
0 |
year |
Integer |
WQ Bulk Coefficient |
The bulk coefficient, kb, is a reaction rate parameter used to calculate the change in concentration of a substance as it reacts with material in the bulk flow. The bulk coefficient has a positive value if the concentration of the substance grows over time, and a negative value if the concentration decays over time. Note:
Source dependent bulk coefficient values may be specified at individual nodes which may override or scale the pipe Bulk Coefficient value when calculating reaction rates for water that entered the system at the node.
YES |
YES |
1 |
2 |
bulk_coeff |
-0.5 |
-10 |
10 |
WQ Wall Coefficient |
The wall coefficient, kw, is a reaction rate parameter used to calculate the change in concentration of a substance as it reacts with material along the pipe walls. The wall coefficient has a positive value if the concentration of the substance grows in time, and a negative value if the concentration decays in time. |
YES |
YES |
1 |
2 |
wall_coeff |
-0.3 |
-10 |
10 |
Criticality |
The criticality grade of the link. This provides an indication of the significance of the effect on the network if the link fails. This field may be updated from a Critical Link Analysis simulation. |
YES |
YES |
1 |
0 |
criticality |
Integer |
Criticality Count |
Number of items (Nodes, Properties, Customer Points or Connections) assessed as critical in the event of link failure. This field may be updated from a Critical Link Analysis simulation. |
YES |
YES |
1 |
0 |
criticality_count |
Integer |
Wave Celerity |
Velocity of propagation of pressure waves caused by sudden increase or decrease in flow rate. See Transients Advisor for more details. |
YES |
YES |
1 |
V |
wave_celerity |
1400 |
Pressure Rating |
Maximum design working pressure of link |
YES |
YES |
1 |
WN_P |
pressure_rating |
System Type |
For information. Type in a system type or select an option from the dropdown list:
YES |
YES |
1 |
40 |
0 |
system_type |
Text |
Isolation Area |
Area identifier used to identify groups of objects to be closed when carrying out a Critical Link Analysis. |
YES |
YES |
1 |
30 |
0 |
isolation_area |
Text |
Diameter |
Pipe diameter |
YES |
YES |
2 |
1 |
PS |
diameter |
10 |
20000 |
Valve Diameter |
Diameter of the valve when fully open |
YES |
YES |
2 |
0 |
PS |
valve_diameter |
10 |
20000 |
Loss Coeff. (Open) |
Local headloss coefficient when the valve is open. Minimum value 0.01 |
YES |
YES |
2 |
4 |
loss_when_open |
0 |
10000 |
Valve Curve |
Reference to built in curve, or user defined curve. Note: Gate valves may be used as isolation valves (on/off control). However, it is recommended that in general gate valves are not used as control valves.
YES |
YES |
2 |
30 |
0 |
construction_type |
Text |
PLUG |
Bends |
This field defines the geometry of the link. The underlying data consists of a series of (x,y) pairs defining the vertices of the link. Each link is made up of a series of straight lines between the defined (x,y) points. This data is not displayed on the grid or property sheet. Link vertices are included when you export link data to CSV files. There are two options available for exporting link vertices. These are selected on the Select CSV Export Options dialog using the Coordinate Arrays Format dropdown list. The options are:
NO |
YES |
NO |
0 |
XY |
bends |
Array |
InfoNet Unique ID |
The InfoNet Unique ID and InfoNet Network ID are unique identifiers associated with the corresponding object and network in an InfoNet database. When importing from InfoNet, these identifiers can be copied from the InfoNet database in order to maintain links between the two networks. |
YES |
YES |
NO |
0 |
asset_uid |
GUID |
InfoNet Network ID |
See InfoNet Unique ID |
NO |
YES |
NO |
0 |
asset_network_uid |
GUID |
Database Table Name: wn_ctl_valve
Field Name |
Help Text |
Flag |
Grid |
Property Page |
Size |
Precision |
Units |
Database Field |
Data Type |
Default |
Error Lower Limit |
Error Upper Limit |
Live Data Point ID |
Name of the associated Live Data Point, Live Data Feed, or Live Data Composite Feed. Note: Duplicate IDs are shown once.
YES |
YES |
3 |
100 |
0 |
live_data_point_id |
Text |
Pipe Closed |
The pipe is permanently closed if the box is checked |
YES |
YES |
3 |
0 |
pipe_closed |
Boolean |
PoW Unit Cost (from - to) |
Cost per cubic metre, in user defined currency units, of transferring water between the From Node and To Node. Prices can be negative to allow for exports or bulk water sale. |
YES |
YES |
3 |
2 |
WN_VCOST |
usds_pow_cost |
PoW Category (from - to) |
The category into which this cost falls, for flow between the From Node and To Node.
YES |
YES |
3 |
16 |
0 |
usds_pow_cat |
Text |
PoW Unit Cost (to - from) |
Cost per cubic metre, in user defined currency units, of transferring water between the To Node and From Node. Prices can be negative to allow for exports or bulk water sale. |
YES |
YES |
3 |
2 |
WN_VCOST |
dsus_pow_cost |
PoW Category (to - from) |
The category into which this cost falls, for flow between the To Node and From Node.
YES |
YES |
3 |
16 |
0 |
dsus_pow_cat |
Text |
Pipe Status |
You can set a time-varying profile for the pipe closed state in the grid. See Closed Pipes for more information The data in this grid is only used if the Pipe Closed checkbox is un-checked. Database Table Name: wn_ctl_pipe_status
YES |
YES |
4 |
status |
Array |
Repeat Period |
Profile period which will be repeated throughout simulation, if the Repeat Profile box is checked.
YES |
YES |
4 |
0 |
repeat_status_period |
Integer |
0 |
Profiles |
This grid contains time varying control parameters for the valve. Different columns are visible for different valve types. See Mode ID help for more details on the control parameters required for each valve type. Database Table Name: wn_ctl_valve_profiles
NO |
YES |
5 |
0 |
profiles |
Array |
Mode ID |
Operation Mode for a valve. The choice is:
YES |
YES |
5 |
4 |
0 |
mode |
Text |
PRSV Priority Mode |
Mode for PRSV
YES |
YES |
5 |
3 |
prsv_priority |
Text |
SUS |
Opening |
Constant percentage valve opening. THV |
YES |
YES |
5 |
2 |
WN_OPEN |
opening |
0 |
100 |
Pressure |
The constant target pressure. PRV and PSV |
YES |
YES |
5 |
2 |
WN_P |
pressure |
0.1 |
200 |
Sustaining Pressure |
The constant upstream target pressure. PRSV |
YES |
YES |
5 |
2 |
WN_P |
prsv_sustaining_p |
0.1 |
200 |
Reducing Pressure |
The constant downstream target pressure. PRSV |
YES |
YES |
5 |
2 |
WN_P |
prsv_reducing_p |
0.1 |
200 |
Flow |
Target flow to be kept constant throughout the simulation. FRV only |
YES |
YES |
5 |
2 |
WN_Q |
flow |
0 |
5000000 |
Initial Pressure |
Initial pressure setting at the start of the simulation. FMV only. |
YES |
YES |
5 |
2 |
WN_P |
initial_pressure |
Single |
0 |
Initial Flow |
Initial flow setting at the start of the simulation. PFV only. |
YES |
YES |
5 |
2 |
WN_Q |
initial_flow |
Single |
0 |
5000000 |
Initial Opening |
Initial opening of the valve at the start of the simulation. FCV, PCV, OCV only If Regulation Type is set to On/Off for OCV valve Initial Opening should be set to 0 or 100%. (A value of >=0.001 will be considered to be 100% open) |
YES |
YES |
5 |
2 |
WN_OPEN |
initial_opening |
0 |
100 |
| Inoperable | Valve control is not operable, such as when it is jammed or cannot be adjusted. | YES | YES | 5 | inoperable | Boolean | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Control Node |
See the Mode ID help entry for more information on how the Control Node is used with different valve types |
YES |
YES |
5 |
30 |
0 |
control_node |
Text |
Control Pipe |
Pipe where flow is measured to control the valve. FCV, FMV only |
YES |
YES |
5 |
63 |
0 |
control_pipe |
Text |
Sustaining Control Node |
Node at which upstream pressure is measured. Target node at which pressure is to be maintained when valve is in Sustaining mode. PRSV only |
YES |
YES |
5 |
30 |
0 |
prsv_sus_ctlnode |
Text |
Reducing Control Node |
Node at which downstream pressure is measured. Target node at which pressure is to be maintained when valve is in Reducing mode. PRSV only |
YES |
YES |
5 |
30 |
0 |
prsv_red_ctlnode |
Text |
| Pressure Open |
Pressure at control node at which valve is fully open (only used if time varying profile has not been specified) OCV only |
YES | YES | 5 | 2 | WN_P | pressure_open | Single | 0.1 | 200 | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Pressure Closed |
Pressure at control node at which valve is fully closed (only used if time varying profile has not been specified) OCV only |
YES | YES | 5 | 2 | WN_P | pressure_closed | Single | 0.1 | 200 | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Regulation Type |
Either continuous or on/off. OCV only
YES | YES | 5 | 0 | regulation_type | Boolean | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Repeat Period |
YES |
YES |
5 |
0 |
repeat_period |
Integer |
0 |
Repeat Profile |
Check the Repeat Profile box to repeat a profile (from 00:00 for the selected Repeat Period) for the duration of the simulation. Note: When using the Repeat Profile option; if the defined profile spans over the selected Repeat Period, the profile will not be repeated.
YES |
YES |
5 |
0 |
repeat_profile |
Boolean |
1 |
After Last Point |
YES |
YES |
5 |
0 |
after_profile |
Integer |
0 |
Repeat Profile |
YES |
YES |
5 |
0 |
repeat_status |
Boolean |
1 |
Before First Point |
YES |
YES |
5 |
0 |
before_profile |
Integer |
0 |
Linear Profile |
This checkbox decides if values in the profile grid are interpolated.
YES |
YES |
5 |
0 |
linear_profile |
Boolean |
0 |
Regulation Precision (%) |
The valve regulation precision enables you to set a tolerance for solving valve status. For example if a PRV has a pressure setting of 20m and you specify a precision of 1%, the valve will solve to a value between 19.8–20.2m. A precision of 1% will be suitable in most cases. The Regulation Precision can be set to any value between 0.5% and 10%. Achievement of the Regulation Precision is dependent on the Computational Accuracy. Once the flow balance set by the Computational Accuracy has been achieved the timestep is deemed to be solved, regardless of the valve regulation precision setting. Tightening the Computational Accuracy will assist with achieving the valve regulation precision required. The option to enforce solving for both the computational accuracy and the regulation precision for valves by continuing the simulation beyond the computational accuracy solution up to a maximum of 99 iterations is available in the Simulation Options dialog on the Schedule Hydraulic Run View. If after the maximum number of iterations one or more valves have still not achieved a value within the specified precision, you will be informed via the run dialog. |
YES |
YES |
5 |
3 |
regulation_precision |
1 |
0 |
99.999 |
UPC Script |
Local UPC Script describing the logical controls for the current network object. |
NO |
YES |
6 |
upc_script |
Memo |
Disable UPC |
Check this box to disable both local and global UPC Scripts for the network object. Any controls defined for the object other than UPC Scripts will be applied. |
NO |
YES |
6 |
disable_upc |
Boolean |
Enable Surge |
Check this option to enable Transient simulation fields for modelling valve using a user-defined Time/Valve opening profile. Note: the Enable Surge field and Enable Regulation field cannot be checked at the same time. |
YES |
YES |
7 |
iwts_enable_surge |
Boolean |
0 |
Valve Event |
Transient simulation field enabled when the Enable Surge field is checked. Time-Opening profile used to dictate valve opening during transients simulation. Database Table Name: wn_ctl_valve_iwts_event
NO |
NO |
7 |
iwts_event |
Array |
Bypass |
Transient simulation field enabled when the Enable Surge field is checked. Check this option to model a bypass pipe for the control valve. |
YES |
NO |
7 |
iwts_bypass |
Boolean |
0 |
Bypass Diameter |
Transient simulation field enabled when the Enable Surge and the Bypass option is checked. Internal diameter of the bypass pipe |
YES |
NO |
7 |
2 |
PS |
iwts_bypass_diameter |
Single |
0.0 |
Bypass Loss Coefficient |
Transient simulation field enabled when the Enable Surge and the Bypass option is checked. Local headloss coefficient of the bypass pipe |
YES |
NO |
7 |
3 |
iwts_bypass_loss_coeff |
Single |
0.0 |
Series NRV |
Transient simulation field enabled when the Enable Surge field is checked. Check this option to model a non-return valve in series with the control valve |
YES |
NO |
7 |
0 |
iwts_series_nrv |
Boolean |
0 |
NRV Do Not Reopen |
Transient simulation field enabled when the Enable Surge and Series NRV option is checked. If this option is checked, the non-return valve will not open once it has closed |
YES |
NO |
7 |
0 |
iwts_nrv_dont_reopen |
Boolean |
0 |
NRV Response Time |
Transient simulation field enabled when the Enable Surge and Series NRV option is checked. The amount of time it takes for non-return valve to go from fully opened to fully closed |
YES |
NO |
7 |
1 |
iwts_nrv_response_time |
Single |
0.0 |
| Enable Regulation |
Check this option to enable Transient Simulation fields for modelling valve as a regulator. Note: the Enable Regulation field and Enable Surge field cannot be checked at the same time. |
YES | NO | 7 | 0 | iwtsEnableRegulation | Double | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Regulator Type |
Transient simulation field enabled when the Enable Regulation field is checked. Type of regulating valve:
YES | NO | 7 | 10 | 0 | iwtsRegulatorType | Text | Flow | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Setting |
Transient simulation field enabled when the Enable Regulation field is checked. Target flow value when Regulator Type is set to Flow. Target pressure value when Regulator Type is set to Pressure. |
YES | NO | 7 | iwtsSetting | Double | 0 | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Response Time |
Transient simulation field enabled when the Enable Regulation field is checked. Used to set the rate at which the valve opens/closes. The modulation of the valve is carried out by changing its resistance (headloss/flow2) by small increments equal to (surge timestep)/(valve response time). |
YES | NO | 7 | TS | iwtsResponseTime | Double | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Use PID Control |
Transient simulation field enabled when the Enable Regulation field is checked. Check this option to enable PID regulation fields. |
YES | NO | 7 | iwts_use_pid_control | Boolean | 0 | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Control Node (Transient) |
Transient simulation field enabled when the Use PID Control field is checked and Regulator Type is set to Pressure. Node where pressure is measured to control the valve. |
YES | NO | 7 | 30 | 0 | iwts_control_node | Text | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Control Pipe (Transient) |
Transient simulation field enabled when the Use PID Control field is checked and Regulator Type is set to Flow. Pipe where flow is measured to control the valve. |
YES | NO | 7 | 63 | iwts_control_pipe | Text | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Controller Gain |
Transient simulation field enabled when the Use PID control field is checked. The Velocity form of the PID equation is used to calculate the change in valve position from one sample time to the next.
YES | NO | 7 | 3 | iwts_controller_gain | Single | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Integral Time |
Transient simulation field enabled when the Use PID Control field is checked. Integral time used in the Velocity PID equation (see Controller Gain for details). |
YES | NO | 7 | 1 | TS | iwts_integral_time | Single | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Differential Time |
Transient simulation field enabled when the Use PID Control field is checked. Differential time used in the Velocity PID equation (see Controller Gain for details). |
YES | NO | 7 | 1 | TS | iwts_differential_time | Single | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Maximum Shear Strength |
The maximum value for the corrosion layer shear strength on the pipe wall. The maximum value for which the hydraulic shear strength will result in material being eroded from the pipe wall. See Water Quality - Turbidity Analysis for further information. |
YES | YES | 8 | WN_STRESS | wq_max_shear_strength | Double | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Initial Shear Strength |
The initial value for the corrosion layer shear strength on the pipe wall. The hydraulic shear strength must rise above this initial value to begin the erosion of material from the pipe wall. See Water Quality - Turbidity Analysis for further information. |
YES | YES | 8 | WN_STRESS | wq_init_shear_strength | Double | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Erosion Coefficient |
Parameter used to calculate the quantity of material eroded from the pipe wall when the hydraulic shear stress exceeds the corrosion layer shear strength; the excess shear. See Water Quality - Turbidity Analysis for further information. |
YES | YES | 8 | WN_RATE | wq_erosion_coefficient | Double | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Erosion Exponent |
The power to which the ratio of excess shear to maximum shear strength is raised when calculating the quantity of material released from the pipe wall. A value of zero will be interpreted as meaning the erosion is independent of the excess shear. See Water Quality - Turbidity Analysis for further information. |
YES | YES | 8 | wq_erosion_exponent | Double | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Release Coefficient |
Parameter used to calculate the increase in turbidity as a result of material eroded from the pipe wall. See Water Quality - Turbidity Analysis for further information. |
YES | YES | 8 | WN_TURBLEN | wq_release_coefficient | Double | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Notes |
You can keep freeform notes about any object in your network. The notes field can be up to 64,000 characters in size, or about 10 pages of printed text. |
NO |
YES |
11 |
0 |
notes |
Memo |
Has Local UPC |
Read only field displayed in the grid view only. If the Has Local UPC box is checked, the network objects has a Local UPC Script defined. The UPC Script can be viewed from the object property sheet. |
NO |
YES |
NO |
has_local_upc |
Boolean |
From Node ID |
YES |
YES |
1 |
30 |
0 |
us_node_id |
Text |
To Node ID |
YES |
YES |
1 |
30 |
0 |
ds_node_id |
Text |
Suffix |
YES |
YES |
NO |
1 |
0 |
link_suffix |
Text |
Asset ID |
YES |
YES |
1 |
30 |
asset_id |
Text |
PoW |
Read only field that indicates if Price of Water data has been entered on the property sheet |
NO |
YES |
NO |
0 |
pow_selected |
Boolean |
All results fields are displayed on the grid when opened while viewing a replay of a simulation, and on a special results page placed at the front of Property Sheets displayed while viewing a simulation replay.
For details of results fields for links, see the Link Results Data Fields topic.