RTC Validation Messages
This topic lists validation messages related to Real Time Control in the network.
These messages are displayed in the Output Window when the network is validated.
For details of other validation messages, see the Validation Messages topic.
Key to Messages
Left Column
The error message number is used internally by InfoWorks ICM. This number is unique, and may be useful when contacting Innovyze Support.
Centre Column
Name:
The error or warning message that is displayed.
Info:
Additional information about the error or warning, such as the name of the network object where the anomaly occurred
Cause:
Why the message has been displayed
Advice:
What, if anything, you need to do about it.
Right Column
Information only - no further action needed
Warning - action may be required
Error - action necessary
List of Validation Messages
E10001
Argument not found
Info
Variable ID
Cause
An Argument specified in the Variable does not correspond to the ID of a Range, Table, Variable or Logic for the Regulator.
Advice
Select a valid Dependent ID in the Argument field of the Variable
E10002
Invalid time value in row n
Info
None
Cause
The date/time value entered in row n of the Table is in the incorrect format.
Values must be entered as a date and time (dd/mm/yy-hh:mm).
  • For a daily range, enter the time (hh:mm) and leave day, month and year as zero.
  • For a weekly range, enter the time (hh:mm) and day (dd). Enter 01 for Monday, 02 for Tuesday and so on. Sunday is 07. Leave month and year as zero.
Advice
Enter date/time in the correct format as described above
E10003
The input value in row n is not greater than the value in the previous row
Info
None
Cause
The Input values in the Table are not specified in ascending order
Advice
Redefine the Table with Input values in ascending order
E10004
Cannot find sensor range
Info
Controller ID
Cause
The Controller is of type PID, but the ID entered in the Sensor field does not correspond to the ID of a local Range, or a value has not been entered in the Sensor field.
Advice
Enter the ID of an existing Range in the Sensor field of the Controller
E10005
Cannot find condition
Info
Logic ID
Cause
An ID specified in one of the Dependent Condition fields of the Logic doe snot correspond to the ID of a local Range or Logic.
Advice
Enter the ID of an existing Range or Logic in the Dependent Condition field of the Logic
E10006
Initial value must be between n and n
Info
None
Cause
The value entered in the Initial field for the Regulator is outside the range displayed.
Applies to objects of type VLDorf, VCWeir, FixPmp, ScrPmp and RotPmp
Advice
Enter a valid value in the Initial field for the Regulator
E10007
Initial value must be between 0 and n
Info
None
Cause
The value entered in the Initial field for the Regulator is less than zero or greater than n.
Applies to objects of type VWWeir, VSPPmp, VFDPmp, VSGate and VRGate
Advice
E10008
Threshold must be between 0 and n
Info
None
Cause
The value entered in the Threshold field for the Regulator is less than zero or greater than n
Advice
Enter a valid value in the Threshold field for the Regulator
E10009
Positive rate of change must be greater than 0 and <= n
Info
None
Cause
The value entered in the Positive rate of change field for the Regulator is less than zero or greater than n
Advice
Enter a valid value in the Positive rate of change field for the Regulator
E10010
Negative rate of change must be greater than 0 and <= n
Info
None
Cause
The value entered in the Negative rate of change field for the Regulator is less than zero or greater than n
Advice
Enter a valid value in the Negative rate of change field for the Regulator
E10011
Local name duplication
Info
Dependent ID
Cause
More than one dependent of the same Type has the same Dependent ID for a particular Regulator.
Applies to Range, Logic or Table dependents.
Advice
Rename the Controller so that it uses a Dependent ID unique to other Controllers for the Regulator
E10012
Undefined operator
Info
Variable ID
Cause
An Operator has not been specified for the Variable, or an invalid operator has been specified.
Advice
Specify a valid Operator for the Variable
E10013
Empty argument found
Info
Variable ID
Cause
Too few Arguments have been specified for the Variable
Advice
Enter the correct number of Arguments for the type of Variable
E10014
Undefined controller type
Info
Controller ID
Cause
Controller Type has not been set to INC or PID
Advice
Select Type of INC or PID for Controller
E10015
Invalid measurement interval
Info
Controller ID
Cause
The Controller is of type INC and the value entered in the Measurement field is too small.
The Measurement interval must be greater than zero and should be a multiple of the run timestep for the controller to function properly.
Advice
Enter a valid Measurement value for the Controller
E10016
The measurement type of the sensor is not appropriate
Info
Controller ID
Cause
The Controller is of type PID, but the Range specified in the Sensor field is not of type Q, V, Y or Z.
Only range types of Q, V, Y and Z can be used as the sensor for a controller.
Advice
Check that the correct Range has been selected in the Sensor field of the Controller.
E10017
Invalid smoothing filter coefficient
Info
Controller ID
Cause
The Controller is of type PID and a value less than zero has been entered in the Filter field.
Advice
Enter a value greater than zero in the Filter field of the Controller
E10018
Invalid integral coefficient
Info
Controller ID
Cause
The Controller is of type PID and a value less than zero has been entered in the Integral field.
Advice
Enter a value greater than zero in the Integral field of the Controller
E10019
Invalid differential coefficient
Info
Controller ID
Cause
The Controller is of type PID and a value less than zero has been entered in the Differential field.
Advice
Enter a value greater than zero in the Differential field of the Controller
E10020
'NOT' operator with more than one dependent
Info
Logic ID
Cause
The Logic is of type NOT, but has more than one Dependent Condition defined
Advice
Remove all but one Dependent Condition from the Logic
E10021
Self-dependent condition
Info
Logic ID
Cause
A Dependent Condition specified for the Logic is the same as the Logic ID
Advice
Remove Dependent Condition referencing this Logic
E10022
Duplicated dependent found
Info
Logic ID
Cause
The same Range or Logic ID has been specified more than once in the Dependent Conditions fields of the Logic
Advice
Remove duplicate references from Dependent Conditions fields of the Logic
E10023
Logical operator demands further dependents
Info
Logic ID
Cause
This type of Logic requires more than one Dependent Condition to be specified
Advice
Enter at least two Range or Logic IDs in the Dependent Conditions fields of the Logic
E10024
Undefined rule type
Info
Rule ID
Cause
There is no entry in the Rule Type field, or a type that does not exist has been entered in the Rule Type field.
Advice
Select an appropriate Rule Type for the Rule
E10025
Local condition duplication
Info
Rule ID
Cause
More than one rule has the same Dependent ID for a particular Regulator
Advice
Enter a Dependent ID for the Rule that is unique to rules for the Regulator
E10026
Controller not found
Info
Rule ID
Cause
The Rule is of type CTRL, but the Controller has not been specified, or the ID entered in the Controller field does not correspond to a Controller ID for this Regulator or in the Global section
Advice
Enter a valid Controller ID for the Rule
E10027
Condition not found
Info
Rule ID
Cause
The Dependent ID of the Rule does not correspond to the ID of a Range or Logic condition defined for this Regulator or in the Global section
Advice
Enter a Dependent ID that corresponds with a Range or Logic.
E10028
Default rule defined after other rules
Info
Rule ID
Cause
The _Default_ rule for a regulator has been added to the editor after another rule for the regulator
Advice
Move the _Default_ rule in the editor so that it is positioned above other rules for the regulator.
E10029
Rule type is inappropriate for this regulator
Info
Rule ID
Cause
The Rule has the wrong type of Rule Type for the regulator. For example: a Rule Type of ON has been specified for a variable crest level weir.
Advice
Enter an appropriate Rule Type for the regulator
E10030
Regulator name duplicated
Info
None
Cause
More than one dependent for a particular regulator has the same Dependent ID
Advice
Enter unique Dependent ID values for all dependents for the regulator
E10031
Regulator is not listed in the asset data
Info
None
Cause
A Regulator ID has been specified which does not correspond to the ID of a Regulator object in the network
Advice
Enter a Regulator ID that exists in the network
E10032
Undefined measurement type
Info
Dependent name
Cause
Advice
E10033
Undefined location
Info
Range ID
Cause
The Range is of a non time variable type and an object (node/link/subcatchment) has not been specified, or the object ID specified does not exist in the network.
Advice
Check that the correct object ID has been entered for the Range.
E10034
Location inappropriate to measurement type
Info
Range ID
Cause
The object ID specified in the Range is the ID of the wrong type of object for the type of Range. For example: a link ID has been specified in the Node cell of a Range of Var Type Z - height above datum.
Advice
E10035
Downstream distance is negative
Info
Range ID
Cause
The Range variable type is measured at a link and the Distance Downstream specified is a negative value.
Advice
Enter a positive value in the Distance Downstream field.
E10036
Downstream distance is too large
Info
Range ID
Cause
The Range variable type is measured at a link and the Distance Downstream specified is greater than 19,999 m
Advice
Enter a value less than 19,999 m in the Distance Downstream field.
E10038
Minimum date must be earlier than or equal to maximum date
Info
Range ID
Cause
The Minimum date specified for the Range is after the Maximum date for the Range
Advice
Check the Minimum date and Maximum date values for the Range
E10039
Minimum and maximum times must be relative
Info
Range ID
Cause
The Range is of type Time Repeat, but the Min day or Max day fields are not set to Daily or a day of the week
Advice
Set a valid value for Min day and Max day fields for the Range
E10041
You cannot mix daily and weekly times
Info
Range ID
Cause
The Range is of type Time Repeat and one of the Min day / Max day fields is set to Daily and the other to a day of the week
Advice
Set both Min day and Max day fields to Daily or to a day of the week
E10042
Minimum value must be less than or equal to maximum value
Info
Range ID
Cause
The value entered in the Minimum field of the Range is greater than the value entered in the Maximum field of the Range
Advice
Check that the Minimum and Maximum values have been entered correctly
E10043
Name should be between 1 and 10 characters
Info
Dependent ID
Cause
Length of Dependent ID is greater than 10 characters
Advice
Rename Dependent ID to a name using 10 characters or less
E10044
Name must not contain spaces
Info
Dependent ID
Cause
The ID of a dependent contains spaces
Advice
Use underscores instead of spaces in the Dependent ID
E10045
Cannot find input variable definition
Info
Table ID
Cause
The value specified in the Input Range field of the Table does not correspond to a Logic, Range or Table ID for the Regulator or in the Global section.
Advice
Enter a valid ID in the Input Range field of the Table
E10046
Table must contain at least one entry
Info
None
Cause
A dependent of type Table has no Input or Output values
Advice
Enter at least one set of Input and Output values to the Table
E10047
You cannot mix absolute and relative input values
Info
None
Cause
Both relative and absolute date/time formats have been used in the Input field of the Table.
Advice
Amend Input entries so that they are all specified in absolute or relative time format