Share
 
 

RTC Variable Example

A variable allows the combination of values (from a Range, Table, Logic operator, Variable or constant value) to derive another value.

All variables are set to zero at the beginning of a simulation. Variable values are preserved from timestep to timestep, so they can be used to accumulate statistics. A variable can also be used as a Timer.

Two examples of the use of variables are given below:

Variable Example 1 - Use of a Variable as a Timer

The following example models controlling the status of a sluice gate, by applying a time delay in order to close the sluice gate 40 minutes after it has been opened.

In this example, a variable is used as a timer. The timer starts when the sluice gate is opened. Once the timer has reached 40 minutes, the gate is closed.

The example is defined by adding components to a sluice gate regulator in the RTC Window Editor.

Component

Parameters

Effect

RANGE 1

Range type: Q - flow

Location link: 120.1

Distance Downstream: 0m

Minimum:

Maximum:

TRUE if flow in conduit 120.1 is between +/- infinity

VARIABLE 1

Measurement: Time

Operator: Timer

Start: RANGE 1

Start Timer when RANGE 1 becomes TRUE

RANGE 2

Range type: Variable

Location definition: VARIABLE 1

Minimum: 2400 s

Maximum:

TRUE if VARIABLE 1 is greater than 2400s

RULE 1

Condition: _default_

Rule type: POS

Setpoint Type: FIXED 0.000 m

DEFAULT status of gate is Closed

RULE 2

Condition: RANGE 1

Rule type: POS

Setpoint Type: FIXED 0.500 m

Set sluice gate to 0.5 m if RANGE 1 is TRUE

RULE 3

Condition: RANGE 2Rule type: POS

Setpoint type: FIXED 0.000 m

Set sluice gate to 0.0 m if RANGE 2 is TRUE

  1. Range 1: Defines Link 120.1 as a control link

  2. Variable 1: Starts Timer when flow in link 120.1 is greater than or equal to 0.01 m3/s

  3. Range 2: Defines the calculated time in Variable 1 as a control with a minimum value of 2400s (40 mins)

  4. Rule 1: Unless subsequent rules are TRUE, sluice gate is closed

  5. Rule 2: Unless subsequent rules are TRUE, sets sluice gate opening to 0.5 m

  6. Rule 3: When the Timer defined in Variable 1 reaches 2400s (40 mins), sluice gate is Closed

Variable Example 2

The following example models controlling the operation of a sluice gate, by measurement of the total flow through a conduit. When the total flow in the conduit reaches a given volume, the sluice gate will be closed.

In this example, a variable is used to convert the flow measured in the control conduit to a cumulative flow over a timestep. A second variable is used to keep a total of the cumulative flow.

The example is defined by adding components to a sluice gate regulator in the RTC Window Editor.

Component

Parameters

Effect

RANGE 1

Range type: Q - flow

Location link: 120.1

Minimum:

Maximum:

TRUE if flow is between - / + infinity

VARIABLE 1

Measurement: Flow

Operator: Times

Argument 1: RANGE 1

Argument 2: Constant = 60

Equals RANGE 1 flow multiplied by 60

VARIABLE 2

Measurement: Volume

Operator: Plus

Argument 1: VARIABLE 2

Argument 2: VARIABLE 1

Equals VARIABLE 1 + VARIABLE 2

RANGE 2

Range type: Variable

Location definition: VARIABLE 2

Minimum: 350 m3

Maximum:

TRUE if VARIABLE 2 is greater than or equal to 350 m3

RULE 1

Condition: _default_

Rule type: POS

Setpoint Type: FIXED 0.000 m

DEFAULT status of sluice gate is 0.0 m

RULE 2

Condition: RANGE 1

Rule type: POS

Setpoint Type: FIXED 0.500 m

Set sluice gate to 0.5 m if RANGE 1 is TRUE

RULE 3

Condition: RANGE 2Rule type: POS

Setpoint type: FIXED 0.000 m

Set sluice gate to 0.0 m if RANGE 2 is TRUE

  1. Range 1: Defines Link 120.1 as a control link in which flow is measured

  2. Variable 1: Calculates total flow over timestep

  3. Variable 2: Calculates cumulative flow through Link 120.1

  4. Range 2: Defines Variable 2 as a control with a minimum value of 350 m3

  5. Rule 1: Unless subsequent rules are TRUE, sets sluice gate to 0.0 m

  6. Rule 2: Unless subsequent rules are TRUE, sets sluice gate to 0.5 m

  7. Rule 3: When cumulative flow through Link 120.1 reaches 350 m3, sets sluice gate to 0.0 m

For a further example of an RTC Scenario, see RTC Example.

Was this information helpful?