The simulation parameters govern how the engine performs the model calculations in the hydraulic simulation.
It is not normally necessary to amend the network simulation parameters; the default values have been chosen for optimum accuracy and performance.
To view simulation parameters, select Model parameters
Simulation parameters from the Model menu. The simulation parameters for the current network are displayed in the
Object Properties Window.
Parameters
Database Table Name: hw_sim_parameters
| Field Name | Help text | Database Field | Data Type | Size | Units | Precision | Default | Error Lower Limit | Error Upper Limit | Warning Lower Limit | Warning Upper Limit | |||||
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
|
Min base flow depth |
The minimum absolute baseflow depth that will be used for base flows in conduits. Valid values: 0 < Minimum base flow depth << Minimum conduit height. This Base Flow used for calculation purposes should not be confused with the Subcatchment Base Flow, which is a real inflow into the system. |
min_base_flow_depth |
Double |
|
Y |
3 |
0.02 m |
0.001 |
99 |
|
|
|||||
|
Base flow factor |
Base flow is necessary to ensure numerical stability of the St. Venant equations. By default the base flow applied is equal to 5% of the conduit height (Base Flow Factor of 0.05) (10% for steeper pipes.) The simulation engine adds base flow to maintain numerical stability at low depths. It does this by altering the true upstream (higher) boundary condition so that there is effectively a wall of the base flow depth at the upstream end of the conduit. The simulation engine then adds the normal flow for the base flow depth to the flows in the conduit. At the true downstream end of the conduit, the boundary condition uses the true flow, so that in effect the base flow is lost between the conduit end and the connected node. This means that node volume balance calculations are based on the true flows.
The base flow factor is used to determine the base flow depth in conduits using the following equation:
Valid values: 0 < Base Flow Factor << 1. |
base_flow_factor |
Double |
|
|
3 |
.05 |
0 |
1 |
|
|
|||||
|
Slope where base flow is doubled |
The slope above which the base flow factor is doubled when determining the base flow depth. Valid values: 0 ≤ Slope where base flow is doubled |
slope_base_flow_x2 |
Double |
|
S |
4 |
.01 m/m |
0 |
1 |
|
|
|||||
|
Min space step |
The Space Step parameters determine the number of computational nodes per conduit / river reach. The Space Step is the distance between computational nodes along the conduit / river reach. Valid values are: Minimum Space Step (DXMIN): DXMIN > 0, DXMIN < DXMAX Maximum Space Step (DXMAX): DXMAX > 0, DXMAX > DXMIN In addition, for river reaches:
The Space Step is determined by the Conduit width multiplier:
Minimum Number of Computational Nodes is the global minimum number of computational nodes per conduit. Controls always have 2 computational nodes. The software will allocate at least 5 computational nodes per conduit. If the number of computational nodes determined by the other space step parameters exceeds the minimum, the software will use that number instead.
|
min_space_step |
Double |
|
L |
2 |
.5 m |
0.01 |
9999 |
|
|
|||||
|
Max space step |
See Min space step |
max_space_step |
Double |
|
L |
2 |
100 m |
0.01 |
9999 |
|
|
|||||
|
Conduit width multiplier |
See Min space step |
width_multiplier |
Double |
|
|
2 |
20 |
0 |
999 |
|
|
|||||
|
Min number of computational nodes |
See Min space step |
min_computational_nodes |
|
|
|
0 |
5 |
5 |
99999999 |
|
|
|||||
|
Min slot width |
Minimum width of the Preissmann slot (overrides value determined by Celerity ratio). Valid values: 0 < Min slot width << Minimum conduit width. |
min_slot_width |
Double |
|
L |
5 |
0.001 m |
0.00001 |
99 |
|
|
|||||
|
Celerity ratio |
The Preissmann slot is used in the hydraulic simulation to model pressurised flow in closed conduits. The Celerity ratio determines the width of the Preissmann slot used in the software to model surcharged flow. The slot width is such that the celerity in the slot is Celerity ratio x the celerity at half conduit height. The standard ratio was chosen so that surcharged flows could be modelled robustly and accurately. This results in a slot that is 2% of the width of the conduit (slightly different for some conduit shapes). If the software is being used to model storage in large surcharged trunk sewers you may want to reduce the slot width to reduce the additional storage that it generates (note that the slot transition generally adds 4-5% area depending on shape). To do this, increase the value of Celerity ratio - a value of 14.414 produces a slot that is 1% of conduit width. Note that narrower slots may make the model less stable. The slot width is inversely proportional to Celerity ratio. Valid values: Celerity ratio > 0 The equations used to calculate the slot width are as follows:
|
celerity_ratio |
Double |
|
|
2 |
10 |
0 |
9999 |
|
|
|||||
|
Lower Froude number |
This is the characteristic Froude number above which the inertia terms in the Saint-Venant equations are phased out for a conduit. The characteristic Froude number for a conduit is determined at half depth. Valid values: 0 < Lower Froude number < Upper Froude number |
lower_froude_number |
Double |
|
|
3 |
.8 |
0 |
99 |
|
|
|||||
|
Upper Froude number |
This is the characteristic Froude number above which the inertia terms in the Saint-Venant equations are dropped. Note that using a value above 1.0 may result in instabilities during simulation. The conduits with the inertia terms dropped will be solved faster by the hydraulic simulation. Valid values: Upper Froude number > 0, Upper Froude number > Lower Froude number |
upper_froude_number |
Double |
|
|
3 |
1 |
0 |
99 |
|
|
|||||
|
Start timestep (s) |
The Initialisation Parameters are used if an initial simulation has not been included in the Simulation State section of the Schedule Hydraulic Run Dialog. The hydraulic system is initialised in a steady state.
The simulation engine will perform up to five initialisation phases. Each time initialisation fails, the phase-in time will be multiplied by a factor of 10 and restartedf from the initial (dry) condition. |
start_timestep |
Double |
|
|
2 |
7.5 |
0.01 |
9999 |
|
|
|||||
|
Max timestep (s) |
Maximum allowed timestep during initialisation process. See Start timestep |
max_timestep |
Double |
|
|
2 |
1920 |
0.01 |
9999 |
|
|
|||||
|
Phase-in time (min) |
Time over which the boundary conditions (initial inflows and tide levels) are linearly phased in during initialisation. See Start timestep |
phase_in_time |
Double |
|
|
2 |
15 |
0.01 |
99999 |
|
|
|||||
|
Steady state flow tolerance |
See Start timestep |
steady_tol_flow |
Double |
|
Q |
6 |
.0005 m3/s |
0.000001 |
999 |
|
|
|||||
|
Steady state depth tolerance |
See Start timestep |
steady_tol_depth |
Double |
|
Y |
6 |
.005 m |
0.000001 |
999 |
|
|
|||||
|
Max number of timestep halvings - initialisation |
Maximum number of timestep halvings to allow convergence of the Newton-Raphson method during the initialisation process. |
ini_max_halvings |
|
|
|
0 |
10 |
1 |
30 |
|
|
|||||
|
Max number of iterations - initialisation |
Maximum number of iterations per timestep during the initialisation process. |
ini_max_iterations |
|
|
|
0 |
10 |
1 |
999 |
|
|
|||||
|
Max number of iterations after doubling - initialisation |
Maximum number of iterations allowed after the timestep has been doubled during the initialisation process. (Rapid convergence of the Newton-Raphson method may result in the timestep being doubled). |
ini_max_iterations_x2 |
|
|
|
0 |
7 |
1 |
999 |
|
|
|||||
|
Tolerance for flow |
During the initialisation process, convergence is achieved when:
|
ini_tolerance_flow |
Double |
|
|
4 |
.01 |
0.0001 |
9 |
|
|
|||||
|
Flow tolerance scaling factor - initialisation |
See Tolerance for flow - initialisation |
ini_scaling_flow |
Double |
|
|
3 |
1 |
0.001 |
999 |
|
|
|||||
|
Tolerance for depth |
See Tolerance for flow - initialisation |
ini_tolerance_depth |
Double |
|
|
4 |
.01 |
0.0001 |
9 |
|
|
|||||
|
Depth tolerance scaling factor - initialisation |
See Tolerance for flow - initialisation |
ini_scaling_depth |
Double |
|
|
3 |
1 |
0.001 |
999 |
|
|
|||||
|
Tolerance for level |
See Tolerance for flow - initialisation |
ini_tolerance_level |
Double |
|
|
4 |
.01 |
0.0001 |
9 |
|
|
|||||
|
Level tolerance scaling factor - initialisation |
See Tolerance for flow - initialisation |
ini_scaling_level |
Double |
|
|
3 |
1 |
0.001 |
999 |
|
|
|||||
|
Min depth in conduits - initialisation |
Minimum depth imposed by the simulation engine during the initialisation process. |
ini_min_depth |
Double |
|
Y |
5 |
.01 m |
0.00001 |
9 |
|
|
|||||
|
Min plan area at nodes - initialisation |
Minimum node plan area imposed by the simulation engine during the initialisation process. |
ini_min_node_area |
Double |
|
NA |
3 |
1 m2 |
0 |
9999 |
|
|
|||||
|
Time weighting factor |
θ is used in the Preissmann 4-point scheme. The 4-point scheme is only unconditionally stable when θ > 0.5. The value of θ = 1.0 provides maximum numerical dispersion during initialisation. |
ini_time_weighting |
Double |
|
|
3 |
1 |
0 |
1 |
0.5 |
|
|||||
|
Tolerance for volume balance |
If Tolerance for volume balance is set to 0.0 (default), no volume balance checking will be carried out. To enable volume balance checking, define a value greater than zero. The recommended value to use is 0.01. When volume balance checking is enabled the simulation engine checks the volume balance at each node at each iteration where the flow, depth, and level increments are within tolerance. If volume balance / (volume balance scaling factor + |largest volume in/out/change in storage|) is greater than the Tolerance for volume balance then the engine will do another iteration, unless the engine has already done the maximum number of iterations for this timestep, in which case the engine will halve the timestep. |
ini_tolerance_volbal |
Double |
|
|
4 |
0 |
0 |
9 |
|
|
|||||
|
Volume balance tolerance scaling factor - initialisation |
See Tolerance for volume balance (Initialisation) |
ini_scaling_volbal |
Double |
|
|
3 |
1 |
0 |
999 |
|
|
|||||
|
Relax tolerance from run t/s - initialisation |
During the initialisation phase:
It is strongly recommended that this option is checked for networks that contain 2D Zones. |
ini_relax_tol |
Boolean |
|
|
0 |
True |
|
|
|
|
|||||
|
Max number of timestep halvings - simulation |
Maximum number of timestep halvings to allow convergence of the Newton-Raphson method during the simulation. |
sim_max_halvings |
|
|
|
0 |
10 |
1 |
30 |
|
|
|||||
|
Max number of iterations - simulation |
Maximum number of iterations allowed per timestep. |
sim_max_iterations |
|
|
|
0 |
10 |
1 |
999 |
|
|
|||||
|
Max number of iterations after doubling - simulation |
Maximum number of iterations allowed after the timestep has been doubled. (Rapid convergence of the Newton-Raphson method may result in the timestep being doubled). |
sim_max_iterations_x2 |
|
|
|
0 |
7 |
1 |
999 |
|
|
|||||
|
Tolerance for flow - simulation |
During the simulation, convergence is achieved when:
|
sim_tolerance_flow |
Double |
|
|
4 |
.01 |
0.0001 |
9 |
|
|
|||||
|
Flow tolerance scaling factor - simulation |
See Tolerance for flow - simulation |
sim_scaling_flow |
Double |
|
|
3 |
1 |
0.001 |
999 |
|
|
|||||
|
Tolerance for depth - simulation |
See Tolerance for flow - simulation |
sim_tolerance_depth |
Double |
|
|
4 |
.01 |
0.0001 |
9 |
|
|
|||||
|
Depth tolerance scaling factor - simulation |
See Tolerance for flow - simulation |
sim_scaling_depth |
Double |
|
|
3 |
1 |
0.001 |
999 |
|
|
|||||
|
Tolerance for level - simulation |
See Tolerance for flow - simulation |
sim_tolerance_level |
Double |
|
|
4 |
.01 |
0.0001 |
9 |
|
|
|||||
|
Level tolerance scaling factor - simulation |
See Tolerance for flow - simulation |
sim_scaling_level |
Double |
|
|
3 |
1 |
0.001 |
999 |
|
|
|||||
|
Min depth in conduits - simulation |
Minimum depth imposed by the simulation engine |
sim_min_depth |
Double |
|
Y |
5 |
.01 m |
0.00001 |
9 |
|
|
|||||
|
Min plan area at nodes - simulation |
Minimum node plan area imposed by the simulation engine |
sim_min_node_area |
Double |
|
NA |
3 |
1 m2 |
0 |
9999 |
|
|
|||||
|
Time weighting factor - simulation |
θ is used in the Preissmann 4-point scheme. The 4-point scheme is only unconditionally stable when θ > 0.5; the value of θ = 0.65 used during simulation introduces a small degree of numerical dispersion. |
sim_time_weighting |
Double |
|
|
3 |
.65 |
0 |
1 |
0.5 |
|
|||||
|
Tolerance for volume balance - simulation |
If Tolerance for volume balance is set to 0.0, no volume balance checking will be carried out. To enable volume balance checking, define a value greater than zero. The recommended value to use is 0.01. When volume balance checking is enabled the simulation engine checks the volume balance at each node at each iteration where the flow, depth, and level increments are within tolerance. If volume balance / (volume balance scaling factor + |largest volume in/out/change in storage|) is greater than the Tolerance for Volume Balance then the engine will do another iteration, unless the engine has already done the maximum number of iterations for this timestep, in which case the engine will halve the timestep. |
sim_tolerance_volbal |
Double |
|
|
4 |
0.01 |
0 |
9 |
|
|
|||||
|
Volume balance tolerance scaling factor |
See Tolerance for volume balance - simulation |
sim_scaling_volbal |
Double |
|
|
3 |
1 |
0 |
999 |
|
|
|||||
|
Relax tolerance from run t/s - simulation |
During the simulation phase:
It is strongly recommended that this option is checked for networks that contain 2D Zones. |
sim_relax_tol |
Boolean |
|
|
0 |
True |
|
|
|
|
|||||
| Use SWMM5 RDII |
A check in the box (default) indicates that SWMM5 RDII (Rainfall Derived Infiltration and Inflow) is to be used in the simulation. If unchecked, the pre-SWMM 5 RDII implementation will be used in the simulation. Note: Pre-SWMM 5 RDII does not support the monthly variation and initial abstraction functionality that is available in SWMM5 RDII for Monthly
RTK Hydrographs, but does allow multiple subcatchments that use RTK Hydrographs (not necessarily the same one) to drain to a single node.
|
swmm5_rdii | Boolean | 0 | True | |||||||||||
|
Stay pressurised |
A pipe should only be pressurised if it is to stay pressurised throughout the simulation. However it is very common that people model pressurised pipes that are not in fact pressurised. By default, the simulation engine will switch to the full solution model for the rest of the simulation if a pressure pipe is not surcharged. You may want to check the Stay pressurised option if you have, for example, a rising main that numerically temporarily goes out of surcharge because of water hammer effects when a pump switches on or off. The simulation may fail in this case, if you have inappropriately set a conduit as a pressure pipe. You should only use the pressurised pipe model for conduits that you know remain permanently surcharged. The field settings are:
|
stay_pressurised |
Boolean |
|
|
0 |
False |
|
|
|
|
|||||
|
Don't linearise conveyance |
In culverts, the conveyance is greater just before the culvert becomes full than at the point when the culvert becomes surcharged. This effect is most pronounced in wide rectangular culverts, and occurs due to the effect of the roughness of the roof of the culvert. When this is option is unchecked (default), conveyance tables are linearised to the pipe full value to eliminate turning points in the conveyance function used by the solver. This is shown by the red line on the graph below. This results in the underestimation of flow capacity in rectangular culverts. However, it is more stable mathematically. When this option is checked, the simulation engine does not linearise conveyance tables (see the black line on the graph). Using this option may result in instabilities when the conduit enters/leaves surcharge.
Conduit Conveyance |
dont_linearise_k |
Boolean |
|
|
0 |
False |
|
|
|
|
|||||
|
No. of geometry table entries |
This field determines the number of entries the simulation uses for conduit cross-section geometry lookup tables between the invert and soffit. More entries provide a more accurate representation of the geometry, at the expense of memory use and computational effort. You may need to change this parameter to get a more accurate representation of pipe behaviour close to pipe full when you turn on the Don't linearise conveyance option above. |
geometry_table_entries |
|
|
|
0 |
15 |
15 |
999 |
|
|
|||||
|
Use full area for headloss calculations |
By default the checkbox is unchecked. The value of velocity passed through to the headloss calculations is calculated from:
When this option is checked headloss calculations are carried out using the full cross section area of the pipe. |
use_full_area_for_hl |
Boolean |
|
|
0 |
False |
|
|
|
|
|||||
|
Inflow is lateral |
The value of this field affects the way in which the simulation engine handles inflow as defined in the Inflow field of conduit, river reach, channel and bridge links. For new models, we recommend that this field is checked. However, if you want to reproduce the behaviour of the simulation engine prior to InfoWorks ICM, version 6.5 then do not check this field.
|
inflow_is_lateral |
Boolean |
|
|
0 |
False |
|
|
|
|
|||||
|
Bottom of headloss transition |
The Bottom of headloss transition and Top of headloss transition parameters are used to define a transition zone in which headloss in conduits is phased out, with the purpose of eliminating unrealistically high headloss results for links with flows at low depths.
The values are given as a proportion of conduit height minus sediment depth:
|
hl_trans_bottom |
Double |
|
|
3 |
0 |
0 |
1 |
|
|
|||||
|
Top of headloss transition |
Used to define a transition zone in which headloss in conduits is phased out, with the purpose of eliminating unrealistically high headloss results for links with flows at low depths. See Bottom of headloss transition for further details. |
hl_trans_top |
Double |
|
|
3 |
0 |
0 |
1 |
|
|
|||||
|
Use Villemonte equation |
When this field is checked the simulation will use the Villemonte equation for drowned weir flow. |
use_villemonte |
Boolean |
|
|
0 |
False |
|
|
|
|
|||||
|
Drop inertia in pressure pipes |
Check this parameter to exclude modelling of inertia in pressure pipes. See Pressurised Pipe Model for more information. |
pressure_drop_inertia |
Boolean |
|
|
0 |
True |
|
|
|
|
|||||
| Drowned bank linearisation threshold |
When calculating bank flow for a drowned spill segment, linearised flow equations will be used when the head difference at both ends of the segment is below this threshold. Applicable to lateral banks, inline banks and irregular weirs; this parameter is used to avoid oscillating flows as the head difference over the bank approaches zero. If set to null, a value of zero is assumed (no linearisation). |
drowned_bank_threshold | Double | Y | 3 | 0.01 m | ||||||||||
| Node level affects groundwater infiltration |
Check this parameter to make groundwater infiltration depend on the depth in the groundwater destination node. In existing networks (created before Version 8.0) this option will be unchecked. In new networks this option will be checked. |
sim_node_affects_infiltration | Boolean | 0 | True | |||||||||||
| Weight Manning roughness by n |
The simulation engines uses the equivalent roughness concept to provide a roughness value for a wetted perimeter that has more than one roughness value. This parameter allows you to choose whether the perimeter is weighted using n (N) or 1/n (MANNING) to represent roughness. Check this parameter to weight Manning roughness by n. If unchecked (default), Manning roughness will be weighted by 1/n. |
weight_by_n | Boolean | 0 | False | |||||||||||
| Use 2d elevations instead of depths |
Used as a measure to avoid oscillating flows due to ground level discrepancy between manholes and 2D mesh elements. Check this parameter to use the elevation in 2D zones to set the elevation at 1D nodes connected to the 2D zone. If this option is unchecked, the engine will use the depth in 2D zones to set the depth above ground at 1D nodes. See Defining 2D Nodes for more information. Note: This setting is over-ridden by the setting on the 1D-2D linkage basisfield for individual nodes. See
Node Data Fields for further information.
|
use_2d_elevations | Boolean | 0 | False | |||||||||||
| Inflow-based node-2d link |
Check this parameter to use the net inflow into an element when calculating maximum flow that can be exchanged between the 2D element and a 1D node within the element. This method monitors the error between the head in the element (measured head) and the corresponding head given by the net inflow into the element (equilibrium head). A PID controller is used to minimise the error by adjusting the maximum flow that can be exchanged between the 2D and 1D network. If this option is unchecked, the engine will use the volume in the element to calculate the maximum flow that can be exchanged. This method may result in discrepancies between head in the 2D mesh and inflow to the 1D network, particularly in cases where 1D nodes are located within small elements and when using long timesteps. |
inflow_manhole_link | Boolean | 0 | True | |||||||||||
| Ground slope term correction |
Check this parameter if the ground slope term at the faces is to be based on a constant slope connecting the adjacent element ground levels. Using this method, the resulting flow under uniform conditions will follow the Manning's equation for any ground slope subject to the 2D Parameters set in a run. This maybe useful when calibrating models in areas with steep slopes. However, using this parameter may result in large flow velocities which may cause a reduction of the engine time step and therefore an increase in run times. To alleviate this issue, it is recommended to reduce the Maximum velocity parameter on the Advanced tab of the 2D Parameters dialog. If this option is unchecked (default), the ground slope term is based on a discontinuous step connecting the adjacent element ground levels. The results using both approaches tend to the same values in areas where the shallow water equation hypothesis is fulfilled, i.e. areas with low to moderate slopes of both the free surface and the ground level. |
ground_slope_correction | Boolean | 0 | False | |||||||||||
| Time step method |
The method for calculating the time step at subgrid 2D elements when using Subgrid Sampling. See Subgrid Sampling Time Step Method for details about this and the equations used to calculate all the time step method options. |
subgrid_timestep_method | Text | 30 | Face depth | |||||||||||
| Min depth tolerance | Minimum allowed depth difference between original and simplified volume/level table.
This values overrides the value specified by the percentage depth tolerance. See Depth tolerances for details. |
subgrid_min_depth_tol | Double | L | 0 | 0 | ||||||||||
| Max depth tolerance |
Maximum allowed depth difference between original and simplified volume/level table. This values overrides the value specified by the percentage depth tolerance. See Depth tolerances for details. |
Double | L | 0 | 0 | |||||||||||
| Percentage depth tolerance | Depth percentage error allowed when simplifying volume/level tables.
See Depth tolerances for details. |
Double | 0 | 100 |