The Run Validation window displays error and warning messages for the currently selected run when that run is validated or simulated.

Validation is implemented on control properties. Values can be viewed and edited for a network object on the Properties window.

Run Validation Window

Validation takes place when:

  • The Validate button of the Current run section is pressed on the Run Manager, or
  • The Simulate button of the Current run section is pressed on the Run Manager.

The window is displayed at the bottom of the Baseline Page beneath the Map view. To display the window, click the Validation button of the Run Manager. (It is only possible to view the validation window once validation has been carried out.)

Right click in the window to display a context menu allowing the following operations to be carried out:

  • Print - print out validation messages
  • Copy to clipboard - copy messages to clipboard for pasting in another application
  • Go to Property Page - right click the validation message and select this option to open the Properties Window of the relevant network object with the offending field selected, and to highlight the network object in the Map view. Alternatively, double-click the error message to display the properties window.

For each error or warning, the validation window displays the following information:

Symbol - the message is an error message. The error must be resolved before the run can be simulated.

- the message is a warning message. This message is for information.

Code The error or warning message number
Priority Priority level (always set to 1)
Object Type The type of object in the Network.
Object The name of the object in the Network.
Field The field where the value is invalid, missing or outside recommended ranges.
Message A description of the problem.

List of validation messages

Message Number Validation Message / Cause / Advice Priority

E0403

Too many profile entries <limit>

Info

Pump Station name. Maximum number of entries permitted.

Cause

There are too many entries in the profiles Editor.

Advice

Reduce number of profile entries to within limit

E0404

Value exceeds depth in control reservoir <reservoir depth>

Info

Pump Station name. Control Reservoir maximum depth.

Cause

Applicable to Pump Stations of Mode of Control type PLAN or FLOW using a Control Reservoir

Pump Station Pressure On value > Control Reservoir maximum depth

Advice

Check Pump Station properties and Reservoir properties

E0405

Value exceeds depth in control reservoir

Info

Pump Station name.

Cause

Applicable to Pump Stations of Mode of Control type PLAN or FLOW using a Control Reservoir

Pump Station Pressure Off value > Control Reservoir maximum depth

Advice

Check Pump Station properties and Reservoir properties

E0409

Cannot find this node in the network

Info

Pump Station name

Cause

The control node specified on the Pump Station properties does not exist in the network, or a control node has not been specified.

Advice

Check control node specified

E0410

on (<index>) Value is out of range (<reservoir depth range>)

Info

Pump Station name. Control Node (Reservoir) depth range.

Cause

May occur at a pump station where mode of control used is AUTO or PROF.

  • AUTO - the pump ON pressure specified is outside the reservoir depth range of the Control Reservoir specified.
  • PROF - the Target Deviation On value is not within range:
    • Control Node is a Reservoir - the Target Deviation On value is greater than +/- half the reservoir depth of the Control Reservoir
    • Control Node is a Node - the Target Deviation On value is < -999.5m or > 99.5m.

Advice

Check pump ON pressure / Target Deviation On

E0412

off (<index>) Value is out of range (<reservoir depth range>)

Info

Pump Station name. Control Node (Reservoir) depth range.

Cause

May occur at a pump station where mode of control used is AUTO or PROF.

  • AUTO - the pump OFF pressure is outside the reservoir depth range of the Control Reservoir
  • PROF - the Target Deviation Off value is not within range:
    • Control Node is a Reservoir - the Target Deviation Off value is greater than +/- half the reservoir depth of the Control Reservoir
    • Control Node is a Node - the Target Deviation Off value is < -999.5m or > 99.5m.

Advice

Check pump OFF pressure / Target Deviation Off

E0416

Initial speed (<index>) value is out of range (<minimum speed to maximum speed>)

Info

Pump Station name

Cause

Pump Station pump Initial Speed value < Minimum Speed of pump or > Maximum Speed of pump

Advice

Check Pump Control properties and Pump Data properties

E0417

pump_status_flags (<index>) Status flags should be 0 or 1

Info

Pump Station name

Cause

Applicable to Pump Station of type = PLAN

A value in the pump status flags field specified on the Profiles editor is not equal to 0 or 1.

Advice

Check status flags entries. 0 = OFF, 1 = ON

E0418

pump_status_flags (<index>) Status flags count should be <no. of pumps in station>

Info

Pump Station name

Cause

The number of pump status flags specified on Profiles editor is not the same as the number of pumps in the pump station

Advice

Enter status flag values for all pumps in the pump station

E0418

pump_availability_flag (<index>) Availability flags count should be 0 or <no. of pumps in station>

Info

Pump Station name

Cause

The number of pump availability flags is not zero or the same as the number of pumps in the pump station

Advice

Enter availability flag values for all pumps in the pump station or remove all availability flags.

If availability flags are not specified, it will be assumed that the pump is available.

E0419

There must be at least one profile entry for PROF mode

Info

Pump Station name

Cause

There is no data in the Date & Time/Target Pressure Depth fields.

Advice

Enter values into Date & Time/Target Pressure Depth grid for Pump Station

E0420

Target_pressure_depth (<index>) Value exceeds reservoir depth (<reservoir depth>)

Info

Pump Station name. Number of entry in Date & Time/Target Pressure Depth grid. Control Node (Reservoir) depth.

Cause

May occur at a pump station where mode of control used is PROF. The target pressure depth specified is outside the reservoir depth range of the Control Reservoir

Advice

Check target pressure depth specified in Date & Time/Target Pressure Depth grid.

E0422

Pump <pump no.> Date & Time <row no.> Dates should be in ascending order

Info

Pump Station name. Number of entry in time varying profile grid

Cause

May occur at a pump station where mode of control used is AUTO, PROF or TFLW.

There are duplicate date-times in the time varying profile grid, or date-time has not been specified for rows in the time varying profile grid.

(If there is only one row in the time varying profile grid, it is not necessary to specify a date-time. If there are multiple rows in the grid, date-time must be specified for each row.)

Advice

Review time varying profile data

E0424

Too many profile entries <limit>

Info

Name of control valve. Maximum number of entries permitted.

Cause

There are too many entries in the profiles

Advice

Reduce number of profile entries to within limit

E0425

depth (<index>) Value exceeds reservoir depth; Value exceeds reservoir depth

Info

Name of control valve. Profile grid entry index (where appropriate).

Cause

May occur when a valve is controlled as a Pressure Controlled Valve (PCV), a Pressure/Flow Valve (PFV) or an Open/Closed Valve (OCV).

For PCV/PFV: depth specified is greater than the control node (reservoir) depth.

For OCV: Pressure Open/Closed value is greater than the control node (reservoir) depth.

Advice

Check depth/pressure entries for the valve

E0430

Pump <index>: % Speed On must be between % Speed Off and 100

Info

Pump Station name

Cause

Applies to pump stations of Control Mode AUTO or PROF.

% Speed On value is less than % Speed Off value, or % Speed On value is greater than 100.

(Reverse logic cannot be applied to pumps controlled by pump speed.)

Advice

Check the % Speed On and % Speed Off values

E0430

Pump <index>: % Speed Off must be between 0 and % Speed On

Info

Pump Station name

Cause

Applies to pump stations of Control Mode AUTO or PROF.

% Speed Off value is less than 0 or greater than % Speed On value.

(Reverse logic cannot be applied to pumps controlled by pump speed.)

Advice

Check the % Speed On and % Speed Off values

E0432

Pump <index> (variable speed): On/Off must be set.

Info

Pump Station name

Cause

Applies to pump stations of Control Mode AUTO or PROF.

The pump identified in the error message is a variable speed pump. Pressure on/off values must be specified.

The Target Deviation On / Target Deviation Off fields for a PROF pump station, or the Pressure On / Off fields for an AUTO pump station, are not set or are set to equal values.

Advice

Check the On and Off values

E0435

Pump <index> (fixed speed): On/Off must be set. (No variable speed pumps present.)

Info

Pump Station name

Cause

Applies to pump stations of Control Mode AUTO, PROF or TFLW.

The pumping station does not include a variable speed pump and the

Target Deviation On / Pressure On and Target Deviation Off / Pressure Off values for a fixed speed pump in the station are equal or not set.

Advice

Check the On and Off values

E0436

Pump <index> (fixed speed): must set either On/Off or %speed-on/off

Info

Pump Station name

Cause

Applies to pump stations of Control Mode AUTO or PROF.

The identified fixed speed pump in the pumping station does not have (Target Deviation) On / Off or % Speed On / Off values set.

(Note: On / Off fields with equal values are treated as unset.)

Advice

Check the On and Off values

E0437

Pump regulation mixes normal and reverse logic

Info

Pump Station/Control Valve name

Cause

Applies to pump stations of Control Mode AUTO or PROF or control valves of Mode OCV.

For pump stations:

Target Deviation On / Pressure On is greater than Target Deviation Off / Pressure Off for some pumps in the pumping station but less than Target Deviation Off / Pressure Off for others.

For valves:

Pressure Open is greater than Pressure Closed for some entries in the Control data grid but less than Pressure Closed for others.

Advice

For pump stations:

Check the On and Off values

For valves:

Check the Pressure Open and Closed values

E0504

The number of entries is not the same as for the network

Info

Pump Station name

Cause

For pumping stations controlled using AUTO, PROF or TFLW modes, the number of entries in the Pump Initial Status grid is not the same as the number of pumps in the pump station

Advice

Check number of Pump Initial Status entries

E0516

Cannot find this link in the network

Info

Control Valve name

Cause

The Control Pipe specified does not exist in the network or has not been specified.

Advice

Check the Control Pipe field.

E0524

Initial depth cannot be greater than reservoir depth <reservoir depth>

Info

Reservoir name

Cause

Value of initial depth is greater than depth specified

Advice

Check initial depth and reservoir depth values are correct

E0542

Cannot find this node in the network

Info

Control Valve name

Cause

Applicable to valves of type: PRV, PCV, PFV, PSV and FMV:

Control Node has not been specified or does not exist in the network

Advice

Check Control Node has been specified

E0871

No Pumping Stations (or Control Valves) chosen for Cost Management

Info

No additional information

Cause

Applicable to Cost Management Simulations and BalanceNet Simulations.

None of the Pump Stations or Control Valves in the network have been selected for optimisation (i.e. have the Cost Management box checked).

Advice

Check that the Control Data being used in the simulation is as expected.

E0872

Min Volume out of range (0% to 100%)

Info

Reservoir ID

Cause

Applicable to Cost Management Simulations and BalanceNet Simulations.

The Cost Management box has been checked and the Minimum Volume optimisation parameter is less than 0% or greater than 100%.

Advice

Set the Minimum Volume Reservoir control data field to a valid value.

E0873

Max Volume out of range (0% to 100%)

Info

Reservoir ID

Cause

Applicable to Cost Management Simulations and BalanceNet Simulations.

The Cost Management box has been checked and the Maximum Volume optimisation parameter is less than 0% or greater than 100%.

Advice

Set the Maximum Volume Reservoir control data field to a valid value.

E0874

Max Switches must be at least 1

Info

Pump Station ID

Cause

Applicable to Cost Management Simulations and BalanceNet Simulations.

The Cost Management box has been checked and the Max Switches value is less than 1.

Advice

Set the Max Switches Pump Station control data field to a value greater than 1.

E0875

Min On Time cannot be negative

Info

Pump Station ID

Cause

Applicable to Cost Management Simulations and BalanceNet Simulations.

The Cost Management box has been checked and the Min On Time value is negative.

Advice

Set the Min On Time Pump Station control data field to a positive value.

E0876

Min Off Time cannot be negative

Info

Pump Station ID

Cause

Applicable to Cost Management Simulations and BalanceNet Simulations.

The Cost Management box has been checked and the Min Off Time value is negative.

Advice

Set the Min Off Time Pump Station control data field to a positive value.

E0879

For a Turbine type the Mode of Control must be set to "TURB"

Info

Pumping Station name

Cause

The Turbine option has been checked, but the Mode of Control is not set to TURB.

Advice

Set Mode of Control to TURB

E0881

Cost management cannot be used for PST in this control mode

Info

Pump Station ID

Cause

Applicable to Cost Management Simulations and BalanceNet Simulations.

The Mode of Control of this pump station is not supported by the optimiser.

Advice

Uncheck the Cost Management box to run a simulation without optimisation of the pump station.

Change the pump station control mode to PLAN (BalanceNet and Cost Management) or PROF (Cost Management only) and carry out optimisation on the pump station.

E0882

Min Volume greater than Max Volume

Info

Reservoir ID

Cause

Applicable to Cost Management Simulations and BalanceNet Simulations.

The Cost Management box has been checked and the Minimum Volume optimisation parameter is greater than the Max Volume parameter defined for the reservoir.

Advice

Check that the Reservoir Cost Management control values are as expected.

E0883

Target Volume out of range (Min Volume to Max Volume)

Info

Reservoir ID

Cause

Applicable to Cost Management Simulations and BalanceNet Simulations.

The Cost Management box has been checked and the Target Volume value is less than the Min Volume or greater than the Max Volume optimisation parameter defined for the reservoir.

Advice

Check that the Reservoir Cost Management control values are as expected.

E0886

Min On Time longer than simulation period

Info

Pump Station ID

Cause

Applicable to Cost Management Simulations and BalanceNet Simulations.

The Cost Management box has been checked and the Min On Time value is greater than the simulation period

Advice

Check that the Min Off Time value is as expected.

Adjust the simulation period if necessary.

E0887

Min Off Time longer than simulation period

Info

Pump Station ID

Cause

Applicable to Cost Management Simulations and BalanceNet Simulations.

The Cost Management box has been checked and the Min Off Time value is greater than the simulation period

Advice

Check that the Min Off Time value is as expected.

Adjust the simulation period if necessary.

E0888

Control node for pump station used in optimisation should be a reservoir

Info

Pump Station ID

Cause

Applicable to Cost Management Simulations and BalanceNet Simulations.

The Cost Management box has been checked and the Control Node is not a Reservoir node.

Advice

Optimisation cannot be carried out on a Pump Station with a control node that is not a Reservoir node.

Uncheck the Cost Management box to run a simulation without optimisation of the Pump Station.

Change the control node to a Reservoir node if possible to carry out optimisation on the Pump Station.

E0891

Only TCV valves can be used in optimisation

Info

Valve ID

Cause

The Cost Management box has been checked and the Valve is not a Time Controlled Valve (Mode ID = TCV)

Advice

Cost Management cannot be carried out on a Valve that is not of Mode ID 'TCV'.

Uncheck the Cost Management box to run a simulation without optimisation of the valve.

Change the valve to a time controlled valve to carry out optimisation on the valve.

E9001

Value too large. Maximum value is <maximum value>

Info

Object Type. Object name. Field name. Maximum acceptable value

Cause

The maximum acceptable value in the field indicated by the error message has been exceeded.

Advice

Enter a valid value in this field

E9001

Value too small. Minimum value is <minimum value>

Info

Object Type. Object name. Field name. Minimum acceptable value

Cause

The value in the field indicated by the error message is less than the minimum acceptable value

Advice

Enter a valid value in this field

E9002

<field> (<index>) Value too large. Maximum value is <maximum value>

Info

Object Type. Object name. Field name. Field entry index. Maximum acceptable value

Cause

The maximum acceptable value in the field indicated by the error message has been exceeded.

Advice

Enter a valid value in this field

E9002

<field> (<index>) Value too small. Minimum value is <minimum value>

Info

Object Type. Object name. Field name. Field entry index. Minimum acceptable value

Cause

The value in the field indicated by the error message is less than the minimum acceptable value

Advice

Enter a valid value in this field

W0334

Value 0 or missing (will default to Reservoir depth)

Info

Float Valve name

Cause

The Control Depth field of the reported Float Valve is 0 or has not been specified

Advice

Enter a valid Control Depth for the float valve.

If the field is left empty or zero, the depth of the associated Reservoir will be assumed.

W0411

The control strategy for this pump does not turn it on

Info

Pump Station name

Cause

The controls specified are such that none of the pumps in the pump station will be turned on.

Advice

This may be intentional. If not, check the pump controls.

W0413

Profile Times out of range

Info

Object name

Cause

Time varying profile defined lies outside of the Control Start and End Time.

Advice

Check that the Control Time Interval and the time varying profile date-times are as expected.

W0415

Control Levels on/off are equal and will be ignored

Info

Pump Station name

Cause

Applies to pump stations of Control Mode AUTO or PROF.

Pump Station Pressure On / Target Deviation On value = Pressure Off / Target Deviation Off value.

Advice

Check the On / Off values

W0416

Speed (<index>) value is out of range (<minimum speed to maximum speed>)

Info

Pump Station name

Cause

Pump Station pump Initial Speed value < Minimum Speed of pump or > Maximum Speed of pump

Advice

Check Pump properties

W0431

Pump <index>: %Speed Off/On is below minimal speed of a variable pump

Info

Pump Station Name

Cause

Applies to pump stations of Control Mode AUTO or PROF.

% Speed On / Off value for the pump identified is less than the Minimum Speed value for any of the variable speed pumps in the pumping station.

Advice

Check the % Speed On and % Speed Off values

W0433

Pump <index> (fixed speed): On/Off will be ignored because %Speed-on/off is set. (Variable speed pumps are present.)

Info

Pump Station Name

Cause

Applies to pump stations of Control Mode AUTO or PROF.

Both %Speed On / Off and (Target Deviation) On / Off values have been defined for the fixed speed pump identified.

Advice

Check the On and Off values

% Speed On / Off values will supersede (Target Deviation) On / Off values.

W0434

Pump <index>: %Speed On and %Speed Off are equal and will be ignored

Info

Pump Station Name

Cause

Applies to pump stations of Control Mode AUTO or PROF.

% Speed On and % Speed Off values are the same for the pump identified.

Advice

Check the On and Off values

(% Speed values are treated as unset. Pressure On / Off values will be used for pump switching instead.)

W0438

Fixed speed pump regulation using a mixture of pressure and speed criteria.

Info

Pump Station Name

Cause

Applies to pump stations of Control Mode AUTO or PROF.

The pump station includes more than one fixed speed pump. Some of the fixed speed pumps are controlled by speed and others by pressure.

Advice

Check the On and Off values

(% Speed On / Off values will supersede (Target Deviation) On / Off values.)

W0439

Pump regulation uses reverse logic

Info

Pump Station Name

Cause

Applies to pump stations of Control Mode AUTO or PROF.

(Target Deviation) On value is greater than (Target Deviation) Off value.

Advice

Check the On and Off values

(Pressure On value less than Pressure Off value expected.)

W0440

target_pressure_depth(<index>) is unset and will be treated as zero

Info

Pump Station Name

Cause

Applies to pump stations of Control Mode PROF.

A Target Pressure Depth value has not been set

Advice

Check the Target Pressure Depth values

W0881

BalanceNet cost management cannot be used for PST in this control mode

Info

Pump Station ID

Cause

Applicable to BalanceNet Simulations.

The Cost Management box has been checked for a Pump Station with Mode of Control other than PLAN.

Only Pump Stations with Mode of Control PLAN will be optimised when carrying out a BalanceNet simulation.

Advice

For information.

The Pump Station will not be optimised when carrying out a BalanceNet simulation.

W0884

Min Volume above 90%

Info

Reservoir ID

Cause

The value in the Reservoir control field Min Volume (used in Optimisation simulations) is greater than 90%

Advice

For information.

Check that the Min Volume value is as expected.

W0885

Max Volume below 10%

Info

Reservoir ID

Cause

The value in the Reservoir control field Max Volume (used in Optimisation simulations) is less than 10%

Advice

For information.

Check that the Max Volume value is as expected.

W9001

Value above recommended value of 199.00m

Info

Pump Station name. Field name (Pressure On / Pressure Off).

Cause

The recommended maximum value for Pressure On or Pressure Off for the pump station indicated has been exceeded.

Applies to PLAN and FLOW pump stations.

Advice

Check that a valid value has been entered in the Pressure On / Pressure Off field