Notes on keywords
An SQL block can contain a number of clauses separated by semicolons.
The individual blocks can be used to perform the following tasks using the following keywords:
- Clear the selection – CLEAR SELECTION
- Set a scalar variable - LET
- Set a list variable - LIST
- Select objects - SELECT
- Deselect objects (i.e. remove objects from the selection) - DESELECT
- Delete objects - DELETE
- Change the values of fields or variables - SET and UPDATE
- Generate a table of values which can be displayed in a grid or output to a CSV file – SELECT
With the exception of the first 3 of these:
- The current table can be overridden by using the FROM keyword
- The current selection mode (i.e. the state of the ‘apply filter to current selection’ check-box) can be overridden by using the ALL or SELECTED keywords
- The objects to which the action is applied can be filtered by using the WHERE keyword.
Let us now give more information on the keywords:
To clear the selection, use the clause
CLEAR SELECTION
To set a scalar variable, say
LET <variablename> = <value>
To set a list variable, say
LIST <variablename> = <value>, <value>, <value>, <value>
- Select objects
To select objects use the SELECT keyword e.g.
SELECT
SELECT ALL
SELECT SELECTED
SELECT FROM conduit
SELECT ALL FROM conduit
SELECT SELECTED FROM conduit
SELECT WHERE x > 0
SELECT ALL WHERE x > 0
SELECT SELECTED WHERE x > 0
SELECT FROM conduit WHERE conduit_width > 250
SELECT ALL FROM conduit WHERE conduit_width > 250
SELECT SELECTED FROM conduit WHERE conduit_width > 250
If you are selecting from the current table with the current selection mode, the SELECT keyword can be omitted e.g.
x>0
- Deselect objects
To deselect objects use the DESELECT keyword
DESELECT
DESELECT ALL
DESELECT SELECTED
DESELECT FROM conduit
DESELECT ALL FROM conduit
DESELECT SELECTED FROM conduit
DESELECT WHERE x > 0
DESELECT ALL WHERE x > 0
DESELECT SELECTED WHERE x > 0
DESELECT FROM conduit WHERE conduit_width > 250
DESELECT ALL FROM conduit WHERE conduit_width > 250
DESELECT SELECTED FROM conduit WHERE conduit_width > 250
- Delete objects
To delete objects use the DELETE keyword
DELETE
DELETE ALL
DELETE SELECTED
DELETE FROM conduit
DELETE ALL FROM conduit
DELETE SELECTED FROM conduit
DELETE WHERE x > 0
DELETE ALL WHERE x > 0
DELETE SELECTED WHERE x > 0
DELETE FROM conduit WHERE conduit_width > 250
DELETE ALL FROM conduit WHERE conduit_width > 250
DELETE SELECTED FROM conduit WHERE conduit_width > 250
- Change the value of fields or variables
To change the value of fields or variables use the SET keyword. It is possible to set more than one value at a time by separating the assignments with commas.
SET x = x – 100, y = y – 100
SET x = x – 100, y = y – 100 WHERE ground_level > 20
To override the current table and current selection mode the UPDATE keyword should be used
UPDATE ALL SET x = x – 100, y = y - 100
UPDATE SELECTED SET x = x – 100, y = y - 100
UPDATE node SET x = x – 100, y = y - 100
UPDATE ALL node SET x = x – 100, y = y - 100
UPDATE SELECTED node SET x = x – 100, y = y – 100
UPDATE ALL SET x = x – 100, y = y – 100 WHERE ground_level > 20
UPDATE SELECTED SET x = x – 100, y = y – 100 100 WHERE ground_level > 20
UPDATE node SET x = x – 100, y = y - 100100 WHERE ground_level > 20
UPDATE ALL node SET x = x – 100, y = y – 100 100 WHERE ground_level > 20
UPDATE SELECTED node SET x = x – 100, y = y – 100 100 WHERE ground_level > 20
To select a number of values use the SELECT keyword then follow it with the values you wish to output separated by commas.
SELECT node_id ,MAX(us_links.conduit_width), MIN(us_links.conduit_width)
It is possible to override the title given to the column in the grid or CSV file using the keyword AS e.g.
SELECT node_id AS title,MAX(us_links.conduit_width) as mymax,MIN(us_links.conduit_width) as mymin
The title can either be without quotes round it in which case there can be no spaces or non-alphanumeric characters or in quotes e.g.
SELECT node_id AS title,MAX(us_links.conduit_width) as mymax,MIN(us_links.conduit_width) as '£% my min'
It is possible to override the table
SELECT node_id AS title,MAX(us_links.conduit_width) as mymax,MIN(us_links.conduit_width) as mymin FROM node
The results will be displayed in a grid unless a file is specified using the INTO keyword
SELECT node_id AS title,MAX(us_links.conduit_width) as mymax,MIN(us_links.conduit_width) as mymin FROM node INTO FILE 'c:\temp\mynodes.csv'
It is possible to filter the objects that will be reported on using the WHERE keyword
SELECT node_id AS title,MAX(us_links.conduit_width) as mymax,MIN(us_links.conduit_width) as mymin FROM node WHERE MAX(us_links.conduit_width) > 450
It is possible to calculate results aggregated over groups of objects
SELECT MAX(MAX(us_links.conduit_width)) GROUP BY system_type
It is possible to limit the aggregates results reported by using the HAVING keyword
SELECT MAX(MAX(us_links.conduit_width)) GROUP BY system_type HAVING MAX(MAX(us_links.conduit_width))<1000
Supported SQL syntax
The table below lists the SQL syntax supported in this Autodesk product. Additional notes can be found below.
You can refer to the SQL in InfoWorks WS Pro technical paper for comprehensive information on the use of SQL and all the functions supported.
Comment text
Comment text is ignored when the query is executed.
| /* | Start of comment text |
| */ | End of comment text |
Functions
INT(number) |
Integer part of a number. |
FLOOR(number) |
Closest integer less than or equal to the parameter. |
CEIL(number) |
Closest integer greater or equal to its parameter. |
| FIXED(number to convert,number of decimal places) | Given a number and a number of decimal places from 0 to 8, convert the number to a string with that number of decimal places, rounding up or down as appropriate. If the number of decimal places is 0 the string will have no decimal point. |
abs(x) |
Takes the absolute value of x. The function returns x if x >= 0, -x otherwise |
left(s,n) |
Returns the first n characters of the string s, or the whole string if n is greater than the length of the string |
right(s,n) |
Returns the last n characters of the string s, or the whole string if n is greater than the length of the string) |
mid(s,n,m) |
Returns the substring of string s containing m characters starting at position n, counting from 1 as the start position |
len(s) |
Returns the length of the string s |
iif(x,y,z) |
If the expression x is true then returns y otherwise returns z |
| nvl(x,y) | If x is null then returns y otherwise returns x |
subst(s1,s2,s3) |
Replaces the first instance of string s2 in string s1 with string s3 For example: subst(node_id,'01','ND') applied to node ID '01880132', returns 'ND880132' |
gsubst(s1,s2,s3) |
Replaces all instances of string s2 in string s1 with string s3 For example: gsubst(node_id,'01','ND') applied to node ID '01880132', returns 'ND88ND32' |
gensubst(s,regexp,format) |
Replaces string s with the format defined if regular expression regxp matches string s, otherwise returns string s unchanged. For example: gensubst(node_id,'(01)(..)(..)(.*)','ND\2\4a\1') applied to node '01880132', returns 'ND8832a01'
| nl() |
Returns a new-line character For example, to set up a three line note field: SET notes = 'Set'+NL()+'new'+NL()+'line' |
yearpart(s) |
YEARPART is applied to / returns the year of a date. If date is 24/09/2007, YEARPART is 2007. Note: The YEARPART, MONTHPART, and DAYPART functions work on date fields and string fields which are formatted as dates. A zero is returned if the string they are applied to is not a date.
monthpart(s) |
MONTHPART is applied to / returns the month of a date. MONTHPART is 09 if we take the example above. Note: The YEARPART, MONTHPART, and DAYPART functions work on date fields and string fields which are formatted as dates. A zero is returned if the string they are applied to is not a date.
daypart(s) |
DAYPART is applied to / returns the day of a date. In the above example, DAYPART is 24. Note: The YEARPART, MONTHPART, and DAYPART functions work on date fields and string fields which are formatted as dates. A zero is returned if the string they are applied to is not a date.
NOW() |
Function without any parameter defining the present. This function looks at the current date and time of the computer, so that SQL queries with NOW do not have to be rewritten every time before they are executed to make them current. |
DATEPART(date) |
DATEPART returns the date part as a date (e.g. removes any minutes from the dates). |
TIMEPART(date) |
TIMEPART returns the time part of a date as a number of minutes after midnight. |
YEARSDIFF(from,to) |
YEARSDIFF returns the number of complete years between two dates. Note: The YEARSDIFF, MONTHSDIFF, and DAYSDIFF functions ignore any minutes part of the dates in question.
MONTHSDIFF(from,to) |
MONTHSDIFF returns the number of complete months between two dates. Note: The YEARSDIFF, MONTHSDIFF, and DAYSDIFF functions ignore any minutes part of the dates in question.
DAYSDIFF(from,to) |
DAYSDIFF returns the number of complete days between two dates. Note: The YEARSDIFF, MONTHSDIFF, and DAYSDIFF functions ignore any minutes part of the dates in question.
INYEAR(date,number) |
INYEAR returns true if the date is in the year given as a number. Note: If any of the parameters to the INYEAR, INMONTH, INYEARS, and INMONTHS functions are not numbers the function will return false. If the number is not an integer, the number is rounded to the nearest integer.
INMONTH(date,month,year) |
INMONTH returns true if the date is in the year and month given as numbers. Note: If any of the parameters to the INYEAR, INMONTH, INYEARS, and INMONTHS functions are not numbers the function will return false. If the number is not an integer, the number is rounded to the nearest integer.
INYEARS(date,startyear,endyear) |
INYEARS returns true if the date is in a year between the start and end years inclusive. Note: If any of the parameters to the INYEAR, INMONTH, INYEARS, and INMONTHS functions are not numbers the function will return false. If the number is not an integer, the number is rounded to the nearest integer.
INMONTHS(date,startmonth,startyear,endmonth,endyear) |
INMONTHS returns true if the date is between the start month in the start year and the end month in the end year inclusive. Note: If any of the parameters to the INYEAR, INMONTH, INYEARS, and INMONTHS functions are not numbers the function will return false. If the number is not an integer, the number is rounded to the nearest integer.
ISDATE(putative_date) |
If the field is a date because it has come from the database returns true, if it is a string then returns true if it can be converted into a date, otherwise returns false. |
MONTHYEARPART(date) |
MONTHYEARPART returns the string "<month>/<year>". |
YEARMONTHPART(date) |
YEARMONTHPART returns the string "<year>/<date>" |
MONTHNAME(date) |
MONTHNAME returns returns the name of the month (in the current locale). |
SHORTMONTHAME(date) |
SHORTMONTHNAME returns the abbreviated name of the month (as determined by the locale and how Windows abbreviates it). |
DAYNAME(date) |
DAYNAME returns the name of the day (in the current locale). |
SHORTDAYNAME(date) |
SHORTDAYNAME returns the abbreviated day name (as determined by the locale and how Windows abbreviates it). |
| NUMTOMONTHNAME(n) | Returns the month name given an integer from 1 to 12. |
| NUMTOSHORTMONTHNAME(n) | Returns the short version of a month name (e.g. JAN) given an integer from 1 to 12. |
| TODATE(year,month,day) | Returns the date given the year, month and day as integers. |
| TODATETIME(year,month,day,hours,minutes) | Returns the date given the year, month and day as integers. |
List functions
The purpose of these functions is to divide values into ranges, score values, map values onto lists etc.
AREF(n,list) |
AREF, given a list variable list and a number from 1 to the length of list, returns the nth element in the list. |
LEN(list variable) |
LEN returns the number of items in a list variable. |
RINDEX(expression, list variable) |
RINDEX is a function that may only be used if the list is sorted. The purpose of the RINDEX function is essentially to divide values into ‘buckets’. |
LOOKUP(expression, list variable) |
If there are n items in the list and the value of the expression is between 1 and n inclusive, LOOKUP will return the appropriate item from the list. |
MEMBER(expression, list variable) |
MEMBER returns true if the value of the expression is one of the values in the list, false otherwise. |
If the result of the expression is the first value in the list, INDEX will return 1, if it is the value of the 2nd it will return 2, if the result of the expression is not the list this will return 1. |
TITLE(n,list) |
TITLE provide titles for the 'buckets' when RINDEX is used to partition values into a number of ranges. |
Mathematical functions
LOG(x) |
Calculates the log (base 10) of x. |
LOGE(x) |
Calculates the log (base e) of x. |
EXP(x) |
Calculates e^x. |
SIN(x) |
Calculates the sin of x. |
COS(x) |
Calculates the cosine of x. |
TAN(x) |
Calculates the tangent of x. |
ASIN(x) |
Calculates the inverse sin of x. |
ACOS(x) |
Calculates the inverse cosine of x. |
ATAN(x) |
Calculates the inverse tangent of x. |
ATAN2(x,y) |
Calculates the inverse tangent of x / y using the signs of x and y to determine the quadrant. |
GAMMALN(x) |
Returns the LOG (base e) of the Gamma function of x. |
Aggregate functions
Aggregate functions are used to allow the calculation of values based on:
- all the rows of an array field
- all the objects related to the object being queried in a particular fashion
- all the timesteps in the simulation results
ANY |
ANY returns true if the expression is true for any row of the array field e.g. ANY(details.code=’JDS’) will return true if any of the rows of the details array field has the code JDS, false otherwise. The expression within the brackets can contain more than one array field, other fields of the object, constants and non-aggregate functions, and these can all be combined with arithmetic, comparison and logical operators. |
ALL |
ALL returns true if the expression is true for all the rows / related objects / timesteps. |
COUNT |
COUNT counts the number of rows / related objects / timesteps for which the expression is true. |
MAX |
MAX returns the maximum value (number, date or string) for all the rows / related objects / timesteps. |
MIN |
MIN return the minimum value (number, date or string) for all the rows / related objects / timesteps. MAX and MIN both work on numerical, date and string fields. In the case of string fields the comparison between strings is performed based on the language in which your Windows installation is set up. |
AVG |
AVG returns the mean of all non-null values of the expression (numerical only) for all the rows / related objects / timesteps. |
FIRST |
FIRST returns the value of the expression for the first row / related object / timestep. |
LAST |
LAST returns the value of the expression for the first row / related object / timestep. Thus, in calculating the value, one of the records in the array field is considered. |
Arithmetic operators
All of these operators do what you would expect for numbers. <> means "not equal to". In addition, + can be used to concatenate strings. + is the only arithmetic operator that has a special meaning for strings. |
The ^ operator means "raise to the power". For example x^2 means x squared. |
a % b gives the remainder of a / b e.g. year % 10 gives the last digit of the year. |
Logical operators
ANDORNOT |
Self-explanatory |
Other operators
IS NULL |
Evaluates to true if a field is NULL |
IS NOT NULL |
Evaluates to true if a field is not NULL |
LIKE |
The two special characters you can use with LIKE are:
Every other character in a string matches only itself. The matching is DOS like i.e.:
As with DOS, once you hit a * everything is matched. Therefore you can't do things like LIKE '*AB' to find things with AB at the end, or LIKE '*AB*' to find something with AB somewhere in the string. Note that this behaviour of LIKE is different from that in Microsoft Access. |
MATCHES |
MATCHES allows you to carry out more complex searches than the LIKE operator by using regular expressions. The important syntax elements are:
The matching works as follows:
Regular expressions are powerful and you can do far more with them than the basic examples shown above. For more information on regular expressions and their syntax, see this article on Wikipedia. |
Constants
True False NULL |
Self-explanatory |
Aggregate functions (results only)
It is possible to use the aggregate functions over all simulation results instead of just one snapshot by using tsr instead of sim.
DURATION |
DURATION - the time (in minutes) for which the expression is true (results only) |
INTEGRAL |
INTEGRAL - the sum of the expression at each timestep multiplied by the length of the timestep in minutes (results only) |
WHENEARLIEST |
WHENEARLIEST - the earliest time for which the expression is true (results only) |
WHENLATEST |
WHENLATEST - the latest time for which the expression is true (results only) |
EARLIEST |
EARLIEST - the first non-null value of the expression (results only) |
LATEST |
LATEST - the last non-null value of the expression (results only) |
WHENMAX |
WHENMAX - the time at which the expression is at its maximum (results only) |
WHENMIN |
WHENMIN - the time at which the expression is at its minimum (results only) |
Additional notes on using SQL
- The SQL engine does not do much in the way of type checking so you can do a number of potentially useful things, such as:
- SET user_number_1 = x > 390000 will set user_number_1 to 1 for things with x > 390000, 0 for the others, as conditional expressions evaluate to 1 for true and 0 for false.
- SET user_text_1 = z - will set user_text_1 to the z value, note that when you do this, the strings have unnecessary decimal points and decimal places trimmed off, this is so you can take these strings and concatenate other stuff on the end if you like.
- SET user_number_1 = user_text_1 will assign the value if the string is a valid number.
- The behaviour of NULL is slightly complex.
- Essentially NULL is an 'I have no value' value - the grid views work the same way for numbers in that there is a difference between putting 0 in a grid cell for a number and leaving it blank. The 'blank' value is NULL, i.e. the objects with blank cells are the ones that are selected if you do x IS NULL.
- The general rule for SQL is that any operation involving anything and NULL gives the answer NULL e.g.
- 3 + NULL is NULL
- 3 > NULL is NULL
- 3 < NULL is NULL
The SQL engine treats equality slightly differently. x = NULL and x <> NULL do the same as X IS NULL and X IS NOT NULL.
- For strings, an empty string is simultaneously NULL and "'' (empty string). Therefore asset_id IS NULL and asset_id = ''" and len(asset_id)=0 all select things with no asset ID string.
- Boolean fields (fields with check boxes) do not have any concept of NULL.
- You may encounter a parsing error when you have included a field name which starts with a number. It is recommended that you place such field name between [ ] in your SQL query. For example, instead of writing SET 2d_pt_id = subcatchment_id, you can use SET [2d_pt_id] = subcatchment_id.
