UPC window

The UPC window is used to view or edit the components of a UPC scenario. UPC scenarios contain details of the regulators, sensors and rules that control the elements within a network. Each scenario contains a number of simple components, which can be combined to build up complex operating instructions. A UPC scenario is a prerequisite for running a UPC simulation. A UPC scenario is read-only in the UPC window if it has been used in a simulation.

To display the UPC window:

  1. Open the network associated with the UPC scenario whose components you want to view or edit.
  2. In the Model Group window, under UPC Group, right-click the required UPC scenario and select Open.

    Alternatively, from the Explorer window or Model Group window, drag the UPC scenario from the UPC group into the InfoWorks background area.

UPC object representation

The left pane of the UPC window gives a representation of a UPC object.

Item Description
Object tree

Initially shows the global object. Components inserted under the global object can be used by any of the regulators in the scenario.

Regulators can be added by right-clicking Global and selecting Insert regulator. (Despite this use of the global object, the new regulator will be created as a top level node in the object tree.)

For any object in the tree, you can insert dependent components by right-clicking the object, selecting Insert dependent, then selecting the required component. The components are: Range, Logic, Table, Variable, Controller, Rule (not available for the global object), Comment.

Object context menu

A context menu is displayed when you right-click an item in the left pane of the UPC window.

Insert regulator Adds a new regulator to the scenario, selected from the available controls on the current network. Each control can be added to the scenario once only. Regulator definitions are edited in the right pane.
Remove regulator Removes the selected regulator and associated dependents from the scenario.
Rename regulator Allows the regulator name to be changed (only within the UPC window).
Insert dependent Adds a range, logic operator, table, variable, controller, rule, or comment for the regulator that is currently selected. The dependent is defined and edited in the right pane.
Remove dependent Removes the selected range, logic operator, table, variable, controller, rule, or comment.
Select and find in GeoPlan Highlights and zooms in on the selected regulator in the GeoPlan window.
Full validation Checks that the scenario is valid. Errors are listed in a message window.
Simplify logics Negates logic conditions where necessary to simplify the description of the conditions controlling the regulator.
Cut, Copy, Paste

UPC data can be copied between different objects within the UPC scenario, or between different scenarios in different UPC windows. Data is copied via the Windows clipboard, so the two scenarios do not need to be open at the same time. However, the data is stored in a special InfoWorks WS Pro format and so cannot be pasted into other applications.

Regulator definitions

The right pane of the UPC window shows different definitions depending on which element of the UPC object has been selected.

Item Description
Regulator pane

A regulator marks the start of a block of records defining the operation of one regulator structure in the system. Regulators in InfoWorks WS Pro are always valves or pumps. The block can contain rules and local definitions of control point ranges and logic rules. Show pane

Regulator pane

Override other control (checkbox)

If checked, the regulator definition overrides any control data defined for the network object in the control data set.

If unchecked, the regulator definition is disabled and will be ignored. Controls defined for the network object in the control data will be used.

Note: In the left pane of the UPC window, the regulator text is highlighted red if this checkbox is unchecked, and green if it is checked.

Initial

For valves: Initial opening (%). If the initial opening of a valve is left blank, an initial opening of 100% will be assumed.

For fixed speed pumps: ON (greater than zero) or OFF (less than or equal to zero). For variable speed pumps: Speed. If the initial status of a pump is left blank, the pump will be assumed to be OFF initially.

Description

A text description of how the regulator will operate. This description is built up from all the ranges, logic operators, controllers, tables, variables, and rules defined for the regulator.

Controller pane

Controllers indirectly control a regulator in order to achieve a defined setpoint. Show pane

Controller pane

Name

A label that identifies a controller.

Type

This field is applicable only to pressure controlled valves, and describes the controller reaction to an input signal.

Reducing/Downstream: controls valve as a PRV - increase opening if below target and vice versa (default)

Sustaining/Upstream: controls valve as a PSV - reduce opening if below target and vice versa

Sensor

A control point (node or pipe) range that is used to provide the input signal to a controller. The controller will be ignored if the sensor does not point to a valid range or the measurement range is not greater than zero. Only range types of Q-Flow, P-Pressure and Z-Head can be used as the sensor for a controller.

Logic pane

You can combine the output from up to four range or logic operators to give a TRUE or FALSE result. This result can be used as the input to either another logic operator or a rule.

If logic operators are defined under the global object, any regulator definition can access them. Logic operators that are part of a regulator definition are local to that regulator definition. A local definition is used in preference to a global definition with the same label. Show pane

Logic pane

Name

The label that identifies the result of this logic definition.

Operator

A logical operator:

AND

All conditions must be TRUE for the result to be TRUE. Otherwise the result is FALSE.

OR

At least one condition must be TRUE for the result to be TRUE. Otherwise the result is FALSE.

NOT

If the first condition is FALSE the result is TRUE. Otherwise the result is FALSE.

NOR

If all conditions are FALSE then the result is TRUE. Otherwise the result is FALSE.

NAND

If any condition is FALSE then the result is TRUE. Otherwise the result is FALSE.

Dependent Conditions (1 to 4)

Input conditions. Each of the conditions is either the label of a previously-defined range or logic definition, or it is left blank. At least one input condition must be given for the NOT operator and at least two for all other operators.

Range pane

Ranges provide a logical output which is TRUE if the control point variable is within the defined range (between defined minimum and maximum values) and FALSE if it is outside the defined range. You can define the variables at any point in the system; they do not have to be local to a regulator. Show pane

Range pane

Name

A label to identify the range.

Type

The range type. Using an invalid range type will result in the range being ignored.

Type Description Location Units

Z

Head (Level above datum)

Node or Reservoir

Z

DZ

Rate of change of level

Node or Reservoir

DZ

P

Pressure / Depth

Node or Reservoir

HEAD

Q

Flow

Link

Q

REG

Regulator State. Valve percentage opening.

Valve

See Regulators for details

PUMP

Binary number representing which pumps are switched on.

The first pump in the pumping station has a value of 1 if it is on, the second pump has a value of 2 for on, the third a value of 4, the fourth 8 and so on. The value is zero for any pump that is off.

Add up the individual values for all pumps in the pumping station to define which pumps are on or off.

Pump

seconds

VAR

Value of a variable, table, range or logic record.

Name of a previously defined variable, table, range or logic record.

-

T

Time

-

dd/mm/yy-hh:mm

TR

Time repeat

Used for simulations carried out over more than 24 hours.

Minimum and maximum values can be set to be repeated daily, or can be defined by day of the week.

-

hh:mm

Location

Specifies the control point for this range. This should match the label of a node or link in the network. If not, the range will be ignored.

The Distance Downstream field is not used and is always disabled.

Values

Minimum: Minimum numeric range value. If blank, the value defaults to minus infinity.

Maximum: Maximum numeric range value. If blank, the value defaults to infinity.

Time/Date

Minimum: If blank, the time defaults to the start time of the simulation. A time range should start on a major timestep.

Maximum: If blank, the time defaults to the end time of the simulation.

Rule pane

A rule controls the status of a regulator. When the conditions on which a rule depend are TRUE the rule takes effect. Show pane

Rule pane

Condition

The label of a range or logic condition previously defined for this regulator or included in the global definitions.

The condition can be set to _default_. A default rule should be defined before any other rules. The default rule is assumed to be TRUE.

The last TRUE rule for a regulator will be the active rule at a particular time during the simulation.

Type

The rule type defines the way in which the rule operates on the regulator. Rule types are:

Ctrl

Control

This rule uses a local controller.

POS

Position

This rule directly sets a value of the local regulator setting (speed or opening).

ON

Switch on

This rule can be used only with pumps.

OFF

Switch off

This rule can be used only with pumps.

Controller

For a rule using an indirect control this is the label of the controller to be used. The controller record must have already been defined for this regulator or in the global section.

Setpoint Type

Fixed: For a control rule using a controller or for a POS rule this is the required value of the setpoint.

Variable: The name of a previously defined range, variable, or table whose value is used as the setpoint.

Table pane

A table allows you to translate measured input values from the control point to new output values. The input values can be the output from a range, table, or variable. You can define a table within the global section or in regulator definitions. The only limit to the number of tables you can define is the amount of computer memory available. Show pane

Table pane

Name

A label that uniquely identifies the table.

Input Range

The name of a previously defined range, table, or variable. The input range defines the control point at which input values are measured.

Output Measurement

The type of output data to be used as a regulator setting or controller setpoint.

Type

Linear - InfoWorks WS Pro uses linear interpolation between the defined output values in the table data grid. InfoWorks WS Pro linearly extrapolates from the first two values if the input value is less than the first table entry, or from the last two values if the input value is greater than the last table entry.

Step - No interpolation is applied to the output values.

Table data grid

Define the table data here. Enter input values in ascending order. Enter a corresponding output value for each input value. The number of records in a table is limited only by the available memory.

Input

If the input range is a time or time repeat range, you enter values here as a date and time (dd/mm/yy-hh:mm).

For a daily range, enter the time (hh:mm) and leave day, month and year as zero.

For a weekly range, enter the time (hh:mm) and day (dd). Enter 01 for Monday, 02 for Tuesday and so on. Sunday is 07. Leave month and year as zero.

Output

Corresponding output value. This will be used as a regulator setting or a controller setpoint.

Variable pane

A variable allows you to combine values (from a range, table, logic operator, variable, or constant value) to derive another value. All variables are set to zero at the beginning of a simulation. Variable values are preserved from timestep to timestep, so you can use them to accumulate statistics. Variable elements are processed in the order in which you enter them. Show pane

Variable pane

Name

An identifier for the variable. This must not be the same name as a range, logic operator or table. However, you can have several variables with the same variable name; the program evaluates them in the order in which they appear in the scenario.

Measurement

The type of data being measured.

Operator

An operator to determine the way in which values will be combined.

Operator Effect

=

Variable = Argument 1

+

Variable = Argument 1 + Argument 2

-

Variable = Argument 1 - Argument 2

/

Variable = Argument 1 / Argument 2

*

Variable = Argument 1 * Argument 2

IF

If Argument 1 is TRUE, Variable = Argument 2If Argument 1 is FALSE, Variable = Argument 3

TIMER

Sets up the variable as a timer (see below).

The TIMER operator allows you to set up the variable as a timer. The value of the variable is the number of seconds since it was started (excluding pauses). The operation of the timer is as follows:

  • When the variable value is zero the timer is stopped.
  • When Argument 1 is TRUE the simulation will start the timer if it is not running.
  • When Argument 2 is TRUE the simulation will reset the timer variable to zero (stopping it running).
  • When Argument 3 is TRUE the simulation will pause the timer.

Arguments 2 and 3 may be blank.

Arguments

The values to be combined.

Argument type Value

Number

Number

Range name

Range's current value

Table name

Current value from table

Variable name

Variable value

Logic

0 (FALSE) or 1 (TRUE)

Description pane

This pane is used for adding a title to the UPC scenario. Access the pane by clicking the Global record. Show pane

Description pane

Description

The title for the UPC scenario.

Comment pane

This pane is used for adding a remark, as a reminder of the effect of the components. A comment can be inserted at any point in the scenario. Show pane

Comment pane

Comment

A remark relating to the current scenario, a regulator, or a component.

Update (button) Validates the data on the current pane, then updates the scenario with the validated data. You will see a message window if the data does not pass validation. These changes are not saved unless you subsequently click the Save All button (or click Yes in the prompt when you attempt to close the UPC window without saving the changes).
Save All (button)

Available if one or more panes have been updated but the scenario has not been saved. Saves all the updates made to the scenario. If updates have been made to the scenario but you have not saved them before attempting to close the UPC window, you will prompted to save them.

Note: Changes that are not validated using the Update button will be lost if you close the UPC window.