The Variable Refrigerant Flow (VRF) loop has a VRF condenser. As an option, the condenser may be water-cooled, in which case it is attached to a condenser loop.
Required Objects
The VRF loop must have the following property.
- It must have at least one VRF Fan Coil Unit attached to the loop.
Design Assumptions
- The VRF Loop has the following default temperature assumptions.
| Property | Value | Notes |
| Rated cooling COP | 3.3 | |
| Rated heating COP | 3.5 | |
| Minimum outdoor air temperature in heating | -20°C | |
| Low temperature loop return temperature | 15.5556°C | Set by hot water loop if hot water coil is used in system |
Heating Coil
The heating coil has the following assumptions.
| Coil leaving air temperature | 40°C |
Supplemental Heating Coil
This is an electric resistance coil with an efficiency of 1.0
Supply Fan
The supply fan has the following properties.
| Pressure rise | 250 Pa | |
| Total efficiency | 70% | |
| Motor efficiency | 90% |