You can use the Demand Factor dialog to create and apply demand factor types.
- Click Manage tab
Settings panel
MEP Settings drop-down
Demand Factors. - Click
to create a new demand factor or select an existing one. - Assign a demand factor using one of the following methods:
Apply a constant demand factor
- For Calculation method, select Constant.
- Accept 100% or enter another demand factor percentage.
You can apply a constant demand factor to the loads regardless of their values. A constant demand factor is the default for any newly created demand factor, and the default calculation method if a demand factor is not specified for a load classification.
Apply a demand factor based on a total quantity
- For Calculation method, select By quantity.
- For Calculation options, select Total at one percentage.
- Click
to add row(s) for additional objects. The table displays the demand factor for each row of objects.
You can assign the demand factor to be based on the number of connected objects. For example, if there are two items, all loads are calculated at 100%. If there are ten items, then all loads are calculated at 65%.
Apply a demand factor based on quantity ranges
- For Calculation options, select Incrementally for each range.
- Click
to add row(s) for additional objects. Each range represented by a row will be summed.
- The table displays the demand factor for each row of objects.
You can assign the demand factor to be based on a percentage that varies as the quantity of objects increases. You can specify that the demand factors are calculated incrementally for different ranges.
For example, you can specify a demand factor for the largest 60 connected loads, and then specify another demand factor for the next 40 largest loads (61 to 100, etc.).
Assign a demand factor based on total load
- For Calculation method, select By load.
- Click
to add row(s) for range of loads. The table displays the demand factor for each row of loads.
You can assign a demand factor based on the total number of objects attached to a panel. Total load calculates the entire load at that demand factor.
For example, if the total load is under 100 VA the loads are calculated at a demand factor of 100%. If the total load is 300 VA, then the loads are calculated at 65%.
Apply a demand factor based on ranges of loads
- Click
to add row(s) for range of loads. Each range represented by a row is summed.
You can assign demand factors that are calculated incrementally for different ranges of loads.
For example, you can specify a demand factor of 50% for the range between 0 to 20,000 VA, and a demand factor of 25% for the range between 20,001 and 30,000 VA.
- Optionally, select Add an additional load to the calculated result.