VAV w/WC & GAS

VAV with Water-Cooled Chiller with Gas Boiler Heat and Reheat - This system consists of a Variable Air Volume Air Handling Unit (AHU) served by a primary only chilled water loop and a primary only hot water loop. The VAV AHU includes a mixing box, a hot water coil and a chilled water coil. Each conditioned thermal zone is served by a single duct VAV box with a hot water reheat coil. The default ASHRAE Standard used to set the efficiency of regulated equipment is ASHRAE 90.1-2016.

system diagram

Water Cooled Chiller:

Quantity: 1

Capacity: Auto-sized

Compressor Type (Screw, Centrifugal or Scroll compressor), based on capacity

Controls: Based on Capacity and ASHRAE Standard

Efficiency: Based on Capacity and ASHRAE Standard

Chilled Water Pumps:

Quantity: 1

Design Flow: Auto-sized

Type: Variable Speed, 30% minimum flow

Efficiency: Based on design flow and ASHRAE Standard

Hot Water Boiler:

Quantity: 1

Capacity: Auto-sized

Type: Natural Gas, Non-Condensing

Controls: Based on Capacity and ASHRAE Standard

Efficiency: Based on Capacity and ASHRAE Standard

Hot Water Pumps:

Quantity: 1

Design Flow: Auto-sized

Type: Variable Speed, 30% minimum flow

Efficiency: Based on Design flow and ASHRAE Standard

ERV:

Quantity: (1) If required, based on Outside Air Flow, Design Flow and ASHRAE Standard Requirements

Design Flow: Auto sized

Controls: Based on Climate Zone and ASHRAE Standard

Effectiveness: Based on Design Airflow, % Outside Air, Climate Zone and ASHRAE Standard

VAV AHU:

Controls: Based on Design Airflow, Climate Zone and ASHRAE Standard

Airside Economizer Type and Controls: Based on Fan Design Airflow, % Outside Air, Climate Zone and ASHRAE Standard

VAV AHU Fans:

Quantity: 1

Design Airflow: Auto-sized

Efficiency: Based on Design Airflow and ASHRAE Standard

VAV Boxes:

Quantity: 1 per thermal zone

Reheat Coil Type: Hot Water

Zone Airflow: Auto sized

VAV Box Controls: Based on Zone Airflow and ASHRAE Standard