Parameters of the seismic simplified analysis according to the equivalent lateral force method depend on a seismic code and a method of defining values of the fundamental periods selected in the Seismic Analysis dialog.
The fundamental period T1 is calculated according to the equation 4.6:
T1 = Ct * H3/4
where:
Ct - building period coefficient depending on the type of seismic-force-resisting system that is used (given by the code)
H - structure height (m) defined by difference between Structure range and Reference level
Only T1 - user defined fundamental period on both directions is to be defined.
According to this method you can calculate the exact value for both X and Y directions. If the option Periods with maximal mass participation is off in the Seismic Analysis dialog, the first mode in direction where more masses is active. If this option is on, one of modes, which fulfill limitations and most masses, is active in the direction
Code parameters
To complete the seismic analysis according to the rules given in a code, define the following parameters.
ag = γ × agR
If the Envelope option is selected, the Parameters button becomes accessible; click it to open the Spectrum Envelope dialog.
Base shear
Base shear force is calculated according to the formula:
Fb = Sd(T1) * m * λ (4.5)
Sd(T1) - value of design spectrum of response for period T1 according to the point 3.2.2.5
m - total mass of the building according to 3.2.4(2)
λ - correction factor, (0.85 or 1.0) set automatically basing on the Clause 4.3.3.2.2
Force distribution is performed according to the formula:
Fi = Fb * zi * mi / (Σ zj * mj) (4.11)
i=1.. storeysCount; j=1.. storeysCount
z - distance from reference level to mass position (appropriate floor)
m - mass according to 3.2.4(2)