Revit calculates the wire sizes for power circuits based on the size specified for circuit protection, voltage drop calculation, and correction factor.
Wire sizes are defined in the Electrical Settings dialog.
The voltage drop for each circuit is reported as line-to-line for 2-pole (single phase) and 3-pole (three phase) circuits. The voltage drop is reported as line-to-neutral for 1-pole circuits.
In this example, the following wire type settings are specified for two circuits created in the project, carried in steel conduit.
| Material | Temperature Rating | Insulation | Max Size | Neutral Multiplier | Neutral Required | Neutral Size | Conduit Type |
| Copper | 90 C | THHN | 500 MCM | 1.5 | Yes | Hot Conductor | Steel |
| Copper | 75 C | THWN | 500 MCM | 1.0 | Yes | Hot Conductor | Steel |
| Circuit | Power Factor | Voltage | Load | Poles | Rating | Wire Type | Ambient Temperature | Length of the Wiring Run |
| Feeder | 0.8 | 240 V | 12 kVA | 2 | 50A | THHN | 80 F | 100 ft. |
Preliminary sizing for the wiring package for circuit 1 is 2-#8, 1-#6, and 1-#10. However, the sizing must consider the correction factor (based on the ambient temperature) and support less than a 2 percent voltage drop at the furthest fixture from the source.
VD = (100 ft. *1.326 * 50A)/1000 = 6.63 V
6.63/240 = 0.027625 = 2.7625% which exceeds the 2 percent allowable voltage drop.
VD = (100 ft. * 0.860 * 50A)/1000 = .3
.3/240 = 0.017917 = 1.7917% within the 2 percent allowable voltage drop.
The wiring package is adjusted to 2-#6, 1-#4, 1#8.
| Branch | 0.9 | 208 V | 24 kVA | 3 | 70A | THHN | 80 F | 150 ft. |
The neutral conductor is sized as 1- 1/0 (0.0829065680 sq. in.).
Before considering voltage drop and ambient temperature, the wiring package consists of 3-#6, 1-1/0, and 1-#6.
Working in reverse from the 2 percent allowable voltage drop and solving for impedance:
The hot conductors are resized as 3-#1.
The neutral conductor is resized to #4 wire (1.5 * 0.0206119720 sq. in. = 0.030917958 sq. in.).
The #6 ground conductor (0.0206119720 sq. in.) must be changed in proportion to the change in the hot conductors:
The ground conductor is resized to #4 wire.
The wiring package is adjusted to 3-#1, 1-#4, 1#4.
For the purposes of Voltage Drop calculations, Revit always assumes Copper conductors. The volt loss tables below are consistent with the Cooper Bussmann® Selecting Protective Devices Handbook. The values indicate the line-to-line voltage drop per 1000 Amp Feet for three phase and single phase circuits. For line to neutral voltage drop on three phase systems, divide by 1.73; for single phase systems, divide by 2.
| Conduit | Wire Size | Three Phase | Single Phase | ||||||||
| Power Factor (%) | 100 | 90 | 80 | 70 | 60 | 100 | 90 | 80 | 70 | 60 | |
| Steel | 14 | 5.369 | 4.887 | 4.371 | 3.848 | 3.322 | 6.2 | 5.643 | 5.047 | 4.444 | 3.836 |
| 12 | 3.464 | 3.169 | 2.841 | 2.508 | 2.172 | 4 | 3.659 | 3.281 | 2.897 | 2.508 | |
| 10 | 2.078 | 1.918 | 1.728 | 1.532 | 1.334 | 2.4 | 2.214 | 1.995 | 1.769 | 1.54 | |
| 8 | 1.35 | 1.264 | 1.148 | 1.026 | 0.9 | 1.56 | 1.46 | 1.326 | 1.184 | 1.04 | |
| 6 | 0.848 | 0.812 | 0.745 | 0.673 | 0.597 | 0.98 | 0.937 | 0.86 | 0.777 | 0.69 | |
| 4 | 0.536 | 0.528 | 0.491 | 0.45 | 0.405 | 0.62 | 0.61 | 0.568 | 0.519 | 0.468 | |
| 3 | 0.433 | 0.434 | 0.407 | 0.376 | 0.341 | 0.5 | 0.501 | 0.47 | 0.434 | 0.394 | |
| 2 | 0.346 | 0.354 | 0.336 | 0.312 | 0.286 | 0.4 | 0.409 | 0.388 | 0.361 | 0.331 | |
| 1 | 0.277 | 0.292 | 0.28 | 0.264 | 0.245 | 0.32 | 0.337 | 0.324 | 0.305 | 0.283 | |
| 1/0 | 0.207 | 0.228 | 0.223 | 0.213 | 0.2 | 0.24 | 0.263 | 0.258 | 0.246 | 0.232 | |
| 2/0 | 0.173 | 0.196 | 0.194 | 0.188 | 0.178 | 0.2 | 0.227 | 0.224 | 0.217 | 0.206 | |
| 3/0 | 0.136 | 0.162 | 0.163 | 0.16 | 0.154 | 0.158 | 0.187 | 0.188 | 0.184 | 0.178 | |
| 4/0 | 0.109 | 0.136 | 0.14 | 0.139 | 0.136 | 0.126 | 0.157 | 0.162 | 0.161 | 0.157 | |
| 250 | 0.093 | 0.132 | 0.128 | 0.129 | 0.128 | 0.108 | 0.142 | 0.148 | 0.149 | 0.148 | |
| 300 | 0.077 | 0.108 | 0.115 | 0.117 | 0.117 | 0.09 | 0.125 | 0.133 | 0.135 | 0.135 | |
| 350 | 0.067 | 0.098 | 0.106 | 0.109 | 0.109 | 0.078 | 0.113 | 0.122 | 0.126 | 0126 | |
| 400 | 0.06 | 0.091 | 0.099 | 0.103 | 0.104 | 0.07 | 0.105 | 0.114 | 0.118 | 0.12 | |
| 500 | 0.05 | 0.081 | 0.09 | 0.094 | 0.096 | 0.058 | 0.094 | 0.104 | 0.109 | 0.111 | |
| 600 | 0.043 | 0.075 | 0.084 | 0.089 | 0.092 | 0.05 | 0.086 | 0.097 | 0.103 | 0.106 | |
| 750 | 0.036 | 0.068 | 0.078 | 0.084 | 0.088 | 0.042 | 0.079 | 0.091 | 0.097 | 0.102 | |
| 1000 | 0.031 | 0.062 | 0.072 | 0.078 | 0.082 | 0.036 | 0.072 | 0.084 | 0.09 | 0.095 | |
| Non-Magnetic | 14 | 5.369 | 5.876 | 4.355 | 3.83 | 3.301 | 6.2 | 5.63 | 5.029 | 4.422 | 3.812 |
| 12 | 3.464 | 3.158 | 2.827 | 2.491 | 2.153 | 4 | 3.647 | 3.264 | 2.877 | 2.486 | |
| 10 | 2.078 | 1.908 | 1.714 | 1.516 | 1.316 | 2.4 | 2.203 | 1.98 | 1.751 | 1.52 | |
| 8 | 1.35 | 1.255 | 1.134 | 1.01 | 0.882 | 1.56 | 1.449 | 1.31 | 1.166 | 1.019 | |
| 6 | 0.848 | 0.802 | 0.731 | 0.657 | 0.579 | 0.98 | 0.926 | 0.845 | 0.758 | 0.669 | |
| 4 | 0.536 | 0.519 | 0.479 | 0.435 | 0.388 | 0.62 | 0.599 | 0.553 | 0.502 | 0.448 | |
| 3 | 0.433 | 0.425 | 0.395 | 0.361 | 0.324 | 0.5 | 0.49 | 0.456 | 0.417 | 375 | |
| 2 | 0.329 | 0.33 | 0.31 | 0.286 | 0.259 | 0.38 | 0.381 | 0.358 | 0.33 | 0.3 | |
| 1 | 0.259 | 0.268 | 0.255 | 0.238 | 0.219 | 0.3 | 0.31 | 0.295 | 0.275 | 0.253 | |
| 1/0 | 0.207 | 0.22 | 0.212 | 0.199 | 0.185 | 0.24 | 0.254 | 0.244 | 0.23 | 0.214 | |
| 2/0 | 0.173 | 0.188 | 0.183 | 0.174 | 0.163 | 0.2 | 0.217 | 0.211 | 0.201 | 0.188 | |
| 3/0 | 0.133 | 0.151 | 0.15 | 0.145 | 0.138 | 0.154 | 0.175 | 0.173 | 0.167 | 0.159 | |
| 4/0 | 0.107 | 0.127 | 0.128 | 0.125 | 0.121 | 0.124 | 0.147 | 0.148 | 0.145 | 0.14 | |
| 250 | 0.09 | 0.112 | 0.114 | 0.113 | 0.11 | 0.104 | 0.129 | 0.132 | 0.131 | 0.128 | |
| 300 | 0.076 | 0.099 | 0.103 | 0.104 | 0.102 | 0.088 | 0.114 | 0.119 | 0.131 | 0.128 | |
| 350 | 0.065 | 0.089 | 0.094 | 0.095 | 0.094 | 0.076 | 0.103 | 0.108 | 0.11 | 0.109 | |
| 400 | 0.057 | 0.081 | 0.087 | 0.089 | 0.089 | 0.066 | 0.094 | 0.1 | 0.103 | 0.103 | |
| 500 | 0.046 | 0.071 | 0.077 | 0.08 | 0.082 | 0.054 | 0.082 | 0.09 | 0.093 | 0.094 | |
| 600 | 0.039 | 0.065 | 0.072 | 0.076 | 0.077 | 0.046 | 0.075 | 0.083 | 0.087 | 0.09 | |
| 750 | 0.032 | 0.058 | 0.065 | 0.07 | 0.072 | 0.038 | 0.067 | 0.076 | 0.08 | 0.083 | |
| 1000 | 0.025 | 0.051 | 0.059 | 0.063 | 0.066 | 0.03 | 0.059 | 0.068 | 0.073 | 0.077 | |
The wire types table lists wire types that are provided with Revit.
| Copper | Aluminum | ||||
| 60 C | 75 C | 90 C | 60 C | 75 C | 90 C |
| TW | FEPW | TA | TW | RH | TA |
| UF | RH | TBS | UF | RHW | TBS |
| RHW | SA | THHW | SA | ||
| THHW | SIS | THW | SIS | ||
| THW | FEP | THWN | THHN | ||
| THWN | FEPB | XHHW | THHW | ||
| USE | MI | USE | THW-2 | ||
| ZW | RHH | THWN-2 | |||
| RHW-2 | RHH | ||||
| THHN | RHW-2 | ||||
| THHW | USE-2 | ||||
| THW-2 | XHH | ||||
| THWN-2 | XHHW-2 | ||||
| USE-2 | ZW-2 | ||||
| XHH | |||||
| XHHW | |||||
| XHHW-2 | |||||
| ZW-2 | |||||
Revit specifies hot wire sizes according to the following table of basic wire sizes.
| Copper | Aluminum | ||||||
| Size | Temperature Rating | Temperature Rating | Size | ||||
| 60 C | 75 C | 90 C | 60 C | 75 C | 90 C | ||
| TW, UF | FEPW, RH, RHW, THHW, THW, THWN, USE, ZW | TA, TBS, SA, SIS, FEP, FEPB, MI, RHH, RHW-2, THHN, THHW, THW-2, THWN-2, USE-2, XHH, XHHW, XHHW-2, ZW | TW, UF | FEPW, RH, RHW, THHW, THW, THWN, USE, ZW | TA, TBS, SA, SIS, FEP, FEPB, MI, RHH, RHW-2, THHN, THHW, THW-2, THWN-2, USE-2, XHH, XHHW, XHHW-2, ZW | ||
| 18 | -- | -- | 14 | -- | -- | -- | 18 |
| 16 | -- | -- | 18 | -- | -- | -- | 16 |
| 14 | 15 | 15 | 15 | -- | -- | -- | 14 |
| 12 | 20 | 20 | 20 | 15 | 15 | 15 | 12 |
| 10 | 30 | 30 | 30 | 25 | 25 | 30 | 10 |
| 8 | 40 | 50 | 55 | 30 | 40 | 45 | 8 |
| 6 | 55 | 65 | 75 | 40 | 50 | 60 | 6 |
| 4 | 70 | 85 | 95 | 55 | 65 | 75 | 4 |
| 3 | 85 | 110 | 110 | 65 | 75 | 85 | 3 |
| 2 | 95 | 115 | 130 | 75 | 90 | 100 | 2 |
| 1 | 110 | 130 | 150 | 85 | 100 | 115 | 1 |
| 0 | 125 | 150 | 170 | 100 | 120 | 135 | 0 |
| 00 | 145 | 175 | 195 | 115 | 135 | 150 | 00 |
| 000 | 165 | 200 | 225 | 130 | 155 | 175 | 000 |
| 0000 | 195 | 230 | 260 | 150 | 180 | 205 | 0000 |
| 250 | 215 | 255 | 290 | 170 | 205 | 230 | 250 |
| 300 | 240 | 285 | 320 | 190 | 230 | 255 | 300 |
| 350 | 260 | 310 | 350 | 210 | 250 | 280 | 350 |
| 400 | 280 | 335 | 380 | 225 | 270 | 305 | 400 |
| 500 | 320 | 380 | 430 | 260 | 310 | 350 | 500 |
| 600 | 355 | 420 | 475 | 285 | 340 | 385 | 600 |
| 700 | 385 | 460 | 520 | 310 | 375 | 420 | 700 |
| 750 | 400 | 475 | 535 | 320 | 385 | 435 | 750 |
| 800 | 410 | 490 | 555 | 330 | 395 | 450 | 800 |
| 900 | 435 | 520 | 585 | 355 | 425 | 480 | 900 |
| 1000 | 455 | 545 | 615 | 375 | 445 | 500 | 1000 |
| 1250 | 495 | 590 | 665 | 405 | 485 | 545 | 1250 |
| 1500 | 520 | 625 | 705 | 435 | 520 | 585 | 1500 |
| 1750 | 545 | 650 | 735 | 455 | 545 | 615 | 1750 |
| 2000 | 560 | 665 | 750 | 470 | 560 | 630 | 2000 |
The circuit rating is adjusted according to the correction factors below (circuit rating * correction factor). Then the correct size for the selected wire type is found in the Wire Sizes table.
| Ambient Temperature C | Ambient Temperature F | 60 C | 75 C | 90 C |
| 21-25 | 70-77 | 1.08 | 1.05 | 1.04 |
| 26-30 | 78-86 | 1 | 1 | 1 |
| 31-35 | 87-95 | 0.91 | 0.94 | 0.96 |
| 36-40 | 96-104 | 0.82 | 0.88 | 0.91 |
| 41-45 | 105-113 | 0.71 | 0.82 | 0.87 |
| 46-50 | 114-122 | 0.58 | 0.75 | 0.82 |
| 51-55 | 123-132 | 0.41 | 0.67 | 0.76 |
| 56-60 | 132-140 | -- | 0.58 | 0.71 |
| 61-70 | 141-158 | -- | 0.33 | 0.58 |
| 71-80 | 159-176 | -- | -- | 0.41 |
Ground conductors are sized according to the circuit rating.
| Size | Copper | Aluminum | Size | Copper | Aluminum | |
| 14 | 15 | -- | 250 | 2000 | 1200 | |
| 12 | 20 | 15 | 300 | 2000 | 1200 | |
| 10 | 60 | 20 | 350 | 2500 | 1600 | |
| 8 | 100 | 60 | 400 | 3000 | 2000 | |
| 6 | 200 | 100 | 500 | 4000 | 2000 | |
| 4 | 300 | 200 | 600 | 5000 | 3000 | |
| 3 | 400 | 200 | 700 | 5000 | 3000 | |
| 2 | 500 | 300 | 750 | 5000 | 3000 | |
| 1 | 600 | 400 | 800 | 6000 | 4000 | |
| 1/0 | 800 | 500 | 900 | 6000 | 4000 | |
| 2/0 | 1000 | 600 | 1000 | 6000 | 4000 | |
| 3/0 | 1200 | 800 | 1250 | 6000 | 5000 | |
| 4/0 | 1600 | 1000 |
When a Neutral Multiplier is specified, Revit calculates the neutral conductor size based on the cross sections listed in the following table:
| Size (AWG/kcmil) | Diameter (in.) | Area (sq. in.) | Size (AWG/kcmil) | Diameter (in.) | Area (sq. in.) | |
| 14 | 0.064080 | 0.0032250357 | 300 | 0.5477226 | 0.2356194490 | |
| 12 | 0.080810 | 0.0015288468 | 350 | 0.5916079 | 0.2748893572 | |
| 10 | 0.101900 | 0.0081552613 | 400 | 0.6324555 | 0.3141592653 | |
| 8 | 0.128500 | 0.0129686799 | 500 | 0.7071068 | 0.3929660816 | |
| 6 | 0.162000 | 0.0206119720 | 600 | 0.7745967 | 0.4712388980 | |
| 4 | 0.204300 | 0.0327813057 | 700 | 0.8366600 | 0.5497787144 | |
| 3 | 0.229400 | 0.0413310408 | 750 | 0.8660254 | 0.5890486225 | |
| 2 | 0.257600 | 0.0521172118 | 800 | 0.8944271 | 0.6283185307 | |
| 1 | 0.289300 | 0.0657664432 | 900 | 0.9486833 | 0.7068583471 | |
| 0 | 0.324900 | 0.0829065680 | 1000 | 1 | 0.785398163 | |
| 00 | 0.364800 | 0.1045199453 | 1250 | 1.118034 | 0.981747704 | |
| 000 | 0.409600 | 0.1317678350 | 1500 | 1.224745 | 1.178097245 | |
| 0000 | 0.460000 | 0.1661901110 | 1750 | 1.322876 | 1.374446786 | |
| 250 | 0.5 | 0.19634954085 | 2000 | 1.414214 | 1.570796327 |