Use Circuit Builder to insert a one-line motor circuit and size the wires based on industry standards.
One-Line.dwg contains a one-line bus. This wire is drawn on a wire layer defined as No Wire Numbering. Such a wire layer behaves normally for inserting, breaking, and scooting components. These wires also show up in the from/to report. Wire numbers are not placed on these wires during the Insert Wire Numbers process.
.  Find
	 The Circuit Selection dialog box displays.
The Circuit Configuration dialog box displays.
The Motor Table Not Found dialog box displays. The sample project is set up to use the NEC standard. However, a MOTOR_NEC table is not supplied, only a default MOTOR table.
The Select Motor dialog box displays.
The values are entered in the Motor Setup section. A default wire size, based on the load for the motor, is selected and shown in the Wire Setup section.
The Wire Size Lookup dialog box displays. The minimum wire size is preselected. The size is based on the load for the selected motor.
The values in the Load section are populated with the values from the Motor Setup. The options available within this dialog box are defined in the electrical standards database file, ace_electrical_standards.mdb.
This option directs Circuit Builder to use a de-rating factor for an elevated ambient temperature. These values are defined in the electrical standards database file.
The de-rating factor is extracted from the electrical standards database file and entered in the dialog box. The wire size grid is adjusted based on the new total de-rating factor. Based on this de-rating factor the minimum wire size can change.
This option directs Circuit Builder to consider the length of the wire run in the voltage drop calculation. Additional columns display in the wire selection grid showing Voltage drop, wire KW loss, and wire loss cost estimate.
Circuit Builder displays parallel energy loss calculations to allow you to make better green design decisions. For example, you can oversize the conductors for a motor to reduce conductor heating losses. It results in a higher initial cost, material, and installation labor, which is recovered many times over in reduced energy losses in the wiring during the life of the motor.
The Catalog Browser dialog box displays.
Disconnecting means: Disconnect switch and fuses
Motor starter: Yes
Power factor correction: No
Overloads: None
Terminal strip or connector: None
Cable marker: Yes
Safety disconnect at the load: None
.  Find