Headloss Curves
A headloss condition must be specified at each end of a conduit. The headloss condition represents the extra energy loss due to turbulence at a manhole or junction.
Headloss conditions are specified in the US headloss type and DS headloss type fields for the conduit by selecting a headloss curve. There are a number of built-in headloss curves available; alternatively a user-defined curve may be specified:
The default headloss condition for an individual conduit is the global value specified in the User Defined Defaults; this has a default value of normal manhole headloss.
Note: In order to use the FHWA headloss condition for networks created in versions of InfoWorks ICM prior to version 3.5, it is necessary to validate the network. Validating the network will update the built-in headloss curves to include the FHWA curve type.
Normal and High headloss conditions
The headloss equation used when using Normal or High headloss types is:
where:
Δh = headloss
ku = user defined headloss factor
ks = surcharge ratio coefficient
kv = velocity coefficient
v = flow velocity (m/s)
g = acceleration due to gravity (m/s2)
The user defined headloss factor ku is defined in the US/DS headloss coefficient fields of the conduit.
The option selected in the US/DS headloss type fields of the conduit determines how ks is calculated.
An in-built curve is used to calculate kv.
There are only two situations in which this equation does not apply:
User defined headloss factor ku
The user defined headloss factor is generally used to represent the fact that the amount of change of flow direction at a manhole affects headloss. The amount of change of direction is described by the angle of approach.
Suggested values of ku for various angles of approach are presented below. If a pipe includes several bends, the values of ku should be summed.
Angle of approach ku
30 3.3
60 6.0
90 6.6
>90 8.0
Inference can be used to automatically apply values of ku to the network.
Surcharge ratio coefficient ks
The surcharge ratio coefficient defines the relationship between headloss and the depth of flow in the pipe:
Surcharge ratio = flow depth / conduit height
where:
flow depth = level in the node - invert level of pipe (immediately up or downstream of it)
The relationship between surcharge ratio coefficient ks and surcharge ratio is given by built in curves for normal and high headloss types.
Surcharge ratio Normal headloss factor High headloss factor
0.50
0.001
0.001
0.75
0.05
0.05
1.00
0.10
0.15
1.25
0.20
0.40
1.50
0.26
0.75
1.75
0.23
0.65
2.00
0.20
0.35
2.25
0.15
0.20
2.50
0.15
0.175
2.75
0.15
0.15
3.00
0.15
0.15
The normal manhole headloss is appropriate for well-constructed manholes on pipe systems, or for small open channel systems. There is negligible headloss for links flowing less than half full and small headloss up to just less than full. The actual values for well-constructed manholes are 0.001 up to half pipe full, 0.05 at 3/4 pipe full and 0.1 at pipe full. The headloss varies with the depth of surcharge, but is equivalent to 0.15 times the velocity head (0.15 V2/2g) for large depths of surcharge.
The high manhole headloss is appropriate for badly constructed manholes that are benched only to half pipe height. There is more headloss for depths less than pipe full than for normal manholes, but at large depths headloss is 0.15 V2/2g (as for a normal manhole).
For normal and high headloss types, InfoWorks automatically assumes that the flow is less turbulent at the downstream end of a conduit. It therefore applies a coefficient of –0.1 to the downstream headloss values. (The value is negative due to headloss being calculated with respect to the flow going from manhole to conduit.)
Velocity coefficient kv
The velocity coefficient defines the relationship between headloss and velocity.
For normal and high headloss types, the relationship between kv and v is presented below:
v kv
< -0.02 -0.1
-0.02 to 0.2 -0.1 + (v - (-0.02)) * (1.0 - (-0.1)) / (0.2 - (-0.02))
>0.2 1.0
Fixed headloss condition
The headloss equation used for the fixed headloss condition is the same as for Normal and High headloss conditions:
In the fixed headloss case, the surcharge ratio coefficient ks is always set to 1.
The velocity coefficient kv defining the relationship between headloss and velocity is given as:
v kv
< 0.2 -1
> 0.2 1
This ensures that the loss is in the direction of flow when flow goes from the conduit into the node.
User defined headloss condition
The headloss equation used for a user-defined headloss condition is the same as for Normal and High headloss conditions:
User-defined headloss curves are used to specify the relationship between:
See the Headloss Curve Data Fields topic for further information.
The FHWA headloss type is based on the FHWA Inlet and Access Hole Energy Loss method as described in section 7.1.6.7 of the FHWA HEC 22 Urban Drainage Manual. This headloss type is appropriate for closed conduits connected to manholes.
In order to use this method, the Benching method field should be set in connecting nodes and Headloss type set to FHWA at the appropriate link end of each pipe.
Notes