RTC Example

The following example of Real Time Control compares the volume in two tanks and regulates the discharge from these tanks so that a maximum flow is not exceeded.

Under this scenario, the flow in conduit H.1 and the levels in tanks D and I are monitored. The volume in Tank D and Tank I is calculated by use of tables, and the difference between the volumes is calculated by use of a Variable. The orifices on the outlet to Tank D and on the outlet to Tank I are controlled incrementally depending on the magnitude of flow in conduit H.1 and which tank contains greater volume:

RTC Scenario Summary

Global dependents

Component

Name

Parameters

Effect

RANGE 1

UPFLOW

Range type: Q - flow

Location Link: H.1

Minimum: 0.000 m3/sMaximum: 0.580 m3/s

TRUE if flow in conduit H.1 is between 0.000 m3/s and 0.580 m3/s

RANGE 2

DOWNFLOW

Range type: Q - flow

Location node: H.1

Minimum: 0.580 m3/s

Maximum:

TRUE if flow in conduit H.1 is greater than 0.580 m3/s

RANGE 3

LEVELD

Range type: Z - Height above datum

Location Node: D

Minimum: Maximum:

TRUE if Height above datum at Node D is between - / + infinity

RANGE 4

LEVELI

Range type: Z - Height above datum

Location Node: I

Minimum:

Maximum:

TRUE if Height above datum at Node I is between - / + infinity

TABLE 1

STORED

Measurement: Volume

Input Range: LEVELD

Type: Linear

Input/Output grid: Height above datum vs Volume

Relationship between level and volume at Node D

TABLE 2

STOREDI

Measurement: Volume

Input Range: LEVELI

Type: Linear

Input/Output grid: Height above datum vs Volume

Relationship between level and volume at Node I

VARIABLE 1

COMP

Measurement: Volume

Operator: MINUS

Condition 1: STORED

Condition 2: STOREDI

VARIABLE 1 = Volume at Node D - Volume at Node I

RANGE 5

DMORE

Range type: Variable

Location Definition: COMP

Minimum: 0.000Maximum:

TRUE if Volume at Node D is greater than Volume at Node I

RANGE 6

IMORE

Range type: Variable

Location Definition: COMP

Minimum: Maximum: 0.000

TRUE if Volume at Node I is greater than Volume at Node D

LOGIC 1

UPD

Operator: AND

Condition 1: UPFLOW

Condition 2: DMORE

TRUE if flow in conduit H.1 is between 0.000 m3/s and 0.580 m3/s AND Volume at Node D is greater than Volume at Node I

LOGIC 2

DOWND

Operator: AND

Condition 1: DOWNFLOW

Condition 2: IMORE

TRUE if flow in conduit H.1 is greater than 0.580 m3/s AND Volume at Node I is greater than Volume at Node D

LOGIC 3

UPI

Operator: AND

Condition 1: UPFLOW

Condition 2: IMORE

TRUE if flow in conduit H.1 is between 0.000 m3/s and 0.580 m3/s AND Volume at Node I is greater than Volume at Node D

LOGIC 4

DOWNI

Operator: AND

Condition 1: DOWNFLOW

Condition 2: DMORE

TRUE if flow in conduit H.1 is greater than 0.580 m3/s AND Volume at Node D is greater than Volume at Node I

CONTROLLER 1

UP

Type: INC

Measurement Interval: 300

Measurement interval of orifice increment equals 300 s

Local Dependents

Variable Limiting Discharge Orifice D.2

Component

Name

Parameters

Effect

RULE 1

UPD

Condition: UPDRule type: CTRL

Controller: UP

Setpoint type: FIXED 0.010 m3/s

If the flow in conduit H.1 is between 0.000 m3/s and 0.580 m3/s AND Volume at Node D is greater than Volume at Node I, increment the regulator by 0.01 m3/s every 300 s.

RULE 2

DOWND

Condition: DOWNDRule type: CTRL

Controlloer: UP

Setpoint type: FIXED -0.010m3/s

If the flow in conduit H.1 is greater than 0.580 m3/s AND Volume at Node I is greater than Volume at Node D, decrement the regulator by 0.01 m3/s every 300 s.

Variable Limiting Discharge Orifice I.2

Component

Name

Parameters

Effect

RULE 1

UPI

Condition: UPIRule type: CTRL

Controller: UP

Setpoint type: FIXED 0.010m3/s

If the flow in conduit H.1 is between 0.000 m3/s and 0.580 m3/s AND Volume at Node I is greater than Volume at Node D, increment the regulator by 0.01 m3/s every 300 s.

RULE 2

DOWNI

Condition: DOWNIRule type: CTRL

Controller: UP

Setpoint type: FIXED -0.010m3/s

If the flow in conduit H.1 is greater than 0.580 m3/s AND Volume at Node D is greater than Volume at Node I, decrement the regulator by 0.01 m3/s every 300 s.

RTC Scenario Steps

  1. Insert Ranges to measure flow in conduit H.1

  2. Insert Ranges to measure level at Node D and Node I

  3. Define relationship between level and volume at Node D and Node I by inserting Tables

  4. Insert a variable to calculate the difference between volume at Node D and volume at Node I

  5. Insert Ranges to measure volumes at Node D or Node I

  6. Insert Logics to determine whether flow in conduit H.1 is less than or greater than 0.580 m3/s and whether the volume at Node D or Node I is greater

  7. Insert Controller to define time interval for incrementing regulator settings

  8. Insert Regulators to be controlled

  9. Insert Rules for each Regulator to determine how the orifice opening is to be regulated