The Audit Report allows you to quickly check properties of the design against criteria, check for errors, or test for compliance.
Print Toolbar
The toolbar in the Print Preview dialog offers a convenient way to modify page setup and printer selection, navigate and view specific output pages, change views and find text within the document.
The Print report icon allows selection of the page size, orientation, and margins.
The Save icon allows exporting of the currently drawn set of reports to a variety of formats:
- CSV
- Excel
- RTF
- TIFF
- Web Archive
The Click to open/close document map icon allows to show or hide the document map.
Report Toolbar
The toolbar in the selection control offers a way to modify fonts and page setting used on the report. It also allows you to save and load the report to an Audit Report File (*.idarx), and to clear the report.
Save - Allows you to save the current report in a *.idarx format.
Open - Allows reports to be loaded from a *.idarx file.
Clear- Allows you to remove the current Audit report.
Header Font - Opens a dialog box to allow changing of font, font style, text size, and script.
Select Report Font - Opens a dialog box to allow changing of font, font style, text size, and script for the Audit report.
Reset Fonts - Resets both the header and report font back to default.
Edit Page Settings - Opens a dialog box to allow page settings to be changed. This is linked to the Local Page Setting in file print.
Select all audits - All audits will be selected for auditing in the Audit Selection.
Deselect all audits - All audits will be deselected for auditing in the Audit Selection.
Phase Selection
Select which Phases to audit from the list of phases in your model.
Audits Selection
The audit selection section allows you to check audits to be included in the audit report. Selecting an audit in the audit selection section will display the details of the audit in the selected audit details section.
- Rainfall
- Proportional Velocity
- Entry Loss
- Surcharge
- Flood Warnings
- Discharge Rate
- Discharge Volume
- No Discharge/First Flush
The Audits Selection section when Sanitary Phase is selected:
When Dry Weather phases are the only phase type selected, the following audits will be disabled as they are incompatible with the phase type:
- Rainfall
- Discharge Rate
- Discharge Volume
Additionally Proportional Velocity and Surcharge audits will have the rainfall option disabled.
The Audits Selection section when Dry Weather Phase is selected:
The following audits are available:
| Audit | Input | Validation | Output |
| Rainfall | No input required. | The site must contain at least one selected rainfall type in the Analysis Criteria. | Table of information on currently selected rainfall types in the analysis criteria, including selected return periods and storm durations. This is similar to the rainfall section in the analysis criteria section seen in print preview. |
| Clash Detection | No input required.
Inputs taken from Clash Detection Analysis. |
At least one phase must be selected. |
Audit Details Mirrors the input information. Results A table of clashes, the phases the clash occurs in, the items in the clash, the easting and northing coordinates of the clash, the horizontal separation and vertical separation of the items in the clash. Only the separations that are below the input value are shown. If no clashes are detected the results table is replaced by a “No Clashes Detected” message. |
| Inflow Summary | No input required. | None. | A table of all catchment area and base flow inflows in the site, with the name of the connected item, and (where applicable) the Flow, selected runoff method, the area, percentage impermeable (PIMP), urban creep, adjusted PIMP and analyzed area of each catchment. |
| Outfall Details | No input required. | Each phase must contain at least one outfall. |
A table of outfalls and table of elevation curves produced in outfall details. |
| Pipe Diameter |
Range - The type of range to audit against, choose any combination of less than a maximum and/or greater than a minimum, inclusive and/or exclusive. Min. - The minimum pipe diameter to be considered passable. Max. - The maximum pipe diameter to be considered passable. Can be exposed by changing the Range field. |
Each phase must contain at least one pipe. |
Audit Details Mirrors the input information. Results A table of pipes with diameter outside of the passable range, and the diameter value. If all pipes have diameter within the passable range, the results table is replaced by a simple "All items pass " message. |
| Pipe Length |
Range - The type of range to audit against, choose any combination of less than a maximum and/or greater than a minimum, inclusive and/or exclusive. Min. - The minimum pipe length to be considered passable. Max. - The maximum pipe length to be considered passable. |
Audit Details Mirrors the input information. Results A table of pipes with length outside of the passable range, and the length value. If all pipes have length within the passable range, the results table is replaced by a simple "All items pass " message. |
| Cover Depth |
Range - The type of range to audit against, choose any combination of less than a maximum and/or greater than a minimum, inclusive and/or exclusive. Min. - The minimum cover depth to be considered passable. Max. - The maximum cover depth to be considered passable. |
Each phase must contain at least one pipe connection. |
Audit Details Mirrors the input information. Result Two tables of connections (upstream and downstream), where the cover depths are outside of the passable range. Additional information includes the connection name, associated junctions, invert elevation, cover elevation and connection diameter/height. The audit covers closed connections such as pipes, box culvert and closed custom connections. If all pipes have cover depths within the passable range, the results table is replaced by a simple "All items pass " message. |
| Backdrops |
Range - The type of range to audit against, choose any combination of less than a maximum and/or greater than a minimum, inclusive and/or exclusive. Min. - The minimum backdrop to be considered passable. Max. - The maximum backdrop to be considered passable. |
Each phase must contain at least one hydraulic connection. Each phase must contain at least one junction. |
Audit Details Mirrors the input information. Results A table of backdrop values outside the passable range, and the junction, upstream connection, and downstream connection relevant to the backdrop value. |
| Minimum Invert Elevation | No input required. | Each Phase must contain at least one pipe connection. |
A table of connections with their individual minimum downstream invert elevations, and their current downstream invert elevations. If all connections have invert elevations above or equal to their minimum downstream invert elevation, the results table will be replaced with a "All items pass " message. |
| Manhole Sizes | No input required. | None. |
Audit Details Name of the manhole size library (selected by user from network design criteria). Results Manhole size library details shown above results of report. A table showing a list of manholes outside of the range set by the selected manhole size library. Displayed are their name, diameter and width, along with recommended corrected diameter and width values. If no manholes fall outside of the given range, a message will replace the table state that all items have passed. |
| Pipe Intersections |
Min. Landing Width - The minimum landing width to be considered passable. Min. Benching Width - The minimum benching width to be considered passable. |
Each phase must contain a valid manhole size library. |
Audit Details Mirrors the input information. Results A table of junctions with landing width or benching width below the minimum passable values, and both the current and recommended diameter, offset easting, and offset northing. If all junctions have landing width and benching width greater than the passable minimums, the results table is replaced by a simple "All items pass " message. A second table lists all junctions which could not be audited, alongside the reason(s). A junction cannot be audited for pipe intersection if it does not meet the criteria for offset calculation in the Manhole Auto Size Calculations. |
| Proportional Velocity |
The proportional velocity considered is the Max. Velocity result, available in the Connections Summary. Range - The type of range to audit against, choose any combination of less than a maximum and/or greater than a minimum, inclusive and/or exclusive. Min. - The minimum proportional velocity to be considered passable. Max. - The maximum proportional velocity to be considered passable. Rainfall: All Rainfall / Selected Rainfall: Toggle between auditing all of the rainfall in the analysis criteria, and a single specific rainfall. Rainfall Source drop-down list: Available if Selected Rainfall is chosen. The rainfall to be audited. Rainfall Source button: Edit the selected rainfall. If no rainfall is selected, opens the rainfall manager. Return Period / AEP: Available if Selected Rainfall is chosen, and a rainfall with multiple return periods / AEPs is selected e.g. FEH. The return period to be audited or for ARR the AEP to be audited. |
Each phase must contain at least one connection. Each phase must be analyzed. If a Selected Rainfall is chosen it must also be selected in the analysis criteria. If a Return Period / AEP is chosen it must also be selected in the analysis criteria.
Audit Details Mirrors the input information. Results A table of connections with any proportional velocity outside of the passable range, the proportional velocity value most outside of the range, and the storm at which this value occurs. For ARR 19 Rainfall the proportional velocity is determined by finding which Max Velocity value for the 10 temporal patterns for an AEP / Increase Rainfall / Storm Duration set is the first temporal pattern above to the mean (average) over the 10 results. If all connections have proportional velocities within the passable range, the results table is replaced by a simple "All items pass " message. |
Pipe Full Bore Velocity
(Calculated as part of the Auto Size Calculations , displayed in the Network Design Report ) |
Range - The type of range to audit against, choose any combination of less than a maximum and/or greater than a minimum, inclusive and/or exclusive. Min. - The minimum full bore velocity to be considered passable. Max - The maximum full bore velocity to be considered passable. |
Audit Details Mirrors the input information. Results A table of pipe connections with full bore velocity outside of the passable range, and the full bore velocity value. If all connections have full bore velocities within the passable range, the results table is replaced by a simple "All items pass " message. |
| Entry Loss |
Max. Angle / Entry Loss table - Each row of the table links an angle range to an expected Entry Loss. The angle range will be from the previous rows Max. Angle (exclusive) to the current rows Max. Angle (inclusive). For the first row the range begins at 0 degrees (inclusive). |
Each phase must contain at least one Hydraulic Connection. Each phase must contain at least one Manhole. |
Audit Details Mirrors the Max. Angle / Entry Loss table. Results A table of connections with entry loss which do not match the value expected from the input table, the manhole upstream of the connection, the connection upstream from the manhole that the angle is made with, the value of this angle, the current entry loss, and the recommended entry loss, from the input table. Caveats Only hydraulic connections downstream of manholes will be considered by this audit. The angle given, and used to find an expected entry loss, is the largest angle calculated between the downstream connection being audited and the all upstream connections of the manhole. If all connections considered by the audit have entry losses that match the expected values from the input table, the results table is replaced by a simple "All items pass " message. |
| Surcharge |
Range - The type of range to audit against, choose any combination of less than a maximum and/or greater than a minimum, inclusive and/or exclusive. Min. - The minimum surcharge to be considered passable. Can be exposed by changing the Range field. Max. - The maximum surcharge to be considered passable. Rainfall: All Rainfall / Selected Rainfall: Toggle between auditing all of the rainfall in the analysis criteria, and a single specific rainfall. Rainfall Source drop-down list: Available if Selected Rainfall is chosen. The rainfall to be audited. Rainfall Source button: Edit the selected rainfall. If no rainfall is selected, opens the rainfall manager. Return Period / AEP: Available if Selected Rainfall is chosen, and a rainfall with multiple return periods / AEPs is selected e.g. FEH. The return period to be audited or for ARR the AEP to be audited. |
Each phase must contain at least one hydraulic connection. Each phase must be analyzed. |
Audit Details Mirrors the input information. Results A table of connections with any surcharge depth outside of the passable range, the name of the junction or SWC the connection is from, the surcharge depth value most outside of the range, and the storm at which this value occurs. A table of connections with any proportional velocity outside of the passable range, the proportional velocity value most outside of the range, and the storm at which this value occurs. For ARR 19 Rainfall the surcharge depth is determined by finding which connection’s surcharge value for the 10 temporal patterns for an AEP / Increase Rainfall / Storm Duration set is the first temporal pattern above the mean (average) over the 10 results. Surcharge value is the difference between the Max. Elevation of the Upstream node and the connection's Upstream Crown. If all connections have surcharge depths within the passable range, the results table is replaced by a simple "All items pass " message. |
| Flood Risk Warning | No input required. | Each phase must be analyzed |
A table of junctions and a table of stormwater controls with flood/flood risk warnings, the flooded volume and the (critical) storm at which these values occur For ARR 19 Rainfall the status of a node is determined by finding which Max. Depth value for the 10 temporal patterns for an AEP / Increase Rainfall / Storm Duration set is the first temporal pattern above the mean (average) over the 10 results. If no flood risk warnings are found for either junctions and stormwater controls, a message stating 'No flood risk warnings are reported' will appear instead of a results table. |
| Discharge Rate |
Rainfall - The rainfall to be audited across all phases. Phase - The phase that the proceeding discharge rates table will apply (shows only selected phases from phase selection tree). Discharge Rates - A table of Maximum discharge rates. Each outfall in the phase corresponds to a row in the table. Storms with similar properties (e.g. return period and increase rainfall %) are grouped into columns. Each value is the maximum allowable discharge rate for the outfall during a storm that matches the rainfall. The discharge rates can be calculated using the UK and Ireland Rural Runoff Calculator. The available methods are ICP SUDS/IH 124, ADAS 345, FEH, ReFH2. The calculations are performed per outfall. The outfall needs to be selected in order to calculate the discharge rates. This functionality is only available for UK and Global regions when FEH and FSR rainfalls are used. |
Each phase must contain at least one Inflow. A rainfall must be selected. Each Discharge Rate must be within the valid range. |
Audit Details Mirrors the input information. Results All results (passes and fails) for this audit are recorded in a table with the following columns: outfall, rainfall, audit discharge rate, actual discharge rate, pass / fail. For ARR 19 Rainfall the discharge rate is determined by finding which outfall's Max. Outflow value for the 10 temporal patterns for an AEP / Increase Rainfall / Storm Duration set is the first temporal pattern above the mean (average) over the 10 results. If multiple storms apply to the same rainfall, then only the largest actual discharge rate is shown, and used to determine a pass / fail state. |
Discharge Volume
(Not available with Static Runoff Type - see Analysis Criteria) |
Rainfall - The rainfall to be audited across all phases: Rainfall Source drop-down list: The rainfall to be audited. Rainfall Source button: Edit the selected rainfall. If no rainfall is selected, opens the Rainfall Manager. Return Period / AEP: Return period / AEP to be audited, if the selected rainfall contains multiple return periods e.g. FEH. or multiple AEPs e.g. ARR. Storm - Storm to be audited, filtered by the previously selected rainfall. Phase - The phase that the following discharge volume table will apply (shows only selected phases from the phase selection tree). Discharge Volumes - A table of maximum allowable discharge volumes. Each outfall in the table corresponds to a row in the table, with their maximum allowable volume in the neighbouring column. The discharge volumes can be calculated using the UK and Ireland Rural Runoff Calculator. The only method available is Greenfield Runoff Volume. The calculations are performed per outfall. The outfall needs to be selected in order to calculate the discharge volume. This functionality is only available for UK and Global regions when FEH and FSR rainfalls are used. |
Each phase must contain at least one Inflow. A rainfall must be selected. Each Discharge Volume must be within the valid range. |
Audit Details Mirrors the input information. Results All results (passes and fails) for this audit are recorded in a table with the following columns: outfall, audit discharge volume, actual discharge volume, pass / fail. For ARR 19 Rainfall the discharge volume is determined by finding which outfall's Total Discharge Volume value for the 10 temporal patterns for an AEP / Increase Rainfall / Storm Duration set is the first temporal pattern above the mean (average) over the 10 results. |
Rainfall Depth - The depth of rainfall that will be applied to the rainfall event. Run Time - The run time that will be applied to the rainfall event. |
Each phase must contain at least one Inflow. |
Audit Details Mirrors the input information. Results A list of all outfalls in the phase with any discharge volume. If all outfalls have no discharge, the list is replaced by a simple "All items pass " message. |
Selected Audit Details
The Selected Audit Details section will display any user inputs an audit requires.
Perform Audit
Pressing the
Perform Audit
button will run the selected audits on the selected phases, and generate a report containing the input details and results of each audit. However, before this happens, validation is run to ensure the report can be generated.
After performing the audit, the audit selection control will display the pass / fail state of the audit. If the audit passes in all selected phases, then the audit will be marked as passing. If the audit fails in a single phase then it will be marked as failing. If a selected audit has not been run, or data has changed since the previous audit, then it will be marked as needing to be rerun.
Audit Validation
Before the audit report is generated, validation is run on the selected audits and phases, to ensure that the audit report can be generated. This validation will include logical validation of the audits (e.g. is the maximum value larger than the minimum value?), and simple validation of the site (e.g. are there any connections to audit?).
Analysis
Some audits will require analysis results to be considered valid. When this is the case, a warning will be displayed in the validation form.
This warning appears once, and offers the following solutions:
- Run Analysis Immediately. When Apply or OK is clicked with this solution selected, the site will be analyzed immediately. Any phases selected for auditing that are currently not included in analysis will be set to be included.
- Run analysis if all audits which do not require it are passed. When OK is clicked with this solution selected, if no other validation errors exist, the audits that do not require analysis are run. If all of these audits pass, the analysis will be run, the audits that require analysis will be run, and a full report is generated. If any audits that do not require analysis fail, then a report containing only audits that do not require analysis is generated. Any phases selected for auditing that are currently not included in analysis will be set to be included.
- Only perform audits which do not require analysis results. When OK is clicked with this solution selected, if no other validation errors exist, a report containing only audits that do not require analysis is generated.
If no solution is selected when OK is clicked, if no other validation errors exist, the audits that do not require results are run. Whether all of these pass, or some fail, is reported with the option to run analysis and generate a full report, or to not run analysis and generate a report containing only audits that do not require analysis. Any phases selected for auditing that are currently not included in analysis will be set to be included.
Review Failures
Review Failures
button can be selected to quickly isolate the causes of the failing audit. In most cases, selecting an error here will take you to the appropriate location to resolve the error. In some cases solutions which can be instantly applied are provided.