Transfer Node data fields can be edited on the Transfer Node Grid View of the Nodes Grid or the Transfer Node Property Sheet.
The following table describes all the Transfer Node specific data needed to define a Transfer Node.
Further information, including units details, about all the Network Object fields stored in the database can be found in the data fields topics listed in the Network Data Fields topic.
Fields that are common to the majority of objects can be found in the Common Data Fields topic.
The pages on the Property Sheet are listed below. When the network object has Control Data additional pages may be displayed on the property sheet. These pages are marked as follows:
- additional page displayed when
Control Data is open
Node Definition Page
Transfer Node Flow Control Page
Node Control Page
Water Quality Profile Page
Water Quality Turbidity Profile
Water Quality Age Profile Page
User Page - see Common Data Fields topic for details of user fields
Hyperlinks Page - see Common Data Fields topic for details of hyperlinks fields
Control Notes Page
Notes Page - see Common Data Fields topic for details of notes fields
The Grid column tells you if the data item is available for editing in the grid view.
Transfer Node Data
Database Table Name: wn_transfer_node
Field Name |
Help Text |
Flag |
Grid |
Property Page |
Size |
Precision |
Units |
Database Field |
Data Type |
Default |
Error Lower Limit |
Error Upper Limit |
Warning Lower Limit |
Warning Upper Limit |
Node ID |
Name of the node |
YES |
YES |
1 |
30 |
0 |
node_id |
Text |
Area Code |
The Area Code parameter is used for closer spatial modelling of demand - each node is allocated to an area and demand can then be factored by area. The factor is set using the Demand Scaling Editor. |
YES |
YES |
1 |
30 |
0 |
area |
Text |
Asset ID |
For reference only. Designed as a reference to an asset database, but could be used for anything. |
YES |
YES |
1 |
30 |
0 |
asset_id |
Text |
Fire Zone |
The Fire Zone field is used when checking minimum pressure constraints during Hydrant Testing simulations. Different pressure constraints may be applied to nodes in a given Fire Zone to nodes outside of the Fire Zone. See Fire Flow Data for more details. |
YES |
YES |
1 |
30 |
0 |
fire_zone |
Text |
System Type |
For information. Type in a system type or select an option from the dropdown list:
YES |
YES |
1 |
40 |
0 |
system_type |
Text |
Isolation Area |
Area identifier used to identify groups of objects to be closed when carrying out a Critical Link Analysis. |
YES |
YES |
1 |
30 |
0 |
isolation_area |
Text |
X |
X coordinate |
YES |
YES |
1 |
2 |
XY |
x |
Double |
Y |
Y coordinate |
YES |
YES |
1 |
2 |
XY |
y |
Double |
Elevation |
Elevation above datum of pipe invert. |
YES |
YES |
1 |
2 |
Z |
z |
Double |
-999 |
9999 |
Ground Level |
Elevation above datum of ground surface. |
YES |
YES |
1 |
2 |
Z |
ground_level |
Double |
-999 |
9999 |
Highest Property Level |
Elevation above datum level of the highest property supplied by the node |
YES |
YES |
1 |
2 |
Z |
highest_property |
Double |
-999 |
9999 |
InfoNet Unique ID |
The InfoNet Unique ID and InfoNet Network ID are unique identifiers associated with the corresponding object and network in an InfoNet database. When importing from InfoNet, these identifiers can be copied from the InfoNet database in order to maintain links between the two networks. |
YES |
YES |
NO |
0 |
asset_uid |
GUID |
InfoNet Network ID |
See InfoNet Unique ID |
NO |
YES |
NO |
0 |
asset_network_uid |
GUID |
Transfer Node Control Data
Database Table Name: wn_ctl_transfer_node
Field Name |
Help Text |
Flag |
Grid |
Property Page |
Size |
Precision |
Units |
Database Field |
Data Type |
Default |
Error Lower Limit |
Error Upper Limit |
Flow Factor |
A scaling factor used in conjunction with the Flows Grid to produce actual flow values. (Negative values represent outflow from the system, positive values represent flow into the system.) |
YES |
YES |
2 |
2 |
flow_factor |
1.0 |
Flows |
The Flows Grid contains a list of flows and date/times. These can be entered manually or imported from a Live Data file. (Negative values represent outflow from the system, positive values represent flow into the system.) The Flows Grid can only be viewed and edited on the Transfer Node Flow Control Page and is described fully there. Database Table Name: wn_ctl_transfer_node_flows
NO |
YES |
2 |
0 |
flows |
Array |
Repeat Profile |
Check the Repeat Profile box to repeat a profile (from 00:00 for the selected Repeat Period) for the duration of the simulation. Note:
When using the Repeat Profile option; if the defined profile spans over the selected Repeat Period, the profile will not be repeated. |
YES |
YES |
2 |
0 |
repeat_flows_profile |
Boolean |
1 |
Linear Profile |
This checkbox decides if values in the profile grid are interpolated.
YES |
YES |
2 |
0 |
linear_flows_profile |
Boolean |
0 |
Before First Point |
YES |
YES |
2 |
0 |
before_flows_profile |
Integer |
2 |
After Last Point |
YES |
YES |
2 |
0 |
after_flows_profile |
Integer |
0 |
Repeat Period |
Profile period which will be repeated throughout simulation, if the Repeat Profile box is checked.
YES |
YES |
2 |
0 |
repeat_flows_period |
Integer |
0 |
Live Data Point ID |
Name of the associated Live Data Point, Live Data Feed, or Live Data Composite Feed. Note: Duplicate IDs are shown once.
YES |
YES |
3 |
100 |
0 |
live_data_point_id |
Text |
Water Quality |
The concentration of pollutant entering the system at this node between the Water Quality start and end times. This concentration is fixed, and does not depend on flow rate. Database Table Name: wn_ctl_node_wq_conc
NO |
YES |
4 |
0 |
wq_profile |
Array |
Water Quality |
The flow rate of pollutant entering the system at this node between the Water Quality start and end times. This mass flow is fixed, and does not depend on flow rate. Database Table Name: wn_ctl_node_wq_flow
NO |
YES |
4 |
0 |
wq_flow_profile |
Array |
Initial Concentration |
The initial concentration of the substance being tested at the start of the simulation. Only one substance can be tested at a time. These nodes are inputs to the system. The Initial Concentration represents a continuous input concentration over the period of the simulation. If you have defined a time dependent concentration for a node, the time dependent concentration overrides this value between its start and end times. |
YES |
YES |
4 |
2 |
WN_C |
initial_concentration |
0 |
9999 |
Linear WQ/Age Profile |
YES |
YES |
4 |
0 |
linear_wq_profile |
Boolean |
0 |
Repeat Profile |
YES |
YES |
4 |
0 |
repeat_wq_profile |
Boolean |
0 |
YES |
YES |
4 |
0 |
before_wq_profile |
Integer |
2 |
SourceType |
Method by which concentration profile defined in the Water Quality grid is applied during the simulation.
YES |
YES |
4 |
0 |
wq_source_type |
Integer |
0 |
After Last Point |
YES |
YES |
4 |
0 |
after_wq_profile |
Integer |
0 |
Repeat Period |
YES |
YES |
4 |
0 |
repeat_wq_period |
Integer |
0 |
Initial Age of Water (hr) |
Age of water at the start of the simulation |
YES |
YES |
4 |
2 |
initial_age |
Double |
0 |
| Bulk Coeff Mode |
Method by which Bulk Coefficient is applied to water entering the system at the node:
YES | YES | 4 | 0 | wq_bulk_coeff_mode | Integer | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||
| Bulk Coeff |
Reaction rate parameter used to calculate the change in concentration of a substance as it reacts with material in the bulk flow. The value specified here is applied to water entering the system at the node. The bulk coefficient has a positive value if the concentration of the substance grows over time, and a negative value if the concentration decays over time. |
YES | YES | 4 | 2 | wq_bulk_coeff | Double | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||
| Res Bulk Coeff Mode |
Method by which Res Bulk Coefficient is applied to water entering the system at the node:
YES | YES | 4 | 0 | wq_res_bulk_coeff_mode | Integer | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||
| Res Bulk Coeff |
Reaction rate parameter used to calculate the change in concentration of a substance as it reacts with material in a reservoir. The value specified here is applied to water entering the system at the node. The bulk coefficient has a positive value if the concentration of the substance grows over time, and a negative value if the concentration decays over time. |
YES | YES | 4 | 2 | wq_res_bulk_coeff | Double | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||
| Initial Turbidity |
Initial turbidity at node at start of simulation. See Water Quality - Turbidity Analysis for further information. |
YES | YES | 5 | 2 | WN_TURBIDITY | wq_initial_turbidity | Single | 0 | 9999 | ||||||||||||||||||||||||||||||||||||||||||||||
| Turbidity Source Type |
Method by which turbidity profile defined in the Turbidity grid is applied during the simulation.
YES | NO | 5 | 0 | wq_turb_source_type | Integer | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||
| Turbidity Profile |
Database Table Name: wn_ctl_node_wq_turb A series of time / turbidity pairs that define the turbidity profile at the node. These values can be interpolated, depending on the state of the Linear Profile flag.
NO | NO | 5 | 0 | wq_turbidity_profile | Array | |||||||||||||||||||||||||||||||||||||||||||||||||
| Linear Turbidity Profile |
This checkbox decides if values in the Turbidity profile grid are interpolated:
YES | NO | 5 | 0 | wq_turb_linear_profile | Boolean | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||
| Before First Point (Turbidity) |
YES | NO | 5 | 0 | wq_turb_before_profile | Integer | 2 | ||||||||||||||||||||||||||||||||||||||||||||||||
| After Last Point (Turbidity) |
YES | NO | 5 | 0 | wq_turb_after_profile | Integer | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||
| Repeat Profile (Turbidity) |
YES | NO | 5 | 0 | wq_turb_repeat_profile | Boolean | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||
| Repeat Period (Turbidity) |
YES | NO | 5 | 0 | wq_turb_repeat_peiord | Integer | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||
Notes |
You can keep freeform notes about any object in your network. The notes field can be up to 64,000 characters in size, or about 10 pages of printed text. |
NO |
YES |
8 |
0 |
notes |
Memo |
Reverse Live Data Flow |
Check this box if you want to reverse the flow of Live Data used to populate the Flows Grid described below. |
YES |
YES |
NO |
0 |
reverse_live_data_flow |
Boolean |
Time Dependent Concentration |
This field is obsolete and is not displayed in the interface. This data is now entered in the Water Quality Grid. The field is maintained for backwards compatibility with old CSV data files. If this value is set when the data is imported, InfoWorks will calculate appropriate values for the Water Quality Grid. |
YES |
YES |
NO |
2 |
WN_C |
time_related_concentration |
0 |
9999 |
Node ID |
Name of the node |
YES |
YES |
1 |
30 |
0 |
node_id |
Text |
Asset ID |
YES |
YES |
1 |
30 |
asset_id |
Text |
WQ Start Date & Time |
YES |
YES |
NO |
0 |
wq_start_date_time |
WQ End Date & Time |
YES |
YES |
NO |
0 |
wq_end_date_time |
Exceptional Flow |
A read only check box displayed only on the grid view. This box is checked if data has been entered in the Exceptional Flow Grid on the property sheet |
NO |
YES |
NO |
0 |
exf_selected |
Boolean |
Water Quality |
A read only check box displayed only on the grid view. This box is checked if data has been entered in the Water Quality Grid on the property sheet |
NO |
YES |
NO |
0 |
wqc_selected |
Boolean |
Transfer Node Results
Results fields are displayed on the grid when opened while viewing a replay of a simulation, and on a special results page placed at the front of Property Sheets displayed while viewing a simulation replay.
For details of results fields for nodes, see the Node Results Data Fields topic.
