This enum describes the different demand factor rule types available to the application.
Within a demand factor a rule will be referenced and the user will have to enter values
corresponding to that rule.
Namespace: Autodesk.Revit.DB.Electrical
Assembly: RevitAPI (in RevitAPI.dll) Version: 26.4.0.0 (26.4.0.0)
Syntax
C#
public enum ElectricalDemandFactorRule
Members
| Member name | Value | Description |
| Constant | 0 | This rule will apply a constant demand factor to the loads, regardless of values. It will also be the default for any newly created demand factor, and the default used if a demand factor cannot be found for a load classification. |
| LoadTable | 2 | This rule will apply the demand factor for the total load of attached objects to a panel. It is purely a look-up table. For example, if there are 5000 kVA, the user can specify 125% value is applied. If there are 20,000 kVA, the user can specify 100% value is applied. |
| LoadTablePerPortion | 4 | This rule will apply the demand factor differently for each row in the table. For example, the 3000kVA will have a 100% demand factor applied, the next 9000 will have a 35% factor applied, and the remaining items will have a 25% factor applied. |
| QuantityTable | 1 | This rule will apply the demand factor for the total quantity of attached objects to a panel. It is purely a look-up table. For example, the user can specify that 0 to 2 objects get 100% and 2 to 4 objects get 85% and so on. |
| QuantityTablePerPortion | 3 | This rule will apply the demand factor differently for each row in the table. For example, the first two (largest) items will have a 125% demand factor applied and the remaining items will have a 75% factor applied. |