RTC Logic Example

Logic operators can be used to combine the results from two ranges to give a TRUE or FALSE result.

The following example shows the RTC for controlling the status of a pump depending on the depth in the controlling node and the flow in a downstream conduit.

Under this example, the pump will be switched ON when the level at node K reaches 20mAD, providing the flow in conduit K.2 does not exceed 0.5 m3/s. At other times, the pump will be switched OFF by default.

The RTC is defined by adding components to a pump regulator in the RTC Window Editor.

Component

Parameters

Effect

RANGE 1

Range type: Z - height above datumLocation node: KMinimum: 20Maximum:

TRUE if water level at node K is greater than or equal to 20 mAD

RANGE 2

Range type: Q - flowLocation link: K.2Minimum: Maximum: 0.5

TRUE if flow in conduit K.2 is less than 0.5 m3/s

LOGIC 1

Operator: ANDCondition 1: RANGE 1Condition 2: RANGE 2

TRUE if both RANGE 1 and RANGE 2 are TRUE

RULE 1

Condition: _default_Rule type: OFF

Default status of pump is OFF

RULE 2

Condition: LOGIC 1Rule type: ON

Switch on pump if LOGIC 1 is TRUE

  1. Range 1: Defines node K as a control point with a minimum value of 20 mAD

  2. Range 2: Defines Link K.2 as a control link with a maximum value of 0.5 m3/s

  3. Logic 1: If the level at node K is at or above 20 mAD and the flow in link K.2 is less than 0.5 m3/s, this logic statement is TRUE

  4. Rule 1: Unless subsequent rules are true, the pump will be set to the default status of OFF

  5. Rule 2: Switches the pump ON if the level at node K is at or above 20 mAD and the flow in link K.2 is less than 0.5 m3/s