Pumping station data fields can be edited on the Pumping Station Grid View or the Pump Station Property Sheet.
The following table describes all the data needed to define a Pumping Station.
Further information, including units details, about all the Network Object fields stored in the database can be found in the data fields topics listed in the Network Data Fields topic.
Fields that are common to the majority of objects can be found in the Common Data Fields topic.
Information on Pump and Pump Curve specific data needed to define a Pump can be found in the Pump Curve topic.
The pages on the Property Sheet are listed below. When the network object has Control Data additional pages may be displayed on the property sheet. These pages are marked as follows:
- additional page displayed when
control data
is open
- Pipe Definition Page
- Pumping Station Parameters Page
- Pump Data Page
Pump Control Page
Pump Control Data Page
UPC Script Page
Transient Page - fields only enabled when
InfoWorks TS (Transient System) licence is present
Transient -Turbine Page - fields only enabled when
WQ Turbidity Page
- User Fields Page - see Common Data Fields topic for details of user fields
- Hyperlinks Page - see Common Data Fields topic for details of hyperlinks fields
Control Notes Page
- Notes Page - see Common Data Fields topic for details of notes fields
The Grid column tells you if the data item is available for editing in the grid view.
Pumping Station Data
Database Table Name: wn_pst
Field Name |
Help Text |
Flag |
Grid |
Property Page |
Size |
Precision |
Units |
Database Field |
Data Type |
Default |
Error Lower Limit |
Error Upper Limit |
Warning Lower Limit |
Warning Upper Limit |
From Node ID |
Name of the From Node for this pipe. You can select the name from the dropdown list of existing nodes, or type the name of a node you have yet to add to the model. From and To represent the typical direction of flow for the pipe. Flow will not always be in this direction. |
YES |
YES |
1 |
30 |
0 |
us_node_id |
Text |
To Node ID |
Name of the To Node for this pipe. From and To represent the typical direction of flow for the pipe. Flow will not always be in this direction. |
YES |
YES |
1 |
30 |
0 |
ds_node_id |
Text |
Suffix |
A suffix added by InfoWorks to ensure that all link Ids are unique |
YES |
YES |
NO |
1 |
0 |
link_suffix |
Text |
Area Code |
The Area Code parameter is used for closer spatial modelling of demand - each node is allocated to an area and demand can then be factored by area. The factor is set using the Demand Scaling Editor. |
YES |
YES |
1 |
30 |
0 |
area |
Text |
Asset ID |
For reference only. Designed as a reference to an asset database, but could be used for anything. |
YES |
YES |
1 |
30 |
0 |
asset_id |
Text |
Local Loss Coefficient |
Local Headloss Coefficient used by the Darcy Weisbach roughness formula |
YES |
YES |
1 |
4 |
local_loss |
0 |
10000000000 |
Length |
the length of the bypass pipe |
YES |
YES |
1 |
2 |
L |
length |
0.1 |
99000 |
Diameter |
Internal diameter of the pipe |
YES |
YES |
1 |
1 |
PS |
diameter |
10 |
20000 |
Friction Type |
The formula used for roughness calculations. Can be Darcy Weisbach, Hazen Williams, Colebrook White, or Modified Hazen-Williams. See Pipe Calculations for more information.
YES |
YES |
1 |
2 |
1 |
roughness_type |
Text |
CW - k |
The value for the friction coefficient appropriate to the chosen roughness type. Follow the links above for more details |
YES |
YES |
1 |
6 |
WN_K |
k |
0.001 |
200 |
DW - f |
YES |
YES |
1 |
6 |
darcy_weissbach |
0.002 |
0.09 |
HW - c |
YES |
YES |
1 |
1 |
hazen_williams |
20 |
5000 |
50 |
200 |
Material |
Link material. For reference only. |
YES |
YES |
1 |
10 |
0 |
material |
Text |
Year |
Year of installation. For reference only. |
YES |
YES |
1 |
0 |
year |
Integer |
WQ Bulk Coefficient |
The bulk coefficient, kb, is a reaction rate parameter used to calculate the change in concentration of a substance as it reacts with material in the bulk flow. The bulk coefficient has a positive value if the concentration of the substance grows over time, and a negative value if the concentration decays over time. Note:
Source dependent bulk coefficient values may be specified at individual nodes which may override or scale the pipe Bulk Coefficient value when calculating reaction rates for water that entered the system at the node.
YES |
YES |
1 |
2 |
bulk_coeff |
-0.5 |
-10 |
10 |
WQ Wall Coefficient |
The wall coefficient, kw, is a reaction rate parameter used to calculate the change in concentration of a substance as it reacts with material along the pipe walls. The wall coefficient has a positive value if the concentration of the substance grows in time, and a negative value if the concentration decays in time. |
YES |
YES |
1 |
2 |
wall_coeff |
-0.3 |
-10 |
10 |
Criticality |
The criticality grade of the link. This provides an indication of the significance of the effect on the network if the link fails. This field may be updated from a Critical Link Analysis simulation. |
YES |
YES |
1 |
0 |
criticality |
Integer |
Wave Celerity |
Velocity of propagation of pressure waves caused by sudden increase or decrease in flow rate. See Transients Advisor for more details. |
YES |
YES |
1 |
V |
wave_celerity |
1400 |
Criticality Count |
Number of items (Nodes, Properties, Customer Points or Connections) assessed as critical in the event of link failure. This field may be updated from a Critical Link Analysis simulation. |
YES |
YES |
1 |
0 |
criticality_count |
Integer |
Pressure Rating |
Maximum design working pressure of link |
YES |
YES |
1 |
WN_P |
pressure_rating |
System Type |
For information. Type in a system type or select an option from the dropdown list:
YES |
YES |
1 |
40 |
0 |
system_type |
Text |
Isolation Area |
Area identifier used to identify groups of objects to be closed when carrying out a Critical Link Analysis. |
YES |
YES |
1 |
30 |
0 |
isolation_area |
Text |
Power Consumption |
Average consumption of electrical energy per unit volume of pumped water. |
YES |
YES |
2 |
3 |
WN_ESC |
power_consumption |
0 |
3 |
Power Factor |
Ratio of active to total electric power in the pumping station. Default is 1. |
YES |
YES |
2 |
2 |
active_total_ratio |
1.0 |
0 |
1 |
PST Duty Head |
Overall (designed) duty head of the pumping station |
YES |
YES |
2 |
1 |
HEAD |
duty_head |
Double |
1 |
5000 |
Electric Mechanical Power Ratio |
Ratio of total electric to mechanical power for the pumping station. A measure of efficiency. Should be > 1.1. Default is 1.25 |
YES |
YES |
2 |
2 |
electric_hydraulic_ratio |
1 |
2 |
Tariff Name |
Name of the Electricity Tariff used for the pumping station |
YES |
YES |
2 |
30 |
0 |
electricity_tariff |
Text |
Voltage |
HIGH (>1000v) or LOW
YES |
YES |
2 |
0 |
voltage |
Boolean |
Bypass |
Flag to indicate if there is a bypass pipe allowing flow in both directions when the pumping station is switched off. The Bypass box on the Pumping Station Parameters Page may be checked to indicate that there is a bypass pipeline at the pumping station (see Figure below).
Booster Station with Bypass Pipeline In normal operation, the check valve in the bypass is closed due to the head increase in the PST. When all the pumps are switched off this valve remains closed until the outlet pressure drops below the inlet pressure. It then releases some flow around the PST to feed downstream demand when the pumps are off. Such an arrangement is common in booster stations, but much less in main pumping stations, where negative heads are unlikely. |
YES |
YES |
2 |
0 |
bypass |
Boolean |
CO2 Factor Regime |
Name of the Energy Factor CO2 Regime used for the pumping station |
YES |
YES |
2 |
30 |
0 |
eghgf_regime |
Text |
| Turbine |
Check this option to model the pump station as a turbine. (When modelling a pump station in turbine mode, Mode of Control (on the Pump Control Page) must be set to TURB) |
YES | YES | 2 | turbine | Boolean | 0 | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Pumps |
This page displays a list of pump curves and a series of parameters for each pump. The Pumping Station Operation dialog can be opened from this page by clicking the PST Operation button. Database Table Name: wn_pst_pumps
NO |
YES |
3 |
0 |
pumps |
Array |
Pumps Used |
This field lists the pumps used in the pumping station. This list is only shown on the grid. Full details of the pumps can be found on the Pump Data grid on the pump property sheet. See below. |
NO |
YES |
NO |
255 |
0 |
pumps_used |
Text |
Bends |
This field defines the geometry of the link. The underlying data consists of a series of (x,y) pairs defining the vertices of the link. Each link is made up of a series of straight lines between the defined (x,y) points. This data is not displayed on the grid or property sheet. Link vertices are included when you export link data to CSV files. There are two options available for exporting link vertices. These are selected on the Select CSV Export Options dialog using the Coordinate Arrays Format dropdown list. The options are:
NO |
YES |
NO |
0 |
XY |
bends |
Array |
InfoNet Unique ID |
The InfoNet Unique ID and InfoNet Network ID are unique identifiers associated with the corresponding object and network in an InfoNet database. When importing from InfoNet, these identifiers can be copied from the InfoNet database in order to maintain links between the two networks. |
YES |
YES |
NO |
0 |
asset_uid |
GUID |
InfoNet Network ID |
See InfoNet Unique ID |
NO |
YES |
NO |
0 |
asset_network_uid |
GUID |
Pumping Station Control Data
Database Table Name: wn_ctl_pst
Field Name |
Help Text |
Flag |
Grid |
Property Page |
Size |
Precision |
Units |
Database Field |
Data Type |
Default |
Error Lower Limit |
Error Upper Limit |
Mode Of Control |
Available modes are:
YES |
YES |
4 |
4 |
0 |
mode |
Text |
System Role |
Available system roles are:
YES |
YES |
4 |
10 |
0 |
system_role |
Text |
Control Node |
Control point for AUTO and PROF Mode of control. |
YES |
YES |
4 |
30 |
0 |
control_node |
Text |
| Control Pipe | Control link for TFLW Mode of control | YES | YES | 4 | 63 | 0 | control_pipe | Text | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Licensed Maximum Power Demand |
Maximum licensed power on the pumping station site (not the maximum installed power) |
YES |
YES |
4 |
1 |
WN_KVA |
max_power |
Override Node |
Optional - name of OVERPRESSURE control node for FLW, PLAN and TFLW Mode of control If the pressure/level at the Override node exceeds the Pressure Off value at any time, the pumping station will be stopped immediately, regardless of profile controls. The station will resume operation only when the pressure/level at the Override node falls below the Pressure On value. |
YES |
YES |
4 |
30 |
0 |
override_node |
Text |
Pressure On |
Restart level of pressure or water level at Override Node. |
YES |
YES |
4 |
2 |
WN_P |
pressure_on |
0 |
199 |
Pressure Off |
Switch off level of pressure or water level at Override Node. |
YES |
YES |
4 |
2 |
WN_P |
pressure_off |
0 |
199 |
Live Data Point ID |
Name of the associated Live Data Point, Live Data Feed, or Live Data Composite Feed. Note: Duplicate IDs are shown once.
YES |
YES |
4 |
100 |
0 |
live_data_point_id |
Text |
Pipe Closed |
The pipe is permanently closed if the box is checked |
YES |
YES |
4 |
0 |
pipe_closed |
Boolean |
Pumps |
Grid displayed for AUTO, PROF and TFLW control modes. List of pump initial values. The order of the pump control data corresponds with the order of the pumps specified on the Pump Data Page. Database Table Name: wn_ctl_pst_pumps
NO |
YES |
5 |
0 |
pumps |
Array |
Profiles |
Pump station profiles grid. Database Table Name: wn_ctl_pst_profiles
NO |
YES |
5 |
0 |
profiles |
Array |
| Pump specific profile |
Time varying profile for specific pumps. Applicable to AUTO, PROF and TFLW mode of control. To display the time varying profile for a pump, click the left hand side of the pump row in the pumps grid.
5 | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Repeat Period |
Profile period which will be repeated throughout simulation, if the Repeat Profile box is checked.
YES |
YES |
5 |
0 |
repeat_period |
Integer |
0 |
Repeat Profile |
Check the Repeat Profile box to repeat a profile (from 00:00 for the selected Repeat Period) for the duration of the simulation. Note: When using the Repeat Profile option; if the defined profile spans over the selected Repeat Period, the profile will not be repeated.
YES |
YES |
5 |
0 |
repeat_profile |
Boolean |
1 |
Repeat Profile |
YES |
YES |
5 |
0 |
repeat_status |
Boolean |
1 |
Repeat Period |
YES |
YES |
5 |
0 |
repeat_status_period |
Integer |
0 |
Linear Profile |
This checkbox decides if values in the profile grid are interpolated.
YES |
YES |
5 |
0 |
linear_profile |
Boolean |
After Last Point |
YES |
YES |
5 |
0 |
after_profile |
Integer |
Before First Point |
YES |
YES |
5 |
0 |
before_profile |
Integer |
| Multiple VSP Regulation |
When this option is checked the pump station will regulate using all identical and available variable speed pumps; pump speeds will vary together to achieve a target. If this option is unchecked, the pump station will only use the first available variable speed pump to regulate. Other pumps in the pump station will be run at full speed. Applicable to TFLW, AUTO and PROF Mode of Control pump stations with more than one variable speed pump. |
YES | YES | 5 | 0 | multi_vsp_regulation | Boolean | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Disable UPC |
Check this box to disable both local and global UPC Scripts for the network object. Any controls defined for the object other than UPC Scripts will be applied. |
NO |
YES |
6 |
disable_upc |
Boolean |
UPC Script |
Local UPC Script describing the logical controls for the current network object. |
NO |
YES |
6 |
upc_script |
Memo |
Enable Surge |
Check this option to enable Transient simulation fields. Note: The Enable Surge field and Enable PID Regulation field cannot be checked at the same time.
YES |
YES |
7 |
iwts_enable_surge |
Boolean |
0 |
Pump Event |
Time-speed profile used to dictate speed of pump during transients simulation when Pump Change is set to SPEED. Database Table Name: wn_ctl_pump_iwts_event
NO |
NO |
7 |
iwts_event |
Array |
Pump Change |
Type of pump operational change to be applied during transient simulation:
YES |
NO |
7 |
10 |
iwts_pump_change |
Text |
SPEED |
Trip Time |
Enabled when Pump Change field is set to TRIP or RATCHET. Time from start of transient simulation at which pump loses power. |
YES |
NO |
7 |
2 |
iwts_trip_time |
Single |
1 |
| Enable PID Regulation |
Check this option to enable PID regulation fields. Note: The Enable PID Regulation field and Enable Surge field cannot be checked at the same time.
YES | NO | 7 | 0 | iwtsEnableRegulation | Boolean | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Regulator Type |
Transient simulation field enabled when the Enable PID Regulation field is checked. Type of regulator:
YES | NO | 7 | 10 | 0 | iwtsRegulatorType | Text | Flow | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Setting |
Transient simulation field enabled when the Enable PID Regulation field is checked. Target flow value when Regulator Type is set to Flow. Target pressure value when Regulator Type is set to Pressure. |
YES | NO | 7 | 0 | iwtsSetting | Double | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Control Node |
Transient simulation field enabled when the Enable PID Regulation field is checked and Regulator Type is set to Pressure. Node where pressure is measured to control the pump station. |
YES | NO | 7 | 30 | 0 | iwts_control_node | Text | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Control Pipe |
Transient simulation field enabled when the Enable PID Regulation field is checked and Regulator Type is set to Flow. Pipe where flow is measured to control the pump station. |
YES | NO | 7 | 63 | 0 | iwts_control_pipe | Text | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Controller Gain |
Transient simulation field enabled when the Enable PID Regulation field is checked. The Velocity form of the PID equation is used to calculate the change in regulator setting from one sample time to the next.
YES | NO | 7 | 3 | iwts_controller_gain | Single | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Integral Time |
Transient simulation field enabled when the Enable PID Regulation field is checked. Integral time used in the Velocity PID equation (see Controller Gain for details). |
YES | NO | 7 | 1 | TS | iwts_integral_time | Single | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Differential Time |
Transient simulation field enabled when the Enable PID Regulation field is checked. Differential time used in the Velocity PID equation (see Controller Gain for details). |
YES | NO | 7 | 1 | TS | iwts_differential_time | Single | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
NRV Diameter |
Diameter of series non-return valve |
YES |
NO |
7 |
1 |
PS |
nrv_diameter |
Single |
0 |
NRV Loss Coefficient |
Local headloss coefficient when the non-return valve is fully open |
YES |
NO |
7 |
3 |
nrv_loss_coeff |
Single |
0 |
NRV Response Time |
The amount of time it takes for non-return valve to go from fully opened to fully closed |
YES |
NO |
7 |
3 |
nrv_response_t |
Single |
0 |
NRV Do Not Reopen |
If this option is checked, the non-return valve will not open once it has closed |
YES |
NO |
7 |
0 |
nrv_dont_reopen |
Boolean |
0 |
| Enable Surge (Turbine) |
Check this option to enable Transient simulation fields for turbines. |
YES | YES | 8 | 0 | iwts_enable_surge_turbine | Boolean | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Rated Efficiency |
Rated efficiency from manufacturer's curve A Transient simulation field. |
YES | YES | 8 | 2 | WN_OPEN | iwts_rated_efficiency | Long Integer | 0 | 100 | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Inertia |
A measure of the turbine's resistance to change in momentum. A Transient simulation field. |
YES | YES | 8 | 2 | WN_INERTIA | iwts_inertia | Single | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Turbine Diameter |
Internal diameter of turbine. A Transient simulation field. |
YES | YES | 8 | 1 | WN_P | iwts_turbine_diameter | Single | 0 | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Wicket Gate Initial Opening |
Opening of wicket gate at start of simulation. A Transient simulation field. |
YES | YES | 8 | 2 | WN_OPEN | iwts_wicket_gate_init_opening | Long Integer | 100 | 0 | 100 | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Change Type |
Type of turbine operational change to be applied during transient simulation:
YES | YES | 8 | 1 | iwts_change_type | Integer | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Trip Time |
Enabled when Change Type field is set to TRIP. Time from start of transient simulation at which pump loses power. |
YES | YES | 8 | 2 | iwts_trip_time | Single | 1 | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Time/Speed Grid |
Time-speed profile used to dictate speed of pump during transients simulation. Database Table Name: wn_ctl_pst_turbine_change
NO | NO | 8 | 0 | iwts_turbine_change | Array | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Wicket Gate Change Time/Opening Grid |
Time-opening profile used to dictate opening of wicket gate during transients simulation. Database Table Name: wn_ctl_pst_wicket_gate_change
NO | NO | 8 | 0 | iwts_wicket_gate_change | Array | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Maximum Shear Strength |
The maximum value for the corrosion layer shear strength on the pipe wall. The maximum value for which the hydraulic shear strength will result in material being eroded from the pipe wall. See Water Quality - Turbidity Analysis for further information. |
YES | YES | 9 | WN_STRESS | wq_max_shear_strength | Double | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Initial Shear Strength |
The initial value for the corrosion layer shear strength on the pipe wall. The hydraulic shear strength must rise above this initial value to begin the erosion of material from the pipe wall. See Water Quality - Turbidity Analysis for further information. |
YES | YES | 9 | WN_STRESS | wq_init_shear_strength | Double | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Erosion Coefficient |
Parameter used to calculate the quantity of material eroded from the pipe wall when the hydraulic shear stress exceeds the corrosion layer shear strength; the excess shear. See Water Quality - Turbidity Analysis for further information. |
YES | YES | 9 | WN_RATE | wq_erosion_coefficient | Double | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Erosion Exponent |
The power to which the ratio of excess shear to maximum shear strength is raised when calculating the quantity of material released from the pipe wall. A value of zero will be interpreted as meaning the erosion is independent of the excess shear. See Water Quality - Turbidity Analysis for further information. |
YES | YES | 9 | wq_erosion_exponent | Double | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| Release Coefficient |
Parameter used to calculate the increase in turbidity as a result of material eroded from the pipe wall. See Water Quality - Turbidity Analysis for further information. |
YES | YES | 9 | WN_TURBLEN | wq_release_coefficient | Double | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Max No. of Switches |
A Cost Management Simulation constraint. The target maximum number of times that pumps may be switched on / off during the simulation. |
YES |
YES |
10 |
0 |
opt_max_switches |
Integer |
8 |
| Period (Max) |
A Cost Management Simulation constraint. Length of time over which Volume (Max) is considered. |
YES | YES | 10 | DUR | opt_MaxFlowVolumePeriod | Long Integer | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Volume (Max) |
A Cost Management Simulation constraint. Target maximum volume of water to flow through the pump over the Period (Max) measured from Period Start (Max) and taking into account Initial Volume (Max). |
YES | YES | 10 | WN_DVO | opt_MaxFlowVolume | Double | 0.0 | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Period Start (Max) |
A Cost Management Simulation constraint. Start Date / Time of the period for assessing whether Volume (Max) through the pump has been reached. Used in conjunction with Initial Volume (Max) if the period start is before the start of the simulation. |
YES | YES | 10 | opt_MaxVolStart_Dtime | Date / Time | 0.0 | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Initial Volume (Max) |
A Cost Management Simulation constraint. Volume of water that has already passed through the pump at the start of the simulation. Used in conjunction with Period Start (Max). |
YES | YES | 10 | 1 | WN_DVO | opt_MaxVolInit_litre | Double | 0.0 | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Volume (Min) |
A Cost Management Simulation constraint. Target minimum volume of water to flow through the pump over the Period (Min) measured from Period Start (Min) and taking into account Initial Volume (Min). |
YES | YES | 10 | WN_DVO | opt_MinFlowVolume | Double | 0.0 | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Period (Min) |
A Cost Management Simulation constraint. Length of time over which Volume (Min) is considered. |
YES | YES | 10 | DUR | opt_MinFlowVolumePeriod | Long Integer | 0 | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Period Start (Min) |
A Cost Management Simulation constraint. Start Date / Time of the period for assessing whether Volume (Min) through the pump has been reached. Used in conjunction with Initial Volume (Min) if the period start is before the start of the simulation. |
YES | YES | 10 | opt_MinVolStart_Dtime | Date / Time | 0.0 | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Initial Volume (Min) |
A Cost Management Simulation constraint. Volume of water that has already passed through the pump at the start of the simulation. Used in conjunction with Period Start (Min). |
YES | YES | 10 | 1 | WN_DVO | opt_MinVolInit_litre | Double | 0.0 | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Notes |
You can keep freeform notes about any object in your network. The notes field can be up to 64,000 characters in size, or about 10 pages of printed text. |
NO |
YES |
13 |
0 |
notes |
Memo |
Has Local UPC |
Read only field displayed in the grid view only. If the Has Local UPC box is checked, the network objects has a Local UPC Script defined. The UPC Script can be viewed from the object property sheet. |
NO |
YES |
NO |
has_local_upc |
Boolean |
PoW Unit Cost (from - to) |
Cost per cubic metre, in user defined currency units, of transferring water between the From Node and To Node. Prices can be negative to allow for exports or bulk water sale. |
YES |
YES |
NO |
2 |
WN_VCOST |
usds_pow_cost |
PoW Category (from - to) |
The category into which this cost falls, for flow between the From Node and To Node.
YES |
YES |
NO |
16 |
0 |
usds_pow_cat |
Text |
PoW Unit Cost (to - from) |
Cost per cubic metre, in user defined currency units, of transferring water between the To Node and From Node. Prices can be negative to allow for exports or bulk water sale. |
YES |
YES |
NO |
2 |
WN_VCOST |
dsus_pow_cost |
PoW Category (to - from) |
The category into which this cost falls, for flow between the To Node and From Node.
YES |
YES |
NO |
16 |
0 |
dsus_pow_cat |
Text |
From Node ID |
YES |
YES |
1 |
30 |
0 |
us_node_id |
Text |
To Node ID |
YES |
YES |
1 |
30 |
0 |
ds_node_id |
Text |
Suffix |
YES |
YES |
NO |
1 |
0 |
link_suffix |
Text |
Asset ID |
YES |
YES |
1 |
30 |
asset_id |
Text |
PoW |
Read only field that indicates if Price of Water data has been entered on the property sheet |
NO |
YES |
NO |
0 |
pow_selected |
Boolean |
Pumping Station Results
All results fields are displayed on the grid when opened while viewing a replay of a simulation, and on a special results page placed at the front of Property Sheets displayed while viewing a simulation replay.
For details of results fields for links, see the Link Results Data Fields topic.
Pumping Station Data fields related to live data
These fields are present in the Pump Station Live Control editor, which is accessible from the Fields tab of the Baseline.
Database Table Name- wn_ctl_f_pst_livec.
Field Name |
Database Name |
Database Field |
Description |
Data Type |
Size |
Units |
Start time |
wn_ctl_f_pst_livec |
start_time |
Date / Time |
DUR |
End time |
end_time |
Date / Time |
DUR |
Pump Status Flags |
pump_status_flags |
Text |
12 |