Condenser Loop

The condenser loop uses a cooling tower to supply cooling water to the water-cooled electric chiller in the chilled water loop.

Required Objects

The condenser loop must have the following property.
  • It must have at least 1 demand object, such as a chiller or water source heat pump (WSHP), attached to the loop.

Design Assumptions

  • A condenser loop can operate in two modes, as follows.

    Cooling-only condenser loop

    • The condenser operates in this mode when it only has cooling-only piece of equipment connected to it.
    • The cooling-only condenser loop has the following default temperature assumptions.
      Property Value Notes
      Design supply temperature 29.44°C
      Design range 5.56°C
      Operational control type Outdoor wet bulb reset
      Operational approach temperature 3.89°C

    Condenser loop with cooling and supplemental heat

    • The condenser operates in this mode when the condenser loop contains a variable refrigerant flow (VRF) condenser or a WHSP.

Configuration

There are 2 configurations for each of the two following condenser loop operations.

Cooling Only

    1. Pump
    2. Cooling Tower

    condenser loop with cooling and supplemental heating

    1. Pump
    2. Boiler
    3. Fluid Cooler

Pump

The pump has the following assumptions.

Property Value Notes
Pressure rise 148556.625 Pa
Flow type Constant speed
Flow control Intermittent Only runs when there is demand.

Cooling Tower

The pump has the following assumptions.

Property Value Notes
Fan type Variable speed
Design approach 3.8888889°C
Design range temperature 5.55555556°C

Fluid Cooler

The pump has the following assumptions.

Property Value Notes
Fan type Constant speed

Boiler

The pump has the following assumptions.

Property Value Notes
Design supply temperature 21.11°C
Efficiency 96%
Flow mode Constant