Variable Refrigerant Flow Loop
The Variable Refrigerant Flow (VRF) loop has a VRF condenser. As an option, the condenser may be water-cooled, in which case it is attached to a condenser loop.
Required Objects
The VRF loop must have the following property.
  • It must have at least one VRF Fan Coil Unit attached to the loop.
Design Assumptions
  • The VRF Loop has the following default temperature assumptions.
Property Value Notes
Rated cooling COP 3.3
Rated heating COP 3.5
Minimum outdoor air temperature in heating -20°C
Low temperature loop return temperature 15.5556°C Set by hot water loop if hot water coil is used in system
Heating Coil
The heating coil has the following assumptions.
Coil leaving air temperature 40°C
Supplemental Heating Coil
This is an electric resistance coil with an efficiency of 1.0
Supply Fan
The supply fan has the following properties.
Pressure rise 250 Pa
Total efficiency 70%
Motor efficiency 90%