Radiant Panel
A radiant panel supplies heat directly to the floor or to panels in the wall or ceiling.
Required Objects
The radiant panel must have the following properties.
  • It must be connected to a hot water loop.
  • It must be connected to a chilled water loop.
  • It must be attached to a conditioned zone.
Design Assumptions
  • The radiant panel is modeled as a four pipe fan coil with no fan power at the moment.
Property Value Notes
Cooling discharge air temperature 17°C This is passive air movement.
Heating discharge air temperature 29.44°C This is passive air movement.
Cooling Coil
The cooling coil has the following assumptions.
Coil entering air temperature N/A Mix of air system and induced zone temperature.
Design coil leaving air temperature 17°C It is on the colder side of discharge temperatures.
Chilled water design inlet temperature N/A Set by the chilled water loop.
Chilled water design outlet temperature N/A Set by the chilled water loop.
Heating Coil
The heating coil has the following assumptions.
Design coil leaving air temperature 29.44°C
Hot water design inlet temperature N/A Set by the hot water loop.
Hot water design outlet temperature N/A Set by the hot water loop.