Active Chilled Beam
An active chilled beam consists of a heat exchanger and an integral air supply. It is normally suspended from a ceiling.
Required Objects
The active chilled beam must have the following properties.
  • It must be connected to an air system.
  • It must be connected to a hot water loop.
  • It must be connected to chilled water loop.
  • It must be attached to a conditioned zone.
Design Assumptions
If a chilled beam is in an air system designated as a dedicated outdoor air system (DOAS), its supply air flow rate is limited to the ventilation rate.
Property Value Notes
System air flow Constant
Induction ratio 2.5 This is a fixed induction ratio.
Cooling discharge air temperature 17°C
Heating discharge air temperature 29.44°C
Air system primary air temperature N/A Determined by the air system (typically 12.7778°C).
Cooling Coil
The cooling coil has the following assumptions.
Coil entering air temperature N/A Mix of air system and induced zone temperature.
Design coil leaving air temperature 17°C It is on the colder side of discharge temperatures.
Chilled water design inlet temperature N/A Set by the chilled water loop.
Chilled water design outlet temperature N/A Set by the chilled water loop.
Heating Coil
The heating coil has the following assumptions.
Coil leaving air temperature 29.44°C
Hot water design inlet temperature N/A Set by the hot water loop.
Hot water design outlet temperature N/A Set by the hot water loop.