Fancoil w/WC & GAS w/ DOAS + ERV
Variable Volume Fan Coils with Water-Cooled Chiller with Gas Boiler with DOAS and ERV - This system consists of a 4-pipe Variable Speed Fan Coil Unit serving each conditioned thermal zone. Chilled water is provided by a primary only variable flow chilled water loop. Hot water is provided by a primary only variable flow hot water loop served by a natural gas boiler. A Single DOAS/ERV system is modeled to precondition the outside air for each thermal zone using an ERV along with chilled and hot water coil. The default ASHRAE Standard used to set the efficiency of regulated equipment is ASHRAE 90.1-2016.
Water Cooled Chiller:
Quantity: 1
Capacity: Auto-sized
Compressor Type (Screw, Centrifugal or Scroll compressor), based on capacity
Controls: Based on Capacity and ASHRAE Standard
Efficiency: Based on Capacity and ASHRAE Standard
Chilled Water Pumps:
Quantity: 1
Design Flow: Auto-sized
Type: Variable Speed, 30% minimum flow
Efficiency: Based on design flow and ASHRAE Standard
Hot Water Boiler:
Quantity: 1
Type: Natural Gas, Efficiency based on Capacity and ASHRAE Standard
Hot Water Pumps:
Quantity: 1
Efficiency: Based on Design Flow and ASHRAE Standard
ERV:
Quantity: 1
Controls: Based on Climate Zone and ASHRAE Standard
Effectiveness: Based on Design Airflow, % Outside Air, Climate Zone and ASHRAE Standard
DOAS AHU:
Controls: Based on Design Airflow, Climate Zone and ASHRAE Standard
DOAS AHU Fans:
Quantity: 1
Design Airflow: Auto-sized
Efficiency: Based on Design Airflow and ASHRAE Standard
Variable Speed Fan Coil Units:
Quantity: 1 per thermal zone
Heating Coil Type: Hot Water
Cooling Coil Type: Chilled Water
Fan Speed Controls: Based on Zone Airflow and ASHRAE Standard