Porous Wall Data Fields (InfoWorks)
Note: Porous wall functionality has been superseded by the Base Linear Structure (2D). Porous wall objects have been retained for backwards compatibility.
Porous wall objects are line objects used as part of the mesh generation process carried out when undertaking 2D Modelling. The lines represent walls with a specified porosity and height which are taken into account during the 2D simulation process. Where a porous wall is collinear with the boundary of a 2D Zone, the porous wall will override the boundary condition of the 2D Zone.
Note: To view all data relating to this object, use the Object Properties Window. These data fields are read-only in ICMLive Operator Client. Network objects are configured in InfoWorks ICM Ultimate and ICMLive Configuration Manager. Please refer to the InfoWorks ICM help for more details.
The following describes all the data which can be used to define a porous wall.
Fields that are common to the majority of objects can be found in the Common Fields topic.
Porous Wall Data
Database Table Name: hw_porous_wall
Field Name
Description
Database Field
Data Type
Size
Units
Precision
Default
Error Lower Limit
Error Upper Limit
Warning Lower Limit
Warning Upper Limit
Porous wall
ID of the line.
line_id
Text
64
0
0
0
0
0
Asset ID
For reference only. Designed as a reference to an asset database, but could be used for anything.
asset_id
Text
64
0
Length
Length of the Line.
length
Single
L
3
Porosity
Porosity factor between 0 and 1, where 0 represents impermeable and 1 represents fully permeable.
porosity
Double
3
0.0
0
1
Crest level
Type of wall.
Note that a porous wall collinear with the boundary of a 2D zone, will override the boundary condition of the 2D zone along the coincident portion of the boundary. The coincident portions of the wall are considered infinitely high, regardless of any crest level specified.
Database Value
Description
Infinite
Wall is considered to be an infinitely high barrier.
Height
The height of the wall (above ground level) is specified in the Height field.
Level
The level of the wall (above datum) is specified in the Level field.
crest_level
Text
20
0
Infinite
0
0
0
0
Height
Enabled if Crest level of type Height is selected.
Height of the top of the wall from ground level.
For each segment of wall, this is the height above the highest of the ground levels of the two computational elements either side of the wall.
height
Double
Y
3
0.0
0
Level
Enabled if Crest level of type Level is selected.
Height above datum of the top of the wall.
level
Double
Z
3
0.0
Remove wall during simulation
Collapse option for wall:
Database Value
Description
Never
Wall never collapses.
Fully
The entire length of the wall collapses when the wall removal threshold is met in any of the mesh elements adjacent to the wall.
Partially
When the wall removal threshold is met in a mesh element adjacent to the wall, the length of the wall adjacent to the mesh element collapses.
remove_wall
Text
10
0
Never
Wall removal trigger
Variable used to determine when wall is collapsed. This trigger variable relates to the 2D results in the mesh elements adjacent to the wall face.
Database Value
Description
Depth
Depth of water in mesh elements adjacent to wall.
Elevation
Water surface elevation of mesh elements adjacent to the wall.
Velocity
Velocity in mesh elements adjacent to the wall, in the normal direction to the wall.
Unit flow
Flow per unit of length in mesh elements adjacent to wall, in the normal direction to the wall.
Total head
Total head in the normal direction to the wall, in adjacent elements to the wall multiplied by the Hydrostatic pressure coefficient. Total head is calculated as:
V = A x H
Where:
H = h + u2/(2g)
V(m): Corrected head
A: Hydrostatic pressure coefficient
H(m): total head
h(m): depth
u(m/s): normal velocity to the wall
g(m/s2): gravity
Force per unit length
Total force per unit length in the normal direction to the wall, in adjacent elements to the wall. Force per unit length is calculated as:
F = A x 0.5 x ρgH2
Where:
F(kN/m): Force per unit length
H(m): total head
ρ (Tm/m3): water density
g(m/s2): gravity
wall_removal_trigger
Text
21
0
Depth
Use difference across wall
If checked, determines when the wall collapses by calculating the difference in the Wall removal trigger variable between the two elements on either side of the wall.
If unchecked, wall collapse will be determined by value of trigger variable in any of the mesh elements adjacent to the wall.
use_diff_across_wall
Boolean
0
0
Depth threshold
Enabled when Wall removal trigger is set to Depth.
  • When the Use difference across wall option is not selected: the wall is collapsed if the depth of water in any of the mesh elements adjacent to the wall exceeds the Depth threshold.
  • When the Use difference across wall option is selected: the wall is collapsed when the difference between the water depths of the two elements adjacent to the wall exceeds the Depth threshold.
depth_threshold
Double
Y
3
0.0
Elevation threshold
Enabled when Wall removal trigger is set to Elevation.
  • When the Use difference across wall option is not selected: the wall is collapsed if the water surface elevation in any of the mesh elements adjacent to the wall exceeds the Elevation threshold.
  • When the Use difference across wall option is selected: the wall is collapsed when the difference between the water surface elevation of the two elements adjacent to the wall exceeds the Elevation threshold.
This only applies if at least one of the adjacent elements is wet.
elevation_threshold
Double
Z
3
0.0
Velocity threshold
Enabled when Wall removal trigger is set to Velocity.
  • When the Use difference across wall option is not selected: the wall is collapsed if the normal velocity to the wall in any of the mesh elements adjacent to the wall exceeds the Velocity threshold.
  • When the Use difference across wall option is selected: the wall is collapsed when the difference between the velocity normal to the wall of the two elements adjacent to the wall exceeds the Velocity threshold.
velocity_threshold
Double
V
3
0.0
Unit flow threshold
Enabled when Wall removal trigger is set to Unit flow.
  • When the Use difference across wall option is not selected: the wall is collapsed if the flow per unit length normal to the wall in any of the mesh elements adjacent to the wall exceeds the Unit flow threshold.
  • When the Use difference across wall option is selected: the wall is collapsed when the difference between the flow per unit length normal to the wall of the two elements adjacent to the wall exceeds the Unit flow threshold.
unit_flow_threshold
Double
UQ
3
0.0
Total head threshold
Enabled when Wall removal trigger is set to Total head.
  • When the Use difference across wall option is not selected: the wall is collapsed if the corrected total head in the normal direction to the wall in any of the mesh elements adjacent to the wall exceeds the Total head threshold.
  • When the Use difference across wall option is selected: the wall is collapsed when the difference between the corrected total head normal to the wall of the two elements adjacent to the wall exceeds the Total head threshold.
Corrected total head is calculated by the following equation:
V = A x H
Where:
H = h + u2/(2g)
H(m): total head
h(m): depth
g(m/s2): gravity
total_head_threshold
Double
Y
3
0.0
Force threshold
Enabled when Wall removal trigger is set to Force per unit length.
  • When the Use difference across wall option is not selected: the wall is collapsed if the force per unit length in the normal direction to the wall in any of the mesh elements adjacent to the wall exceeds the Force threshold.
  • When the Use difference across wall option is selected: the wall is collapsed when the difference between the force per unit length normal to the wall of the two elements adjacent to the wall exceeds the Force threshold.
F = A x 0.5 x ρgH2
Where:
H(m): total head
ρ(Tm/m3): water density
g(m/s2): gravity
force_threshold
Double
UF
3
0.0
Multiplying factor applied when using Total head or Force per unit length as the Wall removal trigger.
hydro_press_coeff
Double
3
1.0
General Line XY Data
The coordinate of the line vertices. The underlying data consists of a series of (x,y) pairs. Each line is made up of a series of straight lines between the defined (x,y) pairs.
This data is not displayed on the grid or property sheet.
Coordinates of line vertices are included when you export line data to CSV files. There are two options available for exporting line coordinates. These are selected on the Select CSV Export Options Dialog using the Coordinate Arrays Format dropdown. The options are:
  • Packed - The data is exported as a series of x,y pairs. {389904.,111350.,390309.,111765.}
  • Separately - the data is appended to the end of the row containing the line data. Each x and y value is in a separate (comma separated) field.
general_line_xy
Array
XY
3